Re: [EnergyPlus_Support] OA Pretreat



Please look at the example file 5ZoneAirCooled.idf.  The cooling coil 
will be part of the AirLoopHVAC:OutdoorAirSystem.
It will need to be included in the 
AirLoopHVAC:OutdoorAirSystem:EquipmentList. In addition to the setpoint 
manager, you
will need a Controller:WaterCoil, which should be referenced in the 
AirLoopHVAC:ControllerList for the outdoor air
system.

Fred Buhl

On 11/25/2009 12:22 PM, grandocu wrote:
> Hello All,
>
> I am trying to model an outside air system that pretreats the air to 72 degrees F and 50% RH.  I see that I can create a setpoint manager for pretreating but I am unsure how it knows which cooling coil it applies to.  I have a fan coil in the zone to take care of internal gains, but where in the .idf do I tell which cooling coil is pretreating the air?  Are there any examples files for this?  Thank you.
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/