Dear Kwang,

thanks a lot for your advices. I did actually use AirflowNetwork object to represent air exchanges between the office, the chimney and outside. Another user advices me to represent the chimney with 2 separated zone to compute the right pressure at each opening level. Do you think this type of discretisation will be efficent?

In the end, do you think the airflow networtk approach is better than the thermalchimney object? or the contrary? or equivalent?

Best Regards,
Aymeric

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Kwang Ho Lee" <kwhlee@...> wrote:
>
>  Dear Aymeric,
> 
>  Yes, you need to use Zone:ThermalChimney object to simulate what you want
> to model. Just simply adding a zone adjacent to the office without using
> Zone:ThermalChimney object won't induce the natural ventilation that you
> would expect unless you separately use AirflowNetwork objects.
> 
>  What Zone:ThermalChimney does is to compute the amount of heat that is
> aborbed into the thermal chimney air after taking into account all the
> detailed heat balances taking place inside the thermal chimney zone. And
> then it calculates the outlet discharge air temperature through the upper
> opening and the enhanced natural ventilation caused by the thermal
> gradient within the thermal chimney.
> 
>  You can also refer to the recently published paper entitled "Enhancement
> of natural ventilation in buildings using a thermal chimney". It is on
> the thermal chimney model of EnergyPlus.
> 
>  Regards,
> 
>  Kwang
> 
> 
> > Dear all,
> >
> > I am struggeling to know whether or not I did simulate properly a solar
> > chimney. It is in Jerusalem climate.
> > I first modelled a zone adjacent to the office I want to cool down. I
> > positionned a low opening on the partition wall separating the two zones.
> > This wall is of course composed by a structural part, here concrete, 2.5cm
> > polyurethan board insulation and a black selective metal plate. The outer
> > wall of the chimney is a glazed wall with an upper opening.
> >
> > Although it seems to work logically, it doesn't match experimental
> > results. Basically it seems it doesn't enhance enough the natural
> > ventilation...
> >
> > Using this method, I certainly don't take into account the temperature
> > gradient within the thermal chimney, right? Is it more reliable to use the
> > object Zone:ThermalChimney?
> >
> > Plus, an additional problem I can't explain is that I get some massflow
> > through ceilings although I do not activate infiltration calculations...
> >
> > If anyone has experience modelling thermal chimney, I would be happy to
> > know more about that!
> >
> > Thanks a million
> > Aymeric
> >
> >
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/