|
This sort of thing is usually caused by a
mismatch between the parameters used in Sizing:* objects and how the systems
actually run during operation. The HVAC controls need to be consistent
with the Sizing inputs. For example, check that the node temperatures on
the supply deck agree with what is used in the Sizing:Zone design supply air
temperature. From: Hello everyone, I am simulating an office building with
VAV with Reheat. I am getting a large number of unmet cooling load hours. The
heating is fine. I am running it for TIME COOLING SETPOINT NOT MET {HOURS
NON-ZERO} [HOURS] I am using autosize options. My
understanding was that it I use autosize options, the
systems would be sized to meet the loads. How should I
diagnose this - i.e. which parameters to look at etc.. I help will be very much appreciated. John __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |