[EnergyPlus_Support] Re: i get this type of error anyone has any idea what I am doing wrong?
I did that Clarice, before I created my schedules, I set up my schedule types and when I expanded the file like you told us to do. i found one more type created by the HvacTemplate
thanks
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Clarice Bleil de Souza <claricebleil@...> wrote:
>
> Hi Fernando,
>
> Start by setting up ScheduleTypeLimits objects for each different type of schedule you want to specify, for example type temperature with its limits for thermostat schedules, etc.
>
> Check all your compact schedules again to see if they refer to these type limits and run the simulation again. You should have less problems.
>
> Hope it helps,
>
> Clarice
>
>
> --- Em seg, 29/11/10, motabmx1 <motabmx1@...> escreveu:
>
> De: motabmx1 <motabmx1@...>
> Assunto: [EnergyPlus_Support] i get this type of error anyone has any idea what I am doing wrong?
> Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Data: Segunda-feira, 29 de Novembro de 2010, 10:30
>
>
>
>
>
>
>
> Â
>
>
>
>
>
>
>
>
>
> If anyone knows what I am doing wrong in any of this errors can please drop me a line to say how I can solve them
>
>
>
> many thanks
>
>
>
> Program Version,EnergyPlus 6.0.0.023, 29/11/2010 12:13,IDD_Version 6.0.0.023
>
> ** Warning ** No Timestep object found. Number of TimeSteps in Hour defaulted to 4.
>
> ** Warning ** No reporting elements have been requested. No simulation results produced.
>
> ** ~~~ ** ...Review requirements such as "Output:Table:SummaryReports", "Output:Table:Monthly", "Output:Variable", "Output:Meter" and others.
>
> ** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
>
> ** Warning ** World Coordinate System selected. Any non-zero Building/Zone North Axes or non-zero Zone Origins are ignored.
>
> ** ~~~ ** These may be used in daylighting reference point coordinate calculations but not in normal geometry inputs.
>
> ** Warning ** Distance between two vertices < .01, possibly coincident. for Surface=ADF1C2, in Zone=TOILET_CORRIDOR
>
> ** ~~~ ** Vertex [3]=(38.50,19.56,0.00)
>
> ** ~~~ ** Vertex [1]=(38.50,19.56,0.00)
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="PEOPLE_OFFICE_WEEKDAY_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_OFFICE_SCHEDULE_dy_1
>
> ** ~~~ ** ref Schedule:Compact="LIGHTS_OFFICE_SCHEDULE"
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_OFFICE_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=ELEC_EQUIP_OFFICE_SCHEDULE_dy_1
>
> ** ~~~ ** ref Schedule:Compact="ELEC_EQUIP_OFFICE_SCHEDULE"
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_OFFICE_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="ACTIVITY_OFFICE_SCH", Schedule Type Limits Name="ANYNUMBER" not found -- will not be validated
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="HEATING-SETPOINT-SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="VENTILATION_ HOURS_OF_OPERATION" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAYS
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_STORAGE_SCHEDULE_dy_1
>
> ** ~~~ ** ref Schedule:Compact="LIGHTS_STORAGE_SCHEDULE"
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_STORAGE_SCHEDULE_dy_2
>
> ** ~~~ ** ref Schedule:Compact="LIGHTS_STORAGE_SCHEDULE"
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_STORAGE_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_1
>
> ** ~~~ ** ref Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE"
>
> ** Severe ** ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_2
>
> ** ~~~ ** ref Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE"
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="LIGHTS_MEETING_ROOM_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_NON-OFFICE_AREAS_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="ELEC_EQUIP_MEETING_SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="HEATING-SETPOINT_NON_OFFICES-SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="COOLING-SETPOINT_NON_OFFICES-SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Warning ** ProcessScheduleInput: Schedule:Compact="COOLING-SETPOINT-SCHEDULE" has missing day types in Through=12/31
>
> ** ~~~ ** Last "For" field=FOR: SUNDAY
>
> ** ~~~ ** Missing day types="Holiday","SummerDesignDay","WinterDesignDay","CustomDay1","CustomDay2"
>
> ** ~~~ ** Missing day types will have 0.0 as Schedule Values
>
> ** Fatal ** ProcessScheduleInput: Preceding Errors cause termination.
>
> ...Summary of Errors that led to program termination:
>
> ..... Reference severe error count=6
>
> ..... Last severe error=ProcessScheduleInput: ProcessIntervalFields, Processing time fields, incomplete day detected, Schedule:Compact DaySchedule Fields=LIGHTS_MEETING_ROOM_SCHEDULE_dy_2
>
> ************* Fatal error -- final processing. More error messages may appear.
>
> ************* Testing Individual Branch Integrity
>
> ************* All Branches passed integrity testing
>
> ************* Testing Individual Supply Air Path Integrity
>
> ************* All Supply Air Paths passed integrity testing
>
> ************* Testing Individual Return Air Path Integrity
>
> ************* All Return Air Paths passed integrity testing
>
> ************* No node connection errors were found.
>
> ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
>
> ************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
>
> ************* EnergyPlus Terminated--Fatal Error Detected. 18 Warning; 6 Severe Errors; Elapsed Time=00hr 00min 3.14sec
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/