Re: [EnergyPlus_Support] How do I correct these errors?





It's pretty clear (I did not run your file):

   ** Severe  ** SetpointManager:SingleZone:Reheat, Zone not found=ZN_1_FLR_1_SEC_1, for Set Point Manager=SUPAIRTEMP MNGRZN_1_FLR_1_SEC_1


Your set point manager SUPAIRTEMP MNGRZN_1_FLR_1_SEC_1

referenced zone ZN_1_FLR_1_SEC_1 and there is no zone named

ZN_1_FLR_1_SEC_1

It appears you only have one zone here and it's named "Retail Space"

At 02:52 PM 7/20/2010, matt youngblood wrote:


I am new to the program and am trying to simulate a single zone retail shopping space and I have been repeatedly getting error messages which I have attached in this email along with my .idf file.  If anyone can clarify how to remedy these errors that would be greatly appreciated because I have tried personally to fix these but have reached a point that I have no clue what I am doing.  Any help would be greatly appreciated.
 
Matt Youngblood







__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___