[EnergyPlus_Support] Re: Pretreating Outside Air
Thanks Richard, but E+ is still crashing. Here is what I added/changed beyond the normal air loop. (I also added the schedule for the set point and the performance curves). Did I overlook something?
Coil:Cooling:DX:SingleSpeed,
Top Core Precool Coil, !- Name
ALWAYS_ON, !- Availability Schedule Name
AUTOSIZE, !- Rated Total Cooling Capacity {W}
AUTOSIZE, !- Rated Sensible Heat Ratio
4.56651, !- Rated COP
AUTOSIZE, !- Rated Air Flow Rate {m3/s}
Top Core Outdoor Air, !- Air Inlet Node Name
Top Core Treated Outdoor Air, !- Air Outlet Node Name
PSZ-AC:1_CoolCStandard10Ton_CapFT, !- Total Cooling Capacity Function of Temperature Curve Name
PSZ-AC:1_CoolCStandard10Ton_CapFF, !- Total Cooling Capacity Function of Flow Fraction Curve Name
PSZ-AC:1_CoolCStandard10Ton_EIRFT, !- Energy Input Ratio Function of Temperature Curve Name
PSZ-AC:1_CoolCStandard10Ton_EIRFFF, !- Energy Input Ratio Function of Flow Fraction Curve Name
PSZ-AC:1_CoolCStandard10Ton_PLR, !- Part Load Fraction Correlation Curve Name
ContinuousFanWithCyclingCompressor; !- Supply Air Fan Operating Mode
AirLoopHVAC:UnitaryCoolOnly,
Top Core Precool Sys, !- Name
ALWAYS_ON, !- Availability Schedule Name
Top Core Outdoor Air, !- DX Cooling Coil System Inlet Node Name
Top Core Treated Outdoor Air, !- DX Cooling Coil System Outlet Node Name
Top Core Treated Outdoor Air, !- DX Cooling Coil System Sensor Node Name
Coil:Cooling:DX:SingleSpeed, !- Cooling Coil Object Type
Top Core Precool Coil, !- Cooling Coil Name
None, !- Dehumidification Control Type
Yes, !- Run on Sensible Load
No; !- Run on Latent Load
AirLoopHVAC:OutdoorAirSystem:EquipmentList,
Top Core OA Equipment, !- Name
AirLoopHVAC:UnitaryCoolOnly, !- Component 1 Object Type
Top Core Precool Sys, !- Component 1 Name
OutdoorAir:Mixer, !- Component 2 Object Type
Top Core Mixing Box; !- Component 2 Name
OutdoorAir:Mixer,
Top Core Mixing Box, !- Name
Top Core Mixed Air, !- Mixed Air Node Name
Top Core Treated Outdoor Air, !- Outdoor Air Stream Node Name
Top Core Relief Air, !- Relief Air Stream Node Name
Top Core Return Air; !- Return Air Stream Node Name
SetpointManager:Scheduled,
Top Core OA Pretreat, !- Name
Temperature, !- Control Variable
OA Pretreat Sched, !- Schedule Name
Top Core Treated Outdoor Air; !- Setpoint Node or NodeList Name
Thanks again; I would appreciate any help.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Use the AirLoopHVAC:UnitaryCoolOnly object in the place where you put
> the DX cooling coil. The DX coil is part of the
> AirLoopHVAC:UnitaryCoolOnly object. Control it with a scheduled set
> point manager.
>
> superbluescooter24 wrote:
> >
> >
> > Hey,
> > I'm trying to condtion outside air before it reaches the mixing box of
> > the air loop. Is there any way to accomplish this with a DX cooling
> > coil? After trying to add a Coil:Cooling:DX:SingleSpeed before the
> > outdoor air stream of the mixing box, E+ crashed. Any advice?
> > Thanks!!!
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/