Hey

I am also currently pursuing research on PCM in the building envelope. You need to know the variation of heat capacity (Cp) of the PCM with temperature. Or at least Cp at solid phase, solid-liquid transition phase and liquid phase. You can try asking the manufacturer for these details, else if you have PCM sample, you can do a DSC (Differential Scanning Calorimetry) analysis to get Cp values. 

To your questions:
1. The PCM thermal conductivity (k) may vary with temperature. That field defines how k varies with temperature. This can also be found using DSC. If not you can take that value as 0. From my research simulation, increasing k value of PCM has insignificant effect on buildings. 

2. Specific Enthalpy = [Heat Capacity * Temperature]/mass 
Unit Check: J/kg = [( J/°C)*(°C)]/(kg)

The units can vary depending upon the DSC instrument. Basically, you will need a enthalpy curve as seen in 1st attachment. You can also read this interesting journal article: "Advanced Zone Simulation in Energyplus: Incorporation of Variable Properties and Phase Change Material (PCM) Capability" by C.O.Pedersen, Proceedings: Building Simulation 2007. 

Please let me know if you have further questions. 

Thanks
Karthik M, LEED GA, EIT
Masters Student
Mechanical Engineering, SEMTE
Vice-President, ASHRAE @ ASU
Arizona State University
kmurugan@xxxxxxx
Tempe, AZ, US




From: alterea_nrjplus <akerneur@xxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Wed, 13 October, 2010 7:28:28 AM
Subject: [EnergyPlus_Support] PCM in energyplus

 

Hi All,

I'd like to use in my project a PCM : ENERGAIN of Dupont
The material property is :

0.18, !- Conductivity {W/m-K}
855, !- Density {kg/m3}
4 140, !- Specific Heat {J/kg-K}

Latent heat storage capacity : 71 kJ/kg
Melt point : 21.7°C

I don't know how definate (with my material property above)the :
Field: Temperature Coefficient for Thermal Conductivity
Field Set: Temperature-Enthalpy
I try to understand with Input-Output Reference but i can't.
Can you help me
Thanks a lot




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\Enthalpy vs. Temp.pdf