Re: [EnergyPlus_Support] Re: Low Temperature Radiant System





Thanks so much.
I think I locate the source of my problem now. My ventilation air is treated to satisfy the whole zone's heating load nothing left to radiant system. (Meanwhile according to E+ documentation radiant systems can only be controlled at priority # 2 which means as a secondary system). I have AHUs serving each floor of the building having several thermal zones. I'll have to work on AHUs to adjust zone loads.
My radiant system is variable flow. AHUs have variablevolume fans.
Do you mean radiant heating set-points temps are 1C cooler than zone heating-setpoints?
thanks.

Omer T. Karaguzel PhD Candidate
Center for Building Performance & Diagnostics (CBPD)
Carnegie Mellon University Pittsburgh, PA 15213


--- On Mon, 7/5/10, M�¡rio <mneves32@xxxxxxxxx> wrote:

From: M�¡rio <mneves32@xxxxxxxxx>
Subject: [EnergyPlus_Support] Re: Low Temperature Radiant System
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Monday, July 5, 2010, 5:31 PM

 

Hello.

First, could it be that you ventilation air witch, usualy is treted is suficient to overcome your Load?

Second is it a variable or constante flow system, you used the direct duct object, is your fan constante volume?

Have you tried to setpoint the air tempreture about 1ºC colder than your space, if everything else is OK the radiant system has to be activated.

Best Regards

MN

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "O. Tugrul Karaguzel" <tugrulkaraguzel@...> wrote:
>
> Hi there,
> In my model zone ventilation is supplied by AHU as well as load function. I also realized that ventilation should be separated from air conditioning so as to couple radiant system. Can it be done by changing parameters of the heating coil of the central system since there should be some sort of pre-heating of outdoor air to be used for ventilation purposes?
> Best.
>
> Omer T. Karaguzel PhD Candidate
>
> Center for Building Performance & Diagnostics (CBPD)
>
> Carnegie Mellon University
> Ã? Pittsburgh, PA 15213
>
> --- On Mon, 7/5/10, MÃ?Æ?Ã?¡rio <mneves32@...> wrote:
>
> From: MÃ?Æ?Ã?¡rio <mneves32@...>
> Subject: [EnergyPlus_Support] Re: Low Temperature Radiant System
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Date: Monday, July 5, 2010, 5:04 PM
>
>
>
>
>
>
>
> Ã? 
>
>
>
>
>
>
>
>
>
> Hello
>
>
>
> What is the AHU set for, load or ventilation functions?
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "O. Tugrul Karaguzel" <tugrulkaraguzel@> wrote:
>
> >
>
> > Hi,
>
> > In my Energy Plus model, I have a low temp (hydronic) radiant system and a single duct uncontrolled air terminal (connected to an AHU with a heating & cooling coil) serving the same thermal zone. I want the radiant system to be the main heating component and any remaining zone loads to be met by the other equipment. So as to do this, I already defined heating priority # 1 to radiant heating system and # 2 to single duct air terminal. However, my simulation results show that radiant system is not operating at all and all the zone loads are still met by air terminal units. How can I reverse this operation? Is there any other settings that can successfully couple these two systems?
>
> > Thanks in Advance.
>
> >
>
> > Omer T. Karaguzel PhD Candidate
>
> > Center for Building Performance & Diagnostics (CBPD)
>
> > Carnegie Mellon University
>
> > Pittsburgh, PA 15213
>
> >
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___