Hi Jia, EnergyPlus calculates glare index by dividing the window into Nx by Ny rectangular elements and integrating the results. Look at the Daylight Discomfort Glare section of the Engineering Manual for description of the calculation procedures. By splitting a large window into small pieces, I expect to see different glare index calculated. To further identify the potential issues, you can make a few more parametric runs by splitting the large window into 2, 5, and 10 small ones, then look at the glare results to see any pattern. Tianzhen On 10/28/2009 12:03 PM, Hu,Jia wrote:
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.