Re: [EnergyPlus_Support] Constant volume, constant temperature
First report the node set point temperature so you can be sure it is
accurate. Second, if you are using the AirloopHVAC:UnitaryHeatCool
object (which is controlled by zone load), change to the
AirloopHVAC:CoolOnly (which can be controlled with a set point manager).
Andrew wrote:
>
> Hi all,
>
> I am trying to build a model for a multi-residential system where
> every room is served by two systems:
>
> 1) Centralised constant volume, constant temperature AHU for outdoor
> air requirements
> 2) Fan coil unit in each room to deal with space loads.
>
> I have setup the system in E+, but my final issue is with control. My
> SetpointManager:Scheduled that controls the off-coil temperature seems
> to be overwritten by the loads requirements of the zone. How do I fix
> the temperature of the air supply branch to be constant and not
> respond to zone loads?
>
> Cheers
> Andrew
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/