Whether a plate or rotary HX, there may be residual power consumed. If
so, enter the value in the Nominal Electric Power field. If you believe
no power is needed for this HX, enter 0.
HeatExchanger:AirToAir:SensibleAndLatent,
50.0, !- Nominal Electric Power {W}
From the IO Reference:
Field: Nominal Electric Power
The electric consumption rate of the unit in watts. Electric power is
considered constant whenever the unit operates. This numeric input can
be used to model electric power consumption by controls (transformers,
relays, etc.) and/or a motor for a rotary heat exchanger. None of this
electric power contributes thermal load to the supply or exhaust air
streams. The default value for this field is 0.
vs114 wrote:
>
>
> Dear users,
>
> I use an ERV, according the example with the HVAC stand alone.
> The ERV i use is a "plate".
> I can understand the consumption for the fans, be also the programm
> gives consumption extra for the ERV.
> Does anybody knows what is this?
>
> Thanks,
> Vaggelis
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/