[EnergyPlus_Support] Re: Zone Simulation



Designbuilder does make things easy in this respect. But, if you're stuck with an IDF you need to:

In a nutshell:
- Delete all the objects exclusive to the zone including the zone itself.
- Edit the references to the deleted zones in other objects.

This could involve the following:
- Delete child surfaces (BuildingSurface:Detailed) of the deleted zones and Fenestration surfaces that are children of these surfaces. 
- Edit the "Surface" or "Zone" boundary condition of surfaces adjacent to the deleted zone to "Adiabatic"
- Delete zone internal gains
- "Simple" Zone ventilation - delete
- Natural ventilation objects - delete
- Delete zone HVAC objects (if you're working with HVAC Templates rather than an expanded IDF this will be easier.) These should consist of Thermostats and ZoneHVAC. 

Hint, if your IDF has a good naming structure that allows to keep track of child/ parent relationships between objects (e.g. surface/ zone respectively or fenestrationSurface/ BuildingSurface respectively) this helps. Take a little time to understand the parent/ child links going on in the file. Work it out on paper. It may be better to start with removal of child objects because they are more numerous leaving the zone till last.

If you're working with expanded IDF's there will a plethora of extra HVAC objects. (e.g. Fans, coils, airloops, controllers). Again, delete the objects exclusive to the zone and edit objects that contain references to the zone. In this case branches, zone splitter/ mixer objects and maybe nodelists will have references to the dead zone(s). Delete references to the Zone in these objects but not the object itself.

This is very rough and correct me somebody if I'm wrong!

The .err file when you run E+ is quite verbose and gives you a lot of clues as to what's going wrong.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Phylroy" <phylroy.lopez@...> wrote:
>
> DesignBuilder has a feature that apparently makes it easier. 
> 
> http://www.designbuilder.co.uk/helpv2/Content/IncludeZone.htm
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Vinay Devanathan <vinay.devanathan@> wrote:
> >
> > Thanks for your suggestions, I think I have a better idea now.
> > 
> > On Mon, Dec 7, 2009 at 12:31 PM, Fred Buhl <wfbuhl@> wrote:
> > 
> > >
> > >
> > > It would be useful but might be tricky to implement. Some how walls between
> > > zones
> > > would have to be made adiabatic. Then there are interior windows ...
> > >
> > > Fred
> > >
> > >
> > > On 12/7/2009 9:14 AM, Fred Buhl wrote:
> > >
> > > I can't think of a way to not simulate zones that are included in an
> > > EnergyPlus input file. It
> > > is easy enough to turn condioned zones into unconditioned zones, but not to
> > > eliminate any
> > > kind of simulation. You'll have to edit your file to include only the zones
> > > you want
> > > to simulate.
> > >
> > > Fred Buhl
> > >
> > > On 12/4/2009 5:52 PM, Vinay Devanathan wrote:
> > >
> > > Hi,
> > >
> > > I want to simulate just a part of zones in a building, so I would like to
> > > know is it possible to just simulate a part of the building or should i just
> > > break down my model in the zones of interest and then simulate.
> > >
> > > Thank you.
> > >
> > >
> > >   
> > >
> >
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/