Report the zone temperatures and make sure heating is actually needed. 
If not, try changing to a colder climate or reduce the heating design 
day outdoor temperature. If heating is required in your run, send your 
input file to:

energyplus-support@xxxxxxxx

Vinay Devanathan wrote:
>
> Hello,
>
> I ran simulations and obtained this warning -
>
> The design coil load is zero for
>
> Coil:Heating:Water HEATING COIL. The autosize value for maximum water 
> flow rate is zero. To change this, input a value for UA, change the 
> heating design day, or lower the system heating design supply air 
> temperature
>
> I have lowered the design heating supply air temperature, but it is of 
> no use. Could anyone please tell me how to rectify this problem.
>
> Thank you.
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/