Rowan, A variable refrigerant system operates much the same way, it
sounds. I recently modeled a VRF by using the same approach as used in the
example file I cited, making the Boiler’s efficiency = 1.0 and the
Chiller’s COP = 1000 (so no compressor heat was added). For
post-processing: ·
I reported Boiler and Chiller energy ·
The loop in that example file operates such that only one of
those is active since the loop always reflects the composite energy of the
entire system ·
Using the VRF manufacturer part load information, I calculated
the electrical energy (in Excel) that would be used to satisfy the Boiler /
Chiller load Your system may well operate differently, since it sounds as
though you can simultaneously heat and cool. In that case, you’ll
need separate heating and cooling loops, but you may be able to do something
similar…. Good luck! The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of rowan.blakers Hello James, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |