Re: [EnergyPlus_Support] A large number of cooling unmet load hours



The Zone:Sizing and System:Sizing objects are used to input information 
concerning sizing. Review these inputs carefully.

The advice was to compare these values with values calculated during the 
simulation.

Such as:

Output:Variable,"The name of the supply air node",Zone/Sys Air 
Temperature,Hourly;
Output:Variable,"The name of the supply air node",Zone Air Humidity 
Ratio,Hourly;

where: "The name of the supply air node" is the node name you gave as 
the outlet of the main AC duct, or cooling coil outlet node, etc.

john_lee68@xxxxxxxxxxx wrote:
>  
> I am still looking for the response...
> Thanks,
> John..
> ----- Original Message -----
> From: "john lee68" <john_lee68@xxxxxxxxxxx>
> To: "EnergyPlus Support" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Wednesday, January 27, 2010 5:45:55 PM GMT -05:00 US/Canada Eastern
> Subject: Re: [EnergyPlus_Support] A large number of cooling unmet load 
> hours
>
> Thank you Brent for your quick response. Which input (or output) 
> variable, are you referring to? If it is output variable then how can 
> I make sure that  these two temperatures are not different. 
>
> thanks again...
> John
>
> ----- Original Message -----
> From: "Brent Griffith" <brent.griffith@xxxxxxxx>
> To: "EnergyPlus Support" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> Sent: Tues  
>
> This sort of thing is usually caused by a mismatch between the 
> parameters used in Sizing:* objects and how the systems actually run 
> during operation.  The HVAC controls need to be consistent with the 
> Sizing inputs.  For example, check that the node temperatures on the 
> supply deck agree with what is used in the Sizing:Zone design supply 
> air temperature.
>
>  
>
> ------------------------------------------------------------------------
>
> *From:* EnergyPlus_Support@xxxxxxxxxxxxxxx 
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] *On Behalf Of 
> *john_lee68@xxxxxxxxxxx
> *Sent:* Tuesday, January 26, 2010 3:48 PM
> *To:* EnergyPlus Support
> *Subject:* [EnergyPlus_Support] A large number of cooling unmet load hours
>
>  
>
>  
>
> Hello everyone,
>
> I am simulating an office building with VAV with Reheat. I am getting 
> a large number of unmet cooling load hours. The heating is fine. I am 
> running it for Chicago weather. 
>
> TIME COOLING SETPOINT NOT MET {HOURS NON-ZERO} [HOURS]
>
>  
>
> I am using autosize options. My understanding was that it I use 
> autosize options, the systems would be sized to meet the loads. 
> How should I diagnose this - i.e. which parameters to look at etc..
>
>  
>
> I help will be very much appreciated...
>
> John
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/