[EnergyPlus_Support] Re: Regarding the Roof Reflectivity



Vigneshkumar,

I would interpet this as such:
Your base reflectance should be .30 and your modeled reflectance should be .45 for the life of the roof. 

It looks like this prevents you from using a modeled reflectance of .70 because the .70 will degrade over time and won't truly be representative.  

Lori Jore, PE 
Pro-Tec Energy
www.Pro-TecEnergy.com

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, vignesh kumar <vigneshkumar1986@...> wrote:
>
>  *Hi  Could any one clarify this :*
> **
> **
> *"By default, exterior roof surfaces, other than those with ventilated
> attics, must be modeled assuming a surface reflectance  **value of 0.30.
> When a proposed design calls for a reflective roof surface, however, the
> model may assume a long-term  **average reflectance of 0.45, which credits
> the lower heat absorption of the reflective surface and makes a conservative
> **allowance for degradation of the reflectivity over its lifetime. In order
> to qualify for this credit, the reflectance of **the proposed design roof
> must exceed 0.70, and its emittance must exceed 0.75. "*
> **
> *So does this mean , if my proposed case roof has a higher roof
> reflectivity  than 0.70 and higher emmitance than 0.75 ,means ** my base
> case roof reflectivity should be 0.45 , if it is the case then my there will
> be reduction in my savings of the proposed case with the base case , then
> how will this becomes a credit *
> **
> *Thanks and Regards*
> vigneshkumar
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/