This is an artefact of how the fan coil unit is controlled. The water flow is varied while the air flow is held constant. In any NTU-effectiveness heat exchanger model, if one capacity flow rate is small in relation to the other stream's capacity flow rate, the small flow stream will exit at the high flow stream's temperature. If both air flow and water flow were varied simultaneously, you woul not see this happening. I'm not sure why the fan coil model is violating the minimum flow rate. Fred Buhl hata102640 wrote: There is a similar problem to me. The cold water flow rate is too much down when the capacity of fan coil unit is controlled,so the cold water outlet temperature has risen. I set field "Minimum Cold Water Flow Rate" of object "ZoneHVAC:FourPipeFanCoil" to limit reduction of the water flow rate. However, although a minimum cold water flow rate is set, the water flow rate is still less than it. There are not too many descriptions for "Minimum Cold Water Flow Rate" in the manual. Hiroyuki --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" <mjwitte@...> wrote: __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.