An object Pump:ConstantSpeed (Flow Rate: autosize) is used for the HW
loop. The object Boiler:HotWater has a variable flow mode. I am not sure
if this variable flow inflicts the HW loop or is just an internal aspect
of the boiler.

The model is run in E+ v.4.0.0.024.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Are you using a variable-speed or constant-speed pump?
>
> avdbree wrote:
> >
> > I am investigating an existing building. The idea is to add
insulation
> > and keep the existing baseboards. So, the (new) heating can work
with
> > a lower supply temperature.
> >
> > When I autosize maximum (water) flow rates and/or UA-factors in the
> > objects ZoneHVAC:Baseboard:Convective:Water, Boiler:HotWater and
> > PlantLoop, I get a Delta T of the HW-loop up to 15 °K (which is
fine).
> >
> > Then I set myself maximum water flow rates for the baseboards (based
> > on the maximum heating rates from a simulation), while keeping the
> > flows of Boiler:HotWater and PlantLoop autosized. Delta T of the
> > HW-loop dropped to about 3 °K (which is to small). The results
for the
> > Zone Mean Air Temperatures and Baseboard Heating Rates are still
fine
> > (and similar to the autosized situation). Apparently, the flow in
the
> > HW-loop is quite big now and most of the flow during most of the
time
> > is going through the bypass on the demand-side of the HW-loop. This
> > increases the return temperature and decreases Delta T. A small
Delta
> > T is not economic.
> >
> > The occuring maximum loop flow in the HW-loop is exactly the sum of
> > all maximum water flows of all the baseboards (as specified in the
> > object ZoneHVAC:Baseboard:Convective:Water). So, I tried to set
myself
> > a lower Maximum Loop Flow Rate of the Plant:Loop (in order to lower
> > the bypassed flow and thus increasing Delta T). I choose the maximum
> > sum of all the baseboards water flows AT ANY GIVEN MOMENT. This
> > maximum is -- in my case-- less then half of the sum of all
> > (non-simultaneously) maximum water flows. And, by the way, about
twice
> > as much as for the completely autosized situation.
> >
> > But even when I manually set the Maximum Loop Flow Rate of the
> > Plant:Loop, the occuring flow in the HW-loop is still the (much
> > higher) sum of all (non-simultaneously) maximum flows of all
baseboards.
> >
> > Did I forgot to change another object too or is this a bug?
> >
> > PS. I tried to attach the idf-file but could not find the way to do
this.
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/