Re: [EnergyPlus_Support] Fatal Error on CFT Withoun having any CFT
The idf file that you sent had different layers defined for construction
= "EXOTERIKOS_M5" compared to what is shown in the severe error message
that you provided:
Construction,
exoterikos_m5, !- Name
epixrisma, !- Outside Layer
toublo_9cm, !- Layer 2
petrombambakas_5cm, !- Layer 3
toublo_9cm, !- Layer 4
epixrisma; !- Layer 5
Regardless, material layer "epixrisma" is 1 meter thick.... is that
really what you want?
As the error message says:
** ~~~ ** The potential causes of this problem are related to the input for the construction
** ~~~ ** listed in the severe error above. The CTF calculate routine is unable to come up
** ~~~ ** with a series of CTF terms that have a reasonable time step and this indicates an
** ~~~ ** error. Check the definition of this construction and the materials that make up
** ~~~ ** the construction. Very thin, highly conductive materials may cause problems.
** ~~~ ** This may be avoided by ignoring the presence of those materials since they probably
** ~~~ ** do not effect the heat transfer characteristics of the construction. Highly
** ~~~ ** conductive or highly resistive layers that are alternated with high mass layers
** ~~~ ** may also result in problems.
kostas ordoumpozanis wrote:
> HI I am modeling a simple 3zone building with the use of openstudio and sketchup. i have create the geometry and the materials,constructions e.t.c., and when i am running the energyplus (not inside the openstudio) i got an error about CTF, without having any CFT data in my input file.
>
> "Severe ** CTF calculation convergence problem for Construction="EXOTERIKOS_M5".
> ** ~~~ ** ...with Materials (outside layer to inside)
> ** ~~~ ** (outside)="EPIXRISMA"
> ** ~~~ ** (next)="PETROMBAMBAKAS_5CM"
> ** ~~~ ** (next)="XPS_5CM"
> ** ~~~ ** (next)="TOUBLO_9CM"
> ** ~~~ ** (inside)="ELAFROSKIRODEMA_30CM"
> ** ~~~ ** Request Output:Report:Construction or Output:Construction to see more information on Constructions.
> ** ~~~ ** The potential causes of this problem are related to the input for the construction
> ** ~~~ ** listed in the severe error above. The CTF calculate routine is unable to come up
> ** ~~~ ** with a series of CTF terms that have a reasonable time step and this indicates an
> ** ~~~ ** error. Check the definition of this construction and the materials that make up
> ** ~~~ ** the construction. Very thin, highly conductive materials may cause problems.
> ** ~~~ ** This may be avoided by ignoring the presence of those materials since they probably
> ** ~~~ ** do not effect the heat transfer characteristics of the construction. Highly
> ** ~~~ ** conductive or highly resistive layers that are alternated with high mass layers
> ** ~~~ ** may also result in problems. After confirming that the input is correct and
> ** ~~~ ** realistic, the user should contact the EnergyPlus support team."
>
> i upload and the idf to check it,
>
> anyone have seen this again (version 3.1)
>
> Kindly regards
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/