Navisa, The ZoneInfiltration:FlowCoefficent model is described in the
ASHRAE handbook of fundamentals (Chapter 27 in the 2005 edition). The flow
Coefficient is a property of the building determined using a blower door test and
can also be derived from a leakage area. The other coefficients are tabulated
in the ASHRAE chapter for various building heights, foundations, etc. Hope that helps, Neal Kruis From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of navisa While using this model to simulate
infiltration, how do we arrive upon the flow coefficients to be entered? How do
we combine all surfaces i.e doors, windows, external walls, roof for these
coefficient values? __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.