Emanuele, WINDOW 6.2 and THERM 6.2 actually can model shading devices of
the three general types: -
Venetian blinds -
Frits -
Woven shades Your system is closest to woven shades type, as the woven shades
are modeled as a grid of vertical and horizontal weaves. While it is true
that woven shades algorithm for diffuse part is developed for denser weave than
you have, it is also true that diffuse portion is very small and will not
significantly affect your results. I would encourage you to try to model your system with WINDOW
6.2/THERM 6.2, because results will be much more accurate than any
approximation and rule of thumb that you may use otherwise. D. Charlie Curcija From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of Emanuele Naboni Hello Edward, Yes, the grid is on the outside, the open area factor could
varies from 44% to 66% as a function of the final product installed. Surely the grid has an impact as a wind shelter so that the
wind coefficient will be effected (I hope to find the way to use a reliable
coefficient without CFD calculations). Playing with WIS I have now that is possible to model this
case too. Thanks for the advices, Emanuele On Thu, Feb 11, 2010 at 1:40 PM, Edward G. Lyon <eglyon@xxxxxxx> wrote: Sounds like your
grid is on the outside and casts a shadow on the window. A fair
approximation is to calculate the glazing alone using Window. Adjust the
exterior wind coefficient if you think the grid creates some shelter for the
window. The grid is just a net free area that limits the % of sun light that
reaches the glass. Most of your light transmittance properties are simply
the % of calculated values. Things can be more complex if the grid is
almost opaque, and you may need to use CFD for air movement and calculate
grid/glass reflections separately. Having the grid
inboard of the glass is also more complicated because of reflections and
absorption that are not as simple as just shading the glass from the outside. Ned Lyon,
P.E. (MA) SIMPSON GUMPERTZ
& HEGER From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Emanuele Naboni Dear All, Does any of you have an idea on what software tools could be
used to calculate thermal and optical
transmission properties (e.g., thermal transmittance, total solar energy
transmittance) of a complex window system based on the ISO 15099:2003 method? The system that I am trying to
study is composed by a double pane glass protected by a vertical metal grid
which is 750mm (2' 6") detached from the window. From
my understanding neither Window 6.2 nor WIS are able to model this
system to describe thermal transmittance, total solar energy
transmittance, visible transmittance, etc.. Is there any suggestion? Thank
you so much for any possible help. Regards, Emanuele --
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image001112.gif
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00221.gif