Re: [EnergyPlus_Support] about SimulationControl





Sizing calculations are done using SizingPeriod objects (SizingPeriod:DesignDay or the SizingPeriod:Weather file selections).

If you also want to run those sizing period and look at results (before you do an entire annual simulation), then you would put Yes in that slot.

At 02:04 AM 4/30/2010, Xavier Garcia Casals wrote:


Hi,
I would like to clarify one point about the SimulationControl object:
If the following SimulationControl is specified, and the IDF has several SizingPeriod:DesignDay objects (WinterDesignDay & SummerDesignDay), are the sizing calculations done with the weather file without using the SizingPeriod:DesignDay objects, or are the sizing calculations done using the SizingPeriod:DesignDay objects and therefore overriding the 'NO,  !- Run Simulation for Sizing Periods' statement?
Thanks,


SimulationControl,
    YES,                     !- Do Zone Sizing Calculation
    YES,                     !- Do System Sizing Calculation
    YES,                     !- Do Plant Sizing Calculation
    NO,                     !- Run Simulation for Sizing Periods
    YES;                    !- Run Simulation for Weather File Run Periods



--

Xavier GarcĂ­a
Casals


__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___