[EnergyPlus_Support] SetpointManager: which node is controlled?
Hello,
I am trying to simulate the simplest plant, a hot water boiler + bypass pipe attached to a load profile.
I set the water flow to split in two halves, 0.5 kg/s through the boiler, 0.5 kg/s through the bypass (have a look at the SVG).
Then I asked SetpointManager to keep the water in the Supply Outlet Node @ 60°C. I expected then that the boiler should heat the water up to about 80°C, in order to reach 60°C after mixing with the cold bypass flow.
What I find, instead, is that the node kept at 60°C is the Boiler Outlet, so that after the mixer the water gets too cold. How this? Where is the mistake?
Please find the idf input file here:
http://f1.grp.yahoofs.com/v1/oA5gS4k7UXMGATeBTsQfbIFe9MCow521F-gzv1KhCTViz8_oSLHLwJwvrTnTkOMMbCzW5-kzZ2X-LIKs74Pl5FJY53xpK7fU/_Problem_Submittals/profilo_caldaia%2Btubo.idf
many thanks
alessandro
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/