[EnergyPlus_Support] Re: U-Value Calculation



exactly..

ok, this looks really like a case of 'not seeing the forest for the trees' .. 

turns out that I had a typo, the thickness of the gypsum varies about one decimal power... that explains everything..

thanks anyway...




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> As I remember you add up the individual R values for each layer and 
> take the inverse.  When you do that you come up with .735
> 
> Output:Constructions, Constructions, Materials;
> 
> Will put it in the .eio file.
> 
> At 03:03 PM 11/20/2009, tobias.leibing wrote:
> >Hey there,
> >
> >I have some problems with the U-value calculation of 
> >EnergyPlus.  For some reason the by EnergyPlus calculated U-values 
> >are not correct.
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/