The minimum and maximum PLR specifies how you want your chiller to
operate, usually these are set to 0 and 1, respectively, but the minimum
may be set higher than 0 if necessary. The optimum PLR is the point
where you get the highest efficiency, the optimum PLR is used when the
plant is optimally controlled (see PlantLoop input for Load Distribution
Scheme). The optimum PLR is also more important for plants with multiple
chillers.
As for your performance curves, EnergyPlus does not have standard curves
for absorption chillers. You must use the manufacturers data to create
these curves. This is done using regression analysis on a large data set
and is based on the specific equations used for each performance curve.
There is an example for how to do this on the Yahoo site under
Files/Examples. Excel Biquadratic Fit.zip shows the methodology using
the LineST function. You will have to adapt this methodology to the
absorption chiller equations. Alternatively, if you have the add-in for
Excel, the regression analysis is found under the Tools menu for Data
Analysis.
Paulo Jose Schiavon Ara wrote:
> Hello,
> I'm trying to define the absorption chiller for my simulation other
> them the absorption chiller presented in the example file.
> When looking for the chiller parameters among the absorption chillers
> catalogs, I'm not finding the parameters needed for EnergyPlus
> simulation such as Part Load Ratio (Minimum, Maximum and Optimum),
> Generator Steam Input Curve, etc.
> I would like to know if is it possible to find this data in other
> sources or if is there a way to estimate these parameters by myself
> based on the data about COP, temperatures and flow rate which I can
> obtain from catalogs.
> Thank you very much,
> Paulo Ara.
>
> ------------------------------------------------------------------------
> Veja quais são os assuntos do momento no Yahoo! + Buscados: Top 10
> <http://br.rd.yahoo.com/mail/taglines/mail/*http://br.maisbuscados.yahoo.com/>
> - Celebridades
> <http://br.rd.yahoo.com/mail/taglines/mail/*http://br.maisbuscados.yahoo.com/celebridades/>
> - Música
> <http://br.rd.yahoo.com/mail/taglines/mail/*http://br.maisbuscados.yahoo.com/m%C3%BAsica/>
> - Esportes
> <http://br.rd.yahoo.com/mail/taglines/mail/*http://br.maisbuscados.yahoo.com/esportes/>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/