|
Dear Vinay, ASHRAE 90.1-2007 specifies Baseline system fan power in Table G3.1.2.9.
For VAV systems, also use Table G3.1.3.15 for part load performance. A sample
object for the VAV fan is shown below. For all baseline fans, I made a spreadsheet which, based on
anticipated motor and fan efficiency, calculates the pressure rise which will
result in the correct ASHRAE 90.1 fan power. Remember that E+, when
asking for “fan efficiency”, really wants (Fan mechanical efficiency
x Motor efficiency). For example, if the fan mechanical efficiency
= .60 and motor efficiency = .90, the E+ “fan efficiency” = .54.
The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay
Devanathan Alan, On Tue, Jun 29, 2010 at 11:33 AM,
Jackson, Alan <ajackson@xxxxxxxxxxxxxxxxx>
wrote: You're going to want to adjust
your Static Pressure DeltaP. Once you
------------------------------------
Yahoo! Groups Links __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |