To develop the parameters for Coil:Cooling:DX:SingleSpeed, you need to obtain performance data for capacity and electric power consumption either from the coil manufacturer or from measurements. Then you need to curve fit the data using the equation form(s) shown in the EnergyPlus Engineering Reference (search for "Single-Speed Electric DX Air Cooling Coil"). There are various example files located in the \ExampleFiles folder which also contain the object Coil:Cooling:DX:SingleSpeed and its associated Curve: objects. You can review these input examples, and maybe use the inputs from these examples to get you started. However, it is best to use performance data for your specific coil to generate the required curve fit inputs for you EnergyPlus simulation. Fabio Augusto Carezia wrote: Hello all __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.