[EnergyPlus_Support] Re: What will the weather file override?



OK, so the best autosizing results will come from the design days in the DDY file. I was hoping to find a way to simplify the process of changing cities, but looks like I have to do it the long way. Thanks for your help.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> They may undersize because they are not the design conditions  --- 
> only the extremes of the weather file.  And if the weather files are 
> "typical" as most are, then they won't represent the real "extremes" 
> of the location.
> 
> At 06:30 AM 7/21/2009, craig_s_simmons wrote:
> >I would be cautious about using SummerExtreme and WinterExtreme if 
> >you are using the simulations for sizing. I have found that they 
> >tend to under-size.
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/