[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: CV AHU and Secondary FCU in Zone
Hi Guys
I've attempted to get a single zone model working. I've taken a single zone model with HVACTemplate:Zone:Fancoil already in place This is generated from designbuilder but taken from it's runtime folder (if you export using the prescribed method it runs ExpandObjects by default).
I've added HVACTemplate:Zone:VAV and HVACTemplate:System:VAV.
Upon running E+ it returns the error:
** Severe ** Sizing:Zone Name, duplicate name=16
Is there anything obvious that could be going wrong. Could I have applied the Templates incorrectly? Or, do I need to mess around with the Sizing:* objects?
Best regards
Chris
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Alan Jackson" <alanjackson7@...> wrote:
>
> Richard
>
> This is excellent. I got it working for a single zone model! I will
> attempt to take the same ideas into the larger model I have, only
> about 10 zones so shouldn't be too difficult. The one thing that
> through me for a loop was setting up a NodeList for the Supply Inlet
> to the Zone since when the connections were expanded both the FCU and
> the outlet from the VAV had the same name for the Supply to the Zone.
> Assuming i did this correctly because i received 0 warnings.
>
> The help was greatly appreciated.
>
> Does anyone see any reason why I shouldnt be using a VAV terminal to
> simulate a CAV even though I have damper min at 1.0 it acts the same,
> yes? Didn't know if there was any advantage to the other CV terminals.
>
> Thanks again!!
>
> -
> aj
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, RRaustad@ wrote:
> >
> > I believe both the airloop VAV system and zone FCU have templates that
> > will expand the connections for you. The VAV system and FCU will each
> > have their own zone inlet node. The VAV system will connect to the
> > zone through the RA node and the FCU will connect through a zone
> > exhaust node.
> >
> > You are on the right track. Again, set this up for a single zone and
> > get it working first. If you have other questions and need for use to
> > look at the input file, it's much easier for us to review a one-zone
> > model.
> >
> > Quoting Alan Jackson <alanjackson7@>:
> >
> > > Couple of questions because I am running into some issues. The first
> > > is can all this be done with the HVAC templates and if so which ones?
> > >
> > > The way I have started is to set up a HVACTemplate:Zone:VAV and
> > > System:VAV and set all the minimum and maximums the same and have no
> > > turndown on the VAV. This was my understanding on how to get a CAV
> > > system from the template. Is this right? should i be using
> > > AirTerminal:SingleDuct:ConstantVolume:Reheat or Uncontrolled instead?
> > >
> > > Then I am going into the expanded idf and trying to add a
> > > ZoneHVAC:FourPipeFanCoil manually, but there are object parameters for
> > > outdoor air which i don't have because it is just recirculating the
> > > zone air. Also it seems like the outlet from the VAV/CAV is the same
> > > node as the outlet for the fan coil, which is the zone inlet. I
> > > thought zones could have only one air inlet and outlet
> > >
> > > Can you see where I am going with this. Looking for a little more
> > > direction.
> > >
> > > I do appreciate the help
> > >
> > > -
> > > aj
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> > > <RRaustad@> wrote:
> > >>
> > >> You can have both. Start with a 1 zone model first. Autosizing the
> > >> equipment will size each to meet the total zone load, so after the
> > > first
> > >> run, manually size the systems as appropriate for your application.
> > >>
> > >> Alan Jackson wrote:
> > >> >
> > >> > Sorry to bring this up again but did not get any response the
> initial
> > >> > go around. I would like to model a CV air system supplying
> ventilation
> > >> > and cooling to a zone that also has perimeter recirculation console
> > >> > FCUs. Do I need to have a seperate perimeter zone just for the
> FCUs or
> > >> > can I have both CV and FCU in the same zone using direct air or
> > >> > something like that.
> > >> >
> > >> > I just don't want to go back and have to add perimeter zones after
> > >> > finding out it doesn't work, otherwise i would just attempt it
> myself.
> > >> >
> > >> > thanks in advance
> > >> >
> > >> > -
> > >> > aj
> > >> >
> > >> >
> > >>
> > >> --
> > >> Richard A. Raustad
> > >> Senior Research Engineer
> > >> Florida Solar Energy Center
> > >> University of Central Florida
> > >> 1679 Clearlake Road
> > >> Cocoa, FL 32922-5703
> > >> Phone: (321) 638-1454
> > >> Fax: (321) 638-1439 or 1010
> > >> Visit our web site at: http://www.fsec.ucf.edu
> > >>
> > >> UCF - From Promise to Prominence: Celebrating 40 Years
> > >>
> > >
> > >
> > >
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/