[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] G3.1.2.8 Design Airflow Rates - Sizing:System





Dear Jeannie,

 

Room temp setpoint - Central cooling design supply air temperature = 11.1C

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef
Sent: Tuesday, August 31, 2010 7:31 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] G3.1.2.8 Design Airflow Rates - Sizing:System

 

 

I'm required to size my system so that the "System design supply airflow rates for the baseline building design shall be based on a supply-air-to-room-air temperature difference of 11°C or the required ventilation air or makeup air, whichever is greater."

I'm looking at:
Sizing:System,
118129 AHU, !- AirLoop Name
Sensible, !- Type of Load to Size On
autosize, !- Design (minimum) outside air volumetric flow rate {m3/s}
1, !- Minimum System Air Flow Ratio
7, !- Preheat design set temperature {C}
0.008, !- Preheat design humidity ratio {kg-H2O/kg-air}
11, !- Precool design temperature {C}
0.008, !- Precool design humidity ratio {kg-H2O/kg-air}
12, !- Central cooling design supply air temperature {C}
50, !- Central heating design supply air temperature {C}
NonCoincident, !- Sizing Option
No, !- 100% Outdoor Air in Cooling
No, !- 100% Outdoor Air in Heating
0.008, !- Central cooling design supply air humidity ratio {kg-H2O/kg-air}
0.008, !- Central heating design supply air humidity ratio {kg-H2O/kg-air}
DesignDay, !- Cooling Design Air Flow Method
0, !- cooling design air flow rate {m3/s}
DesignDay, !- Heating Design Air Flow Method
0; !- heating design air flow rate {m3/s}

Should I specify the design air delivery temperature so that it differs from the design day outdoor dry bulb temperature by 11°?



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___