What is the reporting frequency? Maybe you are comparing results averaged over an hour to an instantaneous hand calculation.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Feng Kelvin
Sent: Thursday, July 23, 2009 11:40 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: Feng Kelvin
Subject: [EnergyPlus_Support] Summer Design Day -- Direct Solar Radiation Calculation
Hi group,
I am using my E+ v2.2 design day to simulate a simple concrete two rooms case. I found E+'s Direct Solar Radiation output result doesn't match with direct normal solar radiation calculation equation: EDN = A / exp ( B / sin(beta) )
I pick up my case at 6:00am simulation results. E+ results give:
solar altitude angle, beta = 12.049 [deg]
direct normal radiation, EDN = 201 [W/m2]
I calculate solar altitude myself by inputting building altitude, declination angle and solar time and found the solar altitude angle, beta = 12.049 is correct. However, when I use
EDN = A / exp ( B / sin(beta) )
where A = 1093 [W/m2]
B = 0.186
I got EDN = 449.98 [W/m2], not 201 [W/m2] calculated by E+.
Am I missing sth in this, or this has been fixed in new E+ version?
--
Best Regards
Kelvin
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___