Re: [EnergyPlus_Support] Compatibility between air system objects



Yes, it is possible to set up an air loop (which uses AirTerminal:* 
objects) and zone equipment (e.g., PTAC and 4PipeFanCoils). See the 
example file ZoneWSHP_wDOAS for an example of an air loop used with zone 
equipment. This is a very simple example file, where there are no 
components in the air loop (but you could add them) and only a single 
piece of zone equipment (you could have more and add additional zones if 
you like). Just reconfigure the air loop as you need and choose the zone 
equipment you would want. Take note of the ZoneHVAC:EquipmentConnections 
object on how to describe multiple exhaust/inlet nodes for a single 
zone. Also, only 1 air loop (AirloopHVAC) is allowed per zone (but can 
serve multiple zones) and connects between a zone return node and a zone 
inlet node. The zone equipment (ZoneHVAC - e.g., PTAC) connects between 
a zone exhaust node and a zone inlet node.


Maria Fernandez wrote:
>
> Hi,
>
> Is it possible to use at the same time, in the zone equipment, a VAV 
> system (AirTerminal:SingleDuct:VAV:HeatandCool:NoReheat) and a 
> ZoneHVAC:PackagedTerminalAirConditioner? I haven’t get that it works, 
> although I got it with “AirTerminal:SingleDuct:Uncontrolled”. My 
> problem is I want to simulate free-cooling and I think to that I need 
> a VAV system, doesn’t it?
>
> In the same way, is it possible to use at the same time 
> “AirTerminal:SingleDuct:VAV:HeatandCool:NoReheat” and 
> “ZoneHVAC:FourPipeFancoil” objects?
>
> Thanks in advance,
>
> María Fernández
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/