[EnergyPlus_Support] Node errors



I get the following errors after simulating my idf file:

 ************* Beginning Plant Sizing Calculations
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
** Node Connection Error, Node="HOT WATER BOILER INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=BRANCH, Name=HOT WATER BOILER BRANCH
   ** Severe  ** Node Connection Error, Node="BASEBOARD1(1) INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=BRANCH, Name=ZONE 1(1) BRANCH
   ** Severe  ** Node Connection Error, Node="BASEBOARD1(2) INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=BRANCH, Name=ZONE 1(2) BRANCH
   ** Severe  ** Node Connection Error, Node="BASEBOARD1(1) INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=ZONEHVAC:BASEBOARD:CONVECTIVE:WATER, Name=BASEBOARD1(1)
   ** Severe  ** Node Connection Error, Node="BASEBOARD1(2) INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=ZONEHVAC:BASEBOARD:CONVECTIVE:WATER, Name=BASEBOARD1(2)
   ** Severe  ** Node Connection Error, Node="HOT WATER BOILER INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
   **   ~~~   ** Reference Object=BOILER:HOTWATER, Name=HOT WATER BOILER
   ************* There were 6 node connection errors noted.
   ************* Beginning Simulation
   ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at Volos GR TMY2-3045 WMO#=, 01/01 00:00 - 00:03
   **   ~~~   ** SimFlags=[TTTFFFFF] AirLoops[T],ZoneEq[T],NonZoneEq[T],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
   **   ~~~   ** HVAC Tolerance Flags=[0000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
   **   ~~~   ** HVAC Tolerance Values, Most Recent listed first
   **   ~~~   ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
   **   ~~~   ** Plant Tolerance Values, Most Recent listed first
   **   ~~~   ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
   **   ~~~   **      FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
   **   ~~~   ** Plant side outlet node=[10 - BASEBOARD1(2) OUTLET NODE]
   **   ~~~   ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
   **   ~~~   **      FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
   **   ~~~   ** Plant side outlet node=[10 - BASEBOARD1(2) OUTLET NODE]
   **   ~~~   ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
   **   ~~~   **      FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
   **   ~~~   ** Plant side outlet node=[10 - BASEBOARD1(2) OUTLET NODE]
   **   ~~~   ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
   **   ~~~   **      FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
   **   ~~~   ** Plant side outlet node=[10 - BASEBOARD1(2) OUTLET NODE]
   **   ~~~   ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
   **   ~~~   **      FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
   **   ~~~   ** Plant side outlet node=[10 - BASEBOARD1(2) OUTLET NODE]
   **   ~~~   ** Plant Flow Tolerance Values, Most Recent listed first
   **   ~~~   ** PlantFlowFlowTol=0.000
   **   ~~~   ** PlantFlowFlowTol=0.000
   **   ~~~   ** PlantFlowFlowTol=0.000
   **   ~~~   ** PlantFlowFlowTol=0.000
   **   ~~~   ** PlantFlowFlowTol=0.000

I am guessing the node errors are to blame for the tolerance failures afterwards. But i cannot understand what i am doing wrong (first time user of E+). Any help in solving my problem will be greatly appreciated.

!-   ===========  ALL OBJECTS IN CLASS: SIZING:ZONE ===========

Sizing:Zone,
    Thermal_B,               !- Zone Name
    12,                      !- Zone Cooling Design Supply Air Temperature {C}
    50,                      !- Zone Heating Design Supply Air Temperature {C}
    0.008,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    Flow/Person,             !- Outdoor Air Method
    0.00944,                 !- Outdoor Air Flow per Person {m3/s}
    0,                       !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
    0,                       !- Outdoor Air Flow per Zone {m3/s}
    ,                        !- Zone Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    ,                        !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Cooling Minimum Air Flow {m3/s}
    ,                        !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    ,                        !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Heating Maximum Air Flow {m3/s}
    0.3;                     !- Heating Maximum Air Flow Fraction

Sizing:Zone,
    Thermal_11,              !- Zone Name
    12,                      !- Zone Cooling Design Supply Air Temperature {C}
    50,                      !- Zone Heating Design Supply Air Temperature {C}
    0.008,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    Flow/Person,             !- Outdoor Air Method
    0.00944,                 !- Outdoor Air Flow per Person {m3/s}
    ,                        !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Outdoor Air Flow per Zone {m3/s}
    ,                        !- Zone Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    ,                        !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Cooling Minimum Air Flow {m3/s}
    ,                        !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    ,                        !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Heating Maximum Air Flow {m3/s}
    0.3;                     !- Heating Maximum Air Flow Fraction

Sizing:Zone,
    Thermal_12,              !- Zone Name
    12,                      !- Zone Cooling Design Supply Air Temperature {C}
    50,                      !- Zone Heating Design Supply Air Temperature {C}
    0.008,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    0.008,                   !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    Flow/Person,             !- Outdoor Air Method
    0.00944,                 !- Outdoor Air Flow per Person {m3/s}
    ,                        !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Outdoor Air Flow per Zone {m3/s}
    ,                        !- Zone Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    ,                        !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Cooling Minimum Air Flow {m3/s}
    ,                        !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    ,                        !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Heating Maximum Air Flow {m3/s}
    0.3;                     !- Heating Maximum Air Flow Fraction


!-   ===========  ALL OBJECTS IN CLASS: SIZING:PLANT ===========

Sizing:Plant,
    Hot Water Loop,          !- Plant or Condenser Loop Name
    Heating,                 !- Loop Type
    82,                      !- Design Loop Exit Temperature {C}
    11;                      !- Loop Design Temperature Difference {deltaC}


!-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========

ZoneControl:Thermostat,
    Zone B Thermostat,       !- Name
    Thermal_B,               !- Zone Name
    Zone Control Type Sch,   !- Control Type Schedule Name
    ThermostatSetpoint:SingleHeating,  !- Control 1 Object Type
    Zone B HS;               !- Control 1 Name

ZoneControl:Thermostat,
    Zone 1(1) Thermostat,    !- Name
    Thermal_11,              !- Zone Name
    Zone Control Type Sch,   !- Control Type Schedule Name
    ThermostatSetpoint:SingleHeating,  !- Control 1 Object Type
    Zone 1(1&2);             !- Control 1 Name

ZoneControl:Thermostat,
    Zone 1(2) Thermostat,    !- Name
    Thermal_12,              !- Zone Name
    Zone Control Type Sch,   !- Control Type Schedule Name
    ThermostatSetpoint:SingleHeating,  !- Control 1 Object Type
    Zone 1(1&2);             !- Control 1 Name


!-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLEHEATING ===========

ThermostatSetpoint:SingleHeating,
    Zone B HS,               !- Name
    Heating Setpoint B Shc;  !- Setpoint Temperature Schedule Name

ThermostatSetpoint:SingleHeating,
    Zone 1(1&2),             !- Name
    Heating Setpoint 01(1)1(2) Sch;  !- Setpoint Temperature Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:BASEBOARD:CONVECTIVE:WATER ===========

ZoneHVAC:Baseboard:Convective:Water,
    BaseboardB,              !- Name
    HWL Operation Sch,       !- Availability Schedule Name
    BaseboardB Inlet Node,   !- Inlet Node Name
    BaseboardB Outlet Node,  !- Outlet Node Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    0.001;                   !- Convergence Tolerance

ZoneHVAC:Baseboard:Convective:Water,
    Baseboard1(1),           !- Name
    HWL Operation Sch,       !- Availability Schedule Name
    Baseboard1(1) Inlet Node,!- Inlet Node Name
    Baseboard1(1) Outlet Node,  !- Outlet Node Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    0.001;                   !- Convergence Tolerance

ZoneHVAC:Baseboard:Convective:Water,
    Baseboard1(2),           !- Name
    HWL Operation Sch,       !- Availability Schedule Name
    Baseboard1(2) Inlet Node,!- Inlet Node Name
    Baseboard1(2) Outlet Node,  !- Outlet Node Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    0.001;                   !- Convergence Tolerance


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========

ZoneHVAC:EquipmentList,
    Zone B Equipment,        !- Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Zone Equipment 1 Object Type
    BaseboardB,              !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Zone 1(1) Equipment,     !- Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Zone Equipment 1 Object Type
    Baseboard1(1),           !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Zone 1(2) Equipment,     !- Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Zone Equipment 1 Object Type
    Baseboard1(2),           !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========

ZoneHVAC:EquipmentConnections,
    Thermal_B,               !- Zone Name
    Zone B Equipment,        !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    B Air Node,              !- Zone Air Node Name
    B Return Air Node;       !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Thermal_11,              !- Zone Name
    Zone 1(1) Equipment,     !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    1(1) Air Node,           !- Zone Air Node Name
    1(1) Return Air Node;    !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Thermal_12,              !- Zone Name
    Zone 1(2) Equipment,     !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    1(2) Air Node,           !- Zone Air Node Name
    1(2) Return Air Node;    !- Zone Return Air Node Name


!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========

Branch,
    Pump Branch,             !- Name
    autosize,                !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pump:VariableSpeed,      !- Component 1 Object Type
    Pump,                    !- Component 1 Name
    Pump Inlet Node,         !- Component 1 Inlet Node Name
    Pump Outlet Node,        !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Hot Water Boiler Branch, !- Name
    autosize,                !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Boiler:HotWater,         !- Component 1 Object Type
    Hot Water Boiler,        !- Component 1 Name
    Hot Water Boiler Inlet Node,  !- Component 1 Inlet Node Name
    Hot Water Boiler Outlet Node,  !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Zone B Branch,           !- Name
    autosize,                !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Component 1 Object Type
    BaseboardB,              !- Component 1 Name
    BaseboardB Inlet Node,   !- Component 1 Inlet Node Name
    BaseboardB Outlet Node,  !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Zone 1(1) Branch,        !- Name
    autosize,                !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Component 1 Object Type
    Baseboard1(1),           !- Component 1 Name
    Baseboard1(1) Inlet Node,!- Component 1 Inlet Node Name
    Baseboard1(1) Outlet Node,  !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Zone 1(2) Branch,        !- Name
    autosize,                !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Component 1 Object Type
    Baseboard1(2),           !- Component 1 Name
    Baseboard1(2) Inlet Node,!- Component 1 Inlet Node Name
    Baseboard1(2) Outlet Node,  !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type


!-   ===========  ALL OBJECTS IN CLASS: BRANCHLIST ===========

BranchList,
    HWL Supply Branch,       !- Name
    Pump Branch,             !- Branch 1 Name
    Hot Water Boiler Branch; !- Branch 2 Name

BranchList,
    HWL Demand Branch,       !- Name
    Zone B Branch,           !- Branch 1 Name
    Zone 1(1) Branch,        !- Branch 2 Name
    Zone 1(2) Branch;        !- Branch 3 Name


!-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========

Pump:VariableSpeed,
    Pump,                    !- Name
    Pump Inlet Node,         !- Inlet Node Name
    Pump Outlet Node,        !- Outlet Node Name
    autosize,                !- Rated Flow Rate {m3/s}
    179352,                  !- Rated Pump Head {Pa}
    autosize,                !- Rated Power Consumption {W}
    0.9,                     !- Motor Efficiency
    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
    0,                       !- Coefficient 1 of the Part Load Performance Curve
    1,                       !- Coefficient 2 of the Part Load Performance Curve
    0,                       !- Coefficient 3 of the Part Load Performance Curve
    0,                       !- Coefficient 4 of the Part Load Performance Curve
    0,                       !- Minimum Flow Rate {m3/s}
    Continuous;              !- Pump Control Type


!-   ===========  ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========

Boiler:HotWater,
    Hot Water Boiler,        !- Name
    Diesel,                  !- Fuel Type
    autosize,                !- Nominal Capacity {W}
    0.9,                     !- Nominal Thermal Efficiency
    ,                        !- Normalized Boiler Efficiency Curve Name
    75,                      !- Design Water Outlet Temperature {C}
    autosize,                !- Design Water Flow Rate {m3/s}
    ,                        !- Minimum Part Load Ratio
    1,                       !- Maximum Part Load Ratio
    1,                       !- Optimum Part Load Ratio
    Hot Water Boiler Inlet Node,  !- Boiler Water Inlet Node Name
    Hot Water Boiler Outlet Node,  !- Boiler Water Outlet Node Name
    99,                      !- Water Outlet Upper Temperature Limit {C}
    VariableFlow;            !- Boiler Flow Mode


!-   ===========  ALL OBJECTS IN CLASS: PLANTLOOP ===========

PlantLoop,
    Hot Water Loop,          !- Name
    Water,                   !- Fluid Type
    Hot Water Loop Operation,!- Plant Equipment Operation Scheme Name
    Hot Water Boiler Outlet Node,  !- Loop Temperature Setpoint Node Name
    100,                     !- Maximum Loop Temperature {C}
    10,                      !- Minimum Loop Temperature {C}
    autosize,                !- Maximum Loop Flow Rate {m3/s}
    0,                       !- Minimum Loop Flow Rate {m3/s}
    autocalculate,           !- Plant Loop Volume {m3}
    Pump Inlet Node,         !- Plant Side Inlet Node Name
    Hot Water Boiler Outlet Node,  !- Plant Side Outlet Node Name
    HWL Supply Branch,       !- Plant Side Branch List Name
    ,                        !- Plant Side Connector List Name
    BaseboardB Inlet Node,   !- Demand Side Inlet Node Name
    Baseboard1(2) Outlet Node,  !- Demand Side Outlet Node Name
    HWL Demand Branch,       !- Demand Side Branch List Name
    ,                        !- Demand Side Connector List Name
    Optimal,                 !- Load Distribution Scheme
    ,                        !- Availability Manager List Name
    SingleSetpoint,          !- Plant Loop Demand Calculation Scheme
    None,                    !- Common Pipe Simulation
    None;                    !- Pressure Simulation Type


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========

PlantEquipmentList,
    Heating Plant,           !- Name
    Boiler:HotWater,         !- Equipment 1 Object Type
    Hot Water Boiler;        !- Equipment 1 Name


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:HEATINGLOAD ===========

PlantEquipmentOperation:HeatingLoad,
    Hot Water Boiler,        !- Name
    0,                       !- Load Range 1 Lower Limit {W}
    10000,                   !- Load Range 1 Upper Limit {W}
    Heating Plant;           !- Priority Control 1 Equipment List Name


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES ===========

PlantEquipmentOperationSchemes,
    Hot Water Loop Operation,!- Name
    PlantEquipmentOperation:HeatingLoad,  !- Control Scheme 1 Object Type
    Hot Water Boiler,        !- Control Scheme 1 Name
    HWL Operation Sch;       !- Control Scheme 1 Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========

SetpointManager:Scheduled,
    Hot Water Loop Setpoint Manager,  !- Name
    Temperature,             !- Control Variable
    HWL Temperature Sch,     !- Schedule Name
    Hot Water Boiler Outlet Node;  !- Setpoint Node or NodeList Name



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/