LBNL spreadsheet should use the word emissivity, not
emittance. Technically emittance is related to the energy emission from the
whole body (volumetric), while emissivity is related to surface emission of
energy. In this case, we are clearly talking about surface emission.
Otherwise, there is no other difference between the two. They are both in
far IR (FIR) portion of the spectrum. It is also important to remember that formula 1 = absorptance +
reflectance + transmittance applies to single wavelength only, but it is
commonly applied to average of the portion of the spectrum, so in the solar
portion of the spectrum (UV+VIS+NIR) this is considered as acceptable, and for
opaque surfaces absorptance = 1 – reflectance. In FIR, same formula
stands, however we are not interested in absorptance in FIR, but emissivity, however
emissivity is equal to absorptance (or better yet absorptivity). Emissivity
is commonly measured using portable emissometers, which gives emissivity
directly as a result of measurement or FIR spectrophotometers, where
transmittance and reflectance are measured and emissivity is calculated from
emissivity = 1 – reflectance. Charlie -------------------------------------------------------------------
From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of csimmons290
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |