[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: severe error with incorrect number of surfaces



Thank you for the replies. 

I further corrected my model and I no longer get this error, but I am interested in finding why this came up the first place. The error file includes the following:


Program Version,EnergyPlus 3.1.0.027, 08/09/2009 11:17,IDD_Version 3.1.0.027
   ** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
   **   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.
   ** Warning ** Weather file location will be used rather than entered Location object.
   **   ~~~   ** ..Location object=CARDIFF WALES - UK
   **   ~~~   ** ..Weather File Location=SAN_FRANCISCO CA USA TMY2-23234 WMO#=724940
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:1178, in Zone=G_CIRC3
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:1788, in Zone=G_G_30
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:1837, in Zone=G_G_27
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:1926, in Zone=G_G_21
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:2198, in Zone=G_TOILETS2
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:2376, in Zone=G_CIRC5
   ** Severe  ** BuildingSurface:Detailed="OBJ:12087", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12088", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12089", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12090", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12091", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12092", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12093", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12094", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:12168, in Zone=LG_FOYER_ATRIUM2
   ** Severe  ** BuildingSurface:Detailed="OBJ:12197", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12198", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12199", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12200", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12201", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12202", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12203", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Severe  ** BuildingSurface:Detailed="OBJ:12204", invalid Construction Name="FF_ATRIUM_WINDOW" - has Window materials.
   **   ~~~   ** ...because Surface Type=WALL
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:12296, in Zone=LG_DR_DENTIST_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:12311, in Zone=LG_DR_DENTIST_1_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:12506, in Zone=LG_L_1
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:12537, in Zone=LG_L_1
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:12766, in Zone=LG_CIRC_3
   ** Severe  ** BuildingSurface:Detailed="OBJ:12876", invalid Surface Type="WINDOW
   ** Severe  ** BuildingSurface:Detailed="OBJ:12876", invalid Construction Name="FF_EXTERNAL_WINDOWS" - has Window materials.
   **   ~~~   ** ...because Surface Type=WINDOW
   ** Severe  ** BuildingSurface:Detailed="OBJ:12892", invalid Surface Type="WINDOW
   ** Severe  ** BuildingSurface:Detailed="OBJ:12892", invalid Construction Name="FF_EXTERNAL_WINDOWS" - has Window materials.
   **   ~~~   ** ...because Surface Type=WINDOW
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13028, in Zone=LG_L_13
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13186, in Zone=LG_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13327, in Zone=LG_L_2
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13403, in Zone=BS_DISPOSABLES_1_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13424, in Zone=BS_PRODUCTIONKITCHEN_1_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13528, in Zone=BS_GYMNASIUM_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13641, in Zone=BS_HVROOM_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13782, in Zone=BS_RESTAURANT_2_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13841, in Zone=BS_LIFT9
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13843, in Zone=BS_LIFT9
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13868, in Zone=BS_SPRINKLERPUMPROOM_1_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:13888, in Zone=BS_CONTROLROOM_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:13920, in Zone=BS_GENERATORROOM_1_
   ** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=OBJ:14301, in Zone=BS_TANKROOM_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:14308, in Zone=BS_TANKROOM_1_
   ** Warning ** Roof/Ceiling Tilt=180.0, much greater than expected tilt of 0, for Surface=OBJ:14312, in Zone=BS_TANKROOM_1_
   ** Severe  ** Reordered # of Surfaces (3707) not = Total # of Surfaces (3709)
   ** Warning ** Remaining surface checks will use "reordered number of surfaces", not number of original surfaces
   ** Severe  ** GetSurfaceData: Potential "OtherZoneSurface" is not matched correctly:
   **   ~~~   ** Surface=OBJ:1117, Zone=G_KITCHEN_1_
   **   ~~~   ** Nonmatched Other/InterZone Surface=OBJ:2230, Zone=G_SERVICES2
   ** Warning ** GetSurfaceData: Interzone surfaces cannot be "SunExposed" -- removing SunExposed
   **   ~~~   **   Surface=OBJ:1117, Zone=G_KITCHEN_1_
   **   ~~~   **   Surface=OBJ:2230, Zone=G_SERVICES2
   ** Warning ** GetSurfaceData: Interzone surfaces cannot be "WindExposed" -- removing WindExposed
   **   ~~~   **   Surface=OBJ:1117, Zone=G_KITCHEN_1_
   **   ~~~   **   Surface=OBJ:2230, Zone=G_SERVICES2
   **   ~~~   ** ... number of sides must be >= 3, this surface # sides=0
   **   ~~~   ** ... number of sides must be >= 3, this surface # sides=0
   ** Warning ** CalcSurfaceCentroid: 587 Surfaces have the Z coordinate < 0.
   **   ~~~   ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
   **   ~~~   ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
   **   ~~~   ** ...that is, these surfaces will have conditions as though at ground level.
   **  Fatal  ** Fatal error discovered in GetSurfaceData, see previous messages
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=22
   ..... Last severe error=GetSurfaceData: Potential "OtherZoneSurface" is not matched correctly:
   ************* Fatal error -- final processing.  More error messages may appear.
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ************* No node connection errors were found.
   *************
   ************* ===== Final Error Summary =====
   ************* The following error categories occurred.  Consider correcting or noting.
   ************* Incorrect Floor Tilt
   ************* ..Floors are usually flat and "tilted" 180 degrees.  If you get this error message,
   ************* ..it's likely that you need to reverse the vertices of your floor.  You can turn on
   ************* ..the report: Report,Surface,Details; to inspect your surfaces.
   *************
   ************* EnergyPlus Terminated--Fatal Error Detected. 34 Warning; 22 Severe Errors; Elapsed Time=00hr 00min 37.88sec

-------------------end of copied information------------

I am not interested in getting help for the rest warnings/errors. Thank you again for the replies

Regards

Eleni



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/