Re: [EnergyPlus_Support] Heat exchanger doubt
I don't think that will work. I have tried several times to "split" the
HX into different air paths with no success. If you must be creative you
have to remember one thing, the HX type and name and the supply
inlet/outlet nodes of the HX must be defined on a branch or outside air
system so that the HX model can be "called" (i.e., simulated). Review
the example files using this HX object to get an idea of this concept.
The secondary side may be placed as needed, with caution, and certainly
with post-simulation verification of operation (i.e., check to see if it
is working correctly by reporting node temps and flow rates). When the
supply side is simulation, so will the secondary side so air flow must
be available on the secondary side.
jordi cipriano wrote:
> I would like to connect, trhough ist outlet node, one zone (ZONE 1),
> to a heat hexchanger and then, connect the heat hexchanger outlet to
> an inlet node of another zone (ZONE 2). The return air from the ZONE
> 2, after an HVAC loop, should be connected to the Heat exchanger
> secondary inlet node. Is it possible to do it?
> In other words, can I substitute the outside air inlet node of a heat
> exchanger by the outlet of the ZONE 1?
>
> Many thanks,
>
> Jordi
> --
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/