Re: [EnergyPlus_Support] Fan Power Pressures and Efficiencies - Are the calculations based on Pstat or Pt
Total pressure.
Ptotal = Pstatic + Pdynamic
Ptotal = Pstatic + 1/2 * rhoV^2
jeannieboef wrote:
>
> Are the calculations based on total pressure or static pressure rise?
>
> Field: Supply Fan Total Efficiency
> Enter the total efficiency of the supply fan. This is the ratio of the
> power delivered to the air to
> the electrical input power at maximum flow. This is also the product
> of the fan motor
> efficiency and fan (impeller) efficiency. The motor efficiency is the
> power delivered to the
> shaft divided by the electrical power input to the motor. The fan
> efficiency is the power
> delivered to the air divided by the shaft power. The power delivered
> to the fluid is the mass
> flow rate of the air multiplied by the pressure rise divided by the
> air density. Must be greater
> than 0 and less than or equal to 1. The default is 0.7.
>
> Field: Supply Fan Delta Pressure
> Enter the pressure rise in Pa at full flow and standard conditions.
> Standard conditions are
> considered 20o C at sea level, 101325 Pa. The default is 1000 Pa.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/