1) You have asked the program to do zone sizing calculations but you have not provided

it with the input (SizingZone objects) it needs to do the calculations. Perhaps you don't really
want the program to do zone sizing calculations; in which case alter your "Do Zone Sizing Calculation"
field in SimulationControl to "No".

2) Look at your GlobalGeometryRules input. You've chosen Coordinate System = World, but you have
included input elsewhere that is only used when  Coordinate System = Relative.

Fred Buhl

On Tue, Nov 30, 2010 at 7:08 PM, motabmx1 <motabmx1@xxxxxxxxx> wrote:
 

hi all

I've managed to sort all the severe errors out i still do not know what the following warning errors means if any one has an idea?

thanks

** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored.
** Warning ** World Coordinate System selected. Any non-zero Building/Zone North Axes or non-zero Zone Origins are ignored.
** ~~~ ** These may be used in daylighting reference point coordinate calculations but not in normal geometry inputs.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
************* There are 2 unused schedules in input.
************* Use Output:Diagnostics,DisplayUnusedSchedules; to see them.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors.
************* EnergyPlus Completed Successfully-- 3 Warning; 0 Severe Errors; Elapsed Time=00hr 02min 1.88sec





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___