[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] losses in plant loop??



Hey there,

I have a model with a central chiller plant serving the water cooling coils of eleven AHUs.

For an electricity breakdown I wanted to separate the total chiller electric consumption up into the cooling coils to reflect the cooling electricity demand of each AHU.
I did this by using the ratio of total cooling energy of each coil (Total Water Cooling Coil Energy) and the total chiller cooling energy (Chiller Evap Heat Trans) and assigned this ratio to the total chiller electricity consumption (Chiller Electric Consumption).
In doing so I discovered a deviation in the cooling energy of about 7% between the chiller cooling energy and the sum of the water cooling coils energy.

I was not able to explain this difference and was hoping somebody in this group can help me out or might have experienced the same thing as well.

Thanks,
Tobias




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/