[EnergyPlus_Support] Re: Custom Weather Files - Radiation
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Custom Weather Files - Radiation
- From: "hollywas" <hollywas@xxxxxxxxx>
- Date: Tue, 05 Oct 2010 22:14:11 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 05 Oct 2010 16:14:26 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1286316866; bh=dMOUcwfcLlHmkPGFOsXRHr2V1lcytsbDy9rdfsuaq9I=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=Otzaze+rrrcMwlkdLx7JBqKTgcrZck5Xdlf/lO8QxceU9+aZ4MxWq5ZxXYCSr+j5SkazP5400MURg16j4a2+f97WMjoIPgsDBN+X8D9YKe9KsRfXYBdTSmXwlWmlLvs+
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=CBa3oItaTXmZbRUZLGjG3Q/jSlkZKO5I9+PscXDqzDd84bX/oK4y6d9YMWDCJcMu+YbHV3BfaJf1bMDVPbEKgAegrKio9IHW9s0Sjh9xSzdbzFP/gKncaGPK0XDdJNaF;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Hi Linda,
Thank you for both replies. Could you possibly elaborate on the view factor calculations making E+ crash?
The complex models will run fine with a standard EPW. And the homemade EPW will run fine with a simple model. However combining the two causes fatal errors.
I know that the fatal errors occur when E+ "doesn't like" the radiation data, but I can't figure out what the specific parameter is that makes it crash. The problem seems to be a large delta in radiation data between timesteps, but it doesn't seem to be consistent.
Thank you for your time.
Holly
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> The weather converter can use the Global horizontal and calculate the
> direct and diffuse based on the Zhang-Huang correlation. It also
> will calculation the Horizontal IR from Sky (using the equation that
> is in the Auxiliary Programs document).
>
> The complexity of geometry may have problems in the view factor
> calculations -- we have worked on that problem for the next release.
>
> At 03:58 PM 10/4/2010, hollywas wrote:
> >Hello,
> >I am trying to make a custom EPW from an on-site weather
> >station. Strangely, the EPW will run successfully when paired with
> >a simple IDF, such as one of the EnergyPlus example files. However,
> >with a more complex model it will fail on certain timesteps. The
> >more zones the model contains, the more timesteps will cause fatal
> >errors... even when modeling the same building. The error message
> >says surface temperatures are out of range. It seems to fail at
> >timesteps when there is a large change in the direct and/or diffuse
> >radiation data. If I manually replace this radiation data, the
> >simulation will run successfully through this timestep.
> >
> >Do you have any idea why the complexity of the geometry would affect
> >the success of the EPW? Do you have any advice on fixing this
> >besides manually replacing the radiation data at every failing timestep?
> >
> >FYI, The Direct Normal and Diffuse Horiz Radiation are calculated
> >from measured Global Horiz Radiation. Horizontal Infrared Radiation
> >from Sky was not measured so I have tried different values
> >including: using TMY3 values and inputting the TMY3 average value
> >for each timestep. I also have one reference for how to model it,
> >but would appreciate any other advice.
> >
> >Thank you in advance for any help!
> >Sincerely,
> >Holly
> >
> >Holly W. Samuelson
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/