[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] solar combisystem
Energyplus does not yet have HVACTemplates for all equipment types. For
those equipment that cannot be configured using HVACTemplate, you must
run the simulation first without the solar collectors. When you run this
simulation the HVACTemplates will be "expanded" into actual EnergyPlus
objects. Then copy the *.expidf file to a new name.idf. Then edit this
file and add the solar collector loop "by hand", meaning to add the
solar collector objects and associated plant loop objects to the new
name.idf.file.
jduverge1979 wrote:
>
> i'm in the process of simulating a solar combisystem on a house?
> i have already connected my hot water solar system. i just need to
> split the hot water to a hot water baseboard. I'm using hvactemplate
> HVACTemplate:Zone PTAC with gas heat. i was told from energyplus to
> use hot water baseboard (which you can add using HVACTemplate and then
> merge with the solar collectors by hand) or low temp radiant hydronic
> heat (which you would add by hand.) What does it mean to add by hand.
> can you help me please?
>
> regards
> Jonathan
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/