[EnergyPlus_Support] Re: Pretreating Outside Air



Thanks Richard, but E+ is still crashing.  Here is what I added/changed beyond the normal air loop.  (I also added the schedule for the set point and the performance curves).  Did I overlook something?

Coil:Cooling:DX:SingleSpeed,
    Top Core Precool Coil,   !- Name
    ALWAYS_ON,               !- Availability Schedule Name
    AUTOSIZE,                !- Rated Total Cooling Capacity {W}
    AUTOSIZE,                !- Rated Sensible Heat Ratio
    4.56651,                 !- Rated COP
    AUTOSIZE,                !- Rated Air Flow Rate {m3/s}
    Top Core Outdoor Air,    !- Air Inlet Node Name
    Top Core Treated Outdoor Air,  !- Air Outlet Node Name
    PSZ-AC:1_CoolCStandard10Ton_CapFT,  !- Total Cooling Capacity Function of Temperature Curve Name
    PSZ-AC:1_CoolCStandard10Ton_CapFF,  !- Total Cooling Capacity Function of Flow Fraction Curve Name
    PSZ-AC:1_CoolCStandard10Ton_EIRFT,  !- Energy Input Ratio Function of Temperature Curve Name
    PSZ-AC:1_CoolCStandard10Ton_EIRFFF,  !- Energy Input Ratio Function of Flow Fraction Curve Name
    PSZ-AC:1_CoolCStandard10Ton_PLR,  !- Part Load Fraction Correlation Curve Name
    ContinuousFanWithCyclingCompressor;  !- Supply Air Fan Operating Mode

AirLoopHVAC:UnitaryCoolOnly,
    Top Core Precool Sys,    !- Name
    ALWAYS_ON,               !- Availability Schedule Name
    Top Core Outdoor Air,    !- DX Cooling Coil System Inlet Node Name
    Top Core Treated Outdoor Air,  !- DX Cooling Coil System Outlet Node Name
    Top Core Treated Outdoor Air,  !- DX Cooling Coil System Sensor Node Name
    Coil:Cooling:DX:SingleSpeed,  !- Cooling Coil Object Type
    Top Core Precool Coil,   !- Cooling Coil Name
    None,                    !- Dehumidification Control Type
    Yes,                     !- Run on Sensible Load
    No;                      !- Run on Latent Load

AirLoopHVAC:OutdoorAirSystem:EquipmentList,
    Top Core OA Equipment,   !- Name
    AirLoopHVAC:UnitaryCoolOnly,  !- Component 1 Object Type
    Top Core Precool Sys,    !- Component 1 Name
    OutdoorAir:Mixer,        !- Component 2 Object Type
    Top Core Mixing Box;     !- Component 2 Name

OutdoorAir:Mixer,
    Top Core Mixing Box,     !- Name
    Top Core Mixed Air,      !- Mixed Air Node Name
    Top Core Treated Outdoor Air,  !- Outdoor Air Stream Node Name
    Top Core Relief Air,     !- Relief Air Stream Node Name
    Top Core Return Air;     !- Return Air Stream Node Name

SetpointManager:Scheduled,
    Top Core OA Pretreat,    !- Name
    Temperature,             !- Control Variable
    OA Pretreat Sched,       !- Schedule Name
    Top Core Treated Outdoor Air;  !- Setpoint Node or NodeList Name


Thanks again; I would appreciate any help.





--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Use the AirLoopHVAC:UnitaryCoolOnly object in the place where you put 
> the DX cooling coil. The DX coil is part of the 
> AirLoopHVAC:UnitaryCoolOnly object. Control it with a scheduled set 
> point manager.
> 
> superbluescooter24 wrote:
> >  
> >
> > Hey,
> > I'm trying to condtion outside air before it reaches the mixing box of 
> > the air loop. Is there any way to accomplish this with a DX cooling 
> > coil? After trying to add a Coil:Cooling:DX:SingleSpeed before the 
> > outdoor air stream of the mixing box, E+ crashed. Any advice?
> > Thanks!!!
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/