Jackson,
 
Both unrealistically high setpoint and off supply fan are good approaches, why don't you also set schedules to 0 fractions, other than what you need for lights/equip?
 
 
---------------------------
Arpan Bakshi
YRG sustainability
 

On Mon, Dec 6, 2010 at 7:37 PM, Jackson Thach <jthach@xxxxxxxxx> wrote:
 

Hi all,

 

I?m running this .idf file to view how a house behaves during the summer if the a/c were to not turn on. To do this, I set the cooling setpoint to 200 degrees Celsius and the supply fan to always off, but the Table.csv file still shows that there is some electricity usage for Cooling. Does anyone have any idea where the electricity used is coming from?

 

Thanks in advance,

Jackson

 

 

!-Generator IDFEditor 1.38a

!-Option SortedOrder UseSpecialFormat ViewInIPunits

 

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.

!-      Use '!' comments if they need to be retained when using the IDFEditor.

 

 

!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========

 

Version,6.0.0;

 

!-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========

 

 

SimulationControl,

    Yes,                     !- Do Zone Sizing Calculation

    Yes,                     !- Do System Sizing Calculation

    Yes,                     !- Do Plant Sizing Calculation

    Yes,                     !- Run Simulation for Sizing Periods

    Yes;                     !- Run Simulation for Weather File Run Periods

 

 

!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========

 

Building,

    Climate Zone 4 CA 2206 ft²,  !- Name

    90.0,                    !- North Axis {deg}

    Urban,                   !- Terrain

    0.005,                   !- Loads Convergence Tolerance Value

    0.05,                    !- Temperature Convergence Tolerance Value {deltaC}

    FullExterior,            !- Solar Distribution

    50;                      !- Maximum Number of Warmup Days

 

 

!-   ===========  ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========

 

ShadowCalculation,

    20,                      !- Calculation Frequency

    200;                     !- Maximum Figures in Shadow Overlap Calculations

 

 

!-   ===========  ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========

 

SurfaceConvectionAlgorithm:Inside,TARP;

 

!-   ===========  ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE ===========

 

SurfaceConvectionAlgorithm:Outside,DOE-2;

 

!-   ===========  ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========

 

HeatBalanceAlgorithm,ConductionTransferFunction,200;

 

!-   ===========  ALL OBJECTS IN CLASS: ZONECAPACITANCEMULTIPLIER:RESEARCHSPECIAL ===========

 

ZoneCapacitanceMultiplier:ResearchSpecial,1,15,1;

 

!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP ===========

 

Timestep,4;

 

!-   ===========  ALL OBJECTS IN CLASS: CONVERGENCELIMITS ===========

 

 

ConvergenceLimits,

    15,                      !- Minimum System Timestep {minutes}

    20;                      !- Maximum HVAC Iterations

 

 

!-   ===========  ALL OBJECTS IN CLASS: SITE:LOCATION ===========

 

Site:Location,

    Climate Zone 4 CA,       !- Name

    37.40,                   !- Latitude {deg}

    -122.4,                  !- Longitude {deg}

    -7.0,                    !- Time Zone {hr}

    29.99232;                !- Elevation {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SIZINGPERIOD:WEATHERFILEDAYS ===========

 

SizingPeriod:WeatherFileDays,

   Heating DD,              !- Name

    12,                      !- Begin Month

    21,                      !- Begin Day of Month

    12,                      !- End Month

    21,                      !- End Day of Month

    Sunday,                  !- Day of Week for Start Day

    Yes,                     !- Use Weather File Daylight Saving Period

    No;                      !- Use Weather File Rain and Snow Indicators

 

SizingPeriod:WeatherFileDays,

    Cooling DD,              !- Name

    7,                       !- Begin Month

    18,                      !- Begin Day of Month

    7,                       !- End Month

    18,                      !- End Day of Month

    Sunday,                  !- Day of Week for Start Day

    Yes,                     !- Use Weather File Daylight Saving Period

    No;                      !- Use Weather File Rain and Snow Indicators

 

 

!-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========

 

RunPeriod,

    Climate Zone 4 CA 2206 ft²,  !- Name

    1,                       !- Begin Month

    1,                       !- Begin Day of Month

    12,                      !- End Month

    31,                      !- End Day of Month

    Sunday,                  !- Day of Week for Start Day

    No,                      !- Use Weather File Holidays and Special Days

    Yes,                     !- Use Weather File Daylight Saving Period

    No,                      !- Apply Weekend Holiday Rule

    Yes,                     !- Use Weather File Rain Indicators

    Yes;                     !- Use Weather File Snow Indicators

 

 

!-   ===========  ALL OBJECTS IN CLASS: RUNPERIODCONTROL:SPECIALDAYS ===========

 

RunPeriodControl:SpecialDays,

    MayVacation,             !- Name

    5/26,                    !- Start Date

    3,                       !- Duration {days}

    CustomDay1;              !- Special Day Type

 

RunPeriodControl:SpecialDays,

    AugVacation,             !- Name

    8/12,                    !- Start Date

    7,                       !- Duration {days}

    CustomDay1;              !- Special Day Type

 

RunPeriodControl:SpecialDays,

    DecVacation,             !- Name

    12/22,                   !- Start Date

    4,                       !- Duration {days}

    CustomDay1;              !- Special Day Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: RUNPERIODCONTROL:DAYLIGHTSAVINGTIME ===========

 

RunPeriodControl:DaylightSavingTime,

    April 2,                 !- Start Date

    October 28;              !- End Date

 

 

!-   ===========  ALL OBJECTS IN CLASS: SITE:WEATHERSTATION ===========

 

Site:WeatherStation,

    9.99744,                 !- Wind Sensor Height Above Ground {m}

    0.15,                    !- Wind Speed Profile Exponent

    269.99184,               !- Wind Speed Profile Boundary Layer Thickness {m}

    1.5;                     !- Air Temperature Sensor Height Above Ground {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SITE:HEIGHTVARIATION ===========

 

Site:HeightVariation,

    0.25,                    !- Wind Speed Profile Exponent

    358.4448,                !- Wind Speed Profile Boundary Layer Thickness {m}

    0.0065;                  !- Air Temperature Gradient Coefficient {K/m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========

 

Site:GroundTemperature:BuildingSurface,13.0727493553463,12.2399434257372,12.1732500873423,12.5684606525496,14.1550074290757,15.7341622569431,17.1032100908167,17.9704619003507,18.0441382163844,17.3387711297337,16.0046391160711,14.4739228347731;

 

!-   ===========  ALL OBJECTS IN CLASS: SITE:WATERMAINSTEMPERATURE ===========

 

 

Site:WaterMainsTemperature,

    Correlation,             !- Calculation Method

    ,                        !- Temperature Schedule Name

    14.9333333333333,        !- Annual Average Outdoor Air Temperature {C}

    10.8888888888889;        !- Maximum Difference In Monthly Average Outdoor Air Temperatures {deltaC}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========

 

ScheduleTypeLimits,

    Multiplier,              !- Name

    ,                        !- Lower Limit Value

    ,                        !- Upper Limit Value

    Continuous;              !- Numeric Type

 

ScheduleTypeLimits,

    Fraction,                !- Name

    0,                       !- Lower Limit Value

    1,                       !- Upper Limit Value

    Continuous;              !- Numeric Type

 

ScheduleTypeLimits,

    On/Off,                  !- Name

    0,                       !- Lower Limit Value

    1,                       !- Upper Limit Value

    Discrete;                !- Numeric Type

 

ScheduleTypeLimits,

    Temperature,             !- Name

    -60,                     !- Lower Limit Value

    200,                     !- Upper Limit Value

    Continuous;              !- Numeric Type

 

ScheduleTypeLimits,

    RelativeHumidity,        !- Name

    0,                       !- Lower Limit Value

    100,                     !- Upper Limit Value

    Continuous;              !- Numeric Type

 

ScheduleTypeLimits,

    AnyNumber;               !- Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:DAY:HOURLY ===========

 

Schedule:Day:Hourly,

    OccupancyDay,            !- Name

    Fraction,                !- Schedule Type Limits Name

    1.00000,                 !- Hour 1

    1.00000,                 !- Hour 2

    1.00000,                 !- Hour 3

    1.00000,                 !- Hour 4

    1.00000,                 !- Hour 5

    1.00000,                 !- Hour 6

    1.00000,                 !- Hour 7

    0.88310,                 !- Hour 8

    0.40861,                 !- Hour 9

    0.24189,                 !- Hour 10

    0.24189,                 !- Hour 11

    0.24189,                 !- Hour 12

    0.24189,                 !- Hour 13

    0.24189,                 !- Hour 14

    0.24189,                 !- Hour 15

    0.24189,                 !- Hour 16

    0.29498,                 !- Hour 17

    0.55310,                 !- Hour 18

    0.89693,                 !- Hour 19

    0.89693,                 !- Hour 20

    0.89693,                 !- Hour 21

    1.00000,                 !- Hour 22

    1.00000,                 !- Hour 23

    1.00000;                 !- Hour 24

 

Schedule:Day:Hourly,

    OccupancyVacationDay,    !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay1,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1127778,               !- Hour 2

    0.08055556,              !- Hour 3

    0.08055556,              !- Hour 4

    0.08055556,              !- Hour 5

    0.08055556,              !- Hour 6

    0.1852778,               !- Hour 7

    0.3786111,               !- Hour 8

    0.3625,                  !- Hour 9

    0.1852778,               !- Hour 10

    0.1530556,               !- Hour 11

    0.1530556,               !- Hour 12

    0.1530556,               !- Hour 13

    0.1530556,               !- Hour 14

    0.1611111,               !- Hour 15

    0.2013889,               !- Hour 16

    0.3383334,               !- Hour 17

    0.6283334,               !- Hour 18

    0.9344445,               !- Hour 19

    0.9908334,               !- Hour 20

    0.8538889,               !- Hour 21

    0.7169445,               !- Hour 22

    0.5397223,               !- Hour 23

    0.3705556;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay2,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1909822,               !- Hour 1

    0.1131746,               !- Hour 2

    0.07780755,              !- Hour 3

    0.07780755,              !- Hour 4

    0.07780755,              !- Hour 5

    0.08488096,              !- Hour 6

    0.1626885,               !- Hour 7

    0.325377,                !- Hour 8

    0.2900099,               !- Hour 9

    0.1414683,               !- Hour 10

    0.1131746,               !- Hour 11

    0.1131746,               !- Hour 12

    0.1131746,               !- Hour 13

    0.1131746,               !- Hour 14

    0.120248,                !- Hour 15

    0.1414683,               !- Hour 16

    0.2192758,               !- Hour 17

    0.4244048,               !- Hour 18

    0.7285616,               !- Hour 19

    0.9336905,               !- Hour 20

    0.8700298,               !- Hour 21

    0.7214881,               !- Hour 22

    0.5375794,               !- Hour 23

    0.3748909;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay3,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1911111,               !- Hour 1

    0.1134722,               !- Hour 2

    0.07763889,              !- Hour 3

    0.07763889,              !- Hour 4

    0.07763889,              !- Hour 5

    0.08361112,              !- Hour 6

    0.1313889,               !- Hour 7

    0.2329167,               !- Hour 8

    0.1851389,               !- Hour 9

    0.09555556,              !- Hour 10

    0.07763889,              !- Hour 11

    0.07763889,              !- Hour 12

    0.07763889,              !- Hour 13

    0.07763889,              !- Hour 14

    0.07763889,              !- Hour 15

    0.08958334,              !- Hour 16

    0.1373611,               !- Hour 17

    0.2747222,               !- Hour 18

    0.5315278,               !- Hour 19

    0.7943056,               !- Hour 20

    0.8540279,               !- Hour 21

    0.7166667,               !- Hour 22

    0.5375,                  !- Hour 23

    0.37625;                 !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay4,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1903056,               !- Hour 1

    0.1171111,               !- Hour 2

    0.07807408,              !- Hour 3

    0.07807408,              !- Hour 4

    0.07807408,              !- Hour 5

    0.08295371,              !- Hour 6

    0.1366296,               !- Hour 7

    0.2537408,               !- Hour 8

    0.2049445,               !- Hour 9

    0.0975926,               !- Hour 10

    0.07807408,              !- Hour 11

    0.07807408,              !- Hour 12

    0.07807408,              !- Hour 13

    0.07807408,              !- Hour 14

    0.07807408,              !- Hour 15

    0.07807408,              !- Hour 16

    0.08295371,              !- Hour 17

    0.1122315,               !- Hour 18

    0.2049445,               !- Hour 19

    0.4050093,               !- Hour 20

    0.6636297,               !- Hour 21

    0.7173056,               !- Hour 22

    0.5367593,               !- Hour 23

    0.3708519;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay5,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.190625,                !- Hour 1

    0.114375,                !- Hour 2

    0.07625,                 !- Hour 3

    0.07625,                 !- Hour 4

    0.07625,                 !- Hour 5

    0.08048612,              !- Hour 6

    0.114375,                !- Hour 7

    0.190625,                !- Hour 8

    0.1440278,               !- Hour 9

    0.07625,                 !- Hour 10

    0.06354167,              !- Hour 11

    0.06354167,              !- Hour 12

    0.06354167,              !- Hour 13

    0.06354167,              !- Hour 14

    0.06354167,              !- Hour 15

    0.06354167,              !- Hour 16

    0.06777778,              !- Hour 17

    0.08472223,              !- Hour 18

    0.1482639,               !- Hour 19

    0.2965278,               !- Hour 20

    0.5210417,               !- Hour 21

    0.6820139,               !- Hour 22

    0.5337501,               !- Hour 23

    0.3727778;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay6,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1894445,               !- Hour 1

    0.114456,                !- Hour 2

    0.07498843,              !- Hour 3

    0.07498843,              !- Hour 4

    0.07498843,              !- Hour 5

    0.07893519,              !- Hour 6

    0.1065625,               !- Hour 7

    0.1697107,               !- Hour 8

    0.1262963,               !- Hour 9

    0.07104167,              !- Hour 10

    0.06314816,              !- Hour 11

    0.05920139,              !- Hour 12

    0.05920139,              !- Hour 13

    0.05920139,              !- Hour 14

    0.05920139,              !- Hour 15

    0.06314816,              !- Hour 16

    0.06314816,              !- Hour 17

    0.07893519,              !- Hour 18

    0.1262963,               !- Hour 19

    0.2446991,               !- Hour 20

    0.4380903,               !- Hour 21

    0.6354283,               !- Hour 22

    0.5328125,               !- Hour 23

    0.3709954;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay7,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1168056,               !- Hour 2

    0.07652778,              !- Hour 3

    0.07652778,              !- Hour 4

    0.07652778,              !- Hour 5

    0.08055556,              !- Hour 6

    0.1127778,               !- Hour 7

    0.1852778,               !- Hour 8

    0.1409722,               !- Hour 9

    0.07652778,              !- Hour 10

    0.06444445,              !- Hour 11

    0.06444445,              !- Hour 12

    0.06444445,              !- Hour 13

    0.06444445,              !- Hour 14

    0.06444445,              !- Hour 15

    0.06444445,              !- Hour 16

    0.06847223,              !- Hour 17

    0.08055556,              !- Hour 18

    0.1288889,               !- Hour 19

    0.2456945,               !- Hour 20

    0.4430556,               !- Hour 21

    0.6404167,               !- Hour 22

    0.5356945,               !- Hour 23

    0.3705556;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay8,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1895833,               !- Hour 1

    0.1128472,               !- Hour 2

    0.07673611,              !- Hour 3

    0.07673611,              !- Hour 4

    0.07673611,              !- Hour 5

    0.08125,                 !- Hour 6

    0.1309028,               !- Hour 7

    0.2302084,               !- Hour 8

    0.1805556,               !- Hour 9

    0.09027778,              !- Hour 10

    0.07222223,              !- Hour 11

    0.07222223,              !- Hour 12

    0.07222223,              !- Hour 13

    0.07222223,              !- Hour 14

    0.07222223,              !- Hour 15

    0.07222223,              !- Hour 16

    0.07673611,              !- Hour 17

    0.09930556,              !- Hour 18

    0.1670139,               !- Hour 19

    0.325,                   !- Hour 20

    0.5552084,               !- Hour 21

    0.7131945,               !- Hour 22

    0.5326389,               !- Hour 23

    0.3701389;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay9,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1908796,               !- Hour 1

    0.1145278,               !- Hour 2

    0.07635186,              !- Hour 3

    0.07635186,              !- Hour 4

    0.07635186,              !- Hour 5

    0.08180556,              !- Hour 6

    0.1527037,               !- Hour 7

    0.2890463,               !- Hour 8

    0.239963,                !- Hour 9

    0.1199815,               !- Hour 10

    0.09271297,              !- Hour 11

    0.09271297,              !- Hour 12

    0.09271297,              !- Hour 13

    0.09271297,              !- Hour 14

    0.09271297,              !- Hour 15

    0.09271297,              !- Hour 16

    0.1036204,               !- Hour 17

    0.1527037,               !- Hour 18

    0.2835926,               !- Hour 19

    0.5181019,               !- Hour 20

    0.774426,                !- Hour 21

    0.7198889,               !- Hour 22

    0.5399167,               !- Hour 23

    0.3763056;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay10,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1893056,               !- Hour 1

    0.1175,                  !- Hour 2

    0.07833334,              !- Hour 3

    0.07833334,              !- Hour 4

    0.07833334,              !- Hour 5

    0.08486111,              !- Hour 6

    0.17625,                 !- Hour 7

    0.3590278,               !- Hour 8

    0.3198611,               !- Hour 9

    0.1566667,               !- Hour 10

    0.1240278,               !- Hour 11

    0.1240278,               !- Hour 12

    0.1240278,               !- Hour 13

    0.1240278,               !- Hour 14

    0.1240278,               !- Hour 15

    0.1305556,               !- Hour 16

    0.1631945,               !- Hour 17

    0.2676389,               !- Hour 18

    0.4895834,               !- Hour 19

    0.7702779,               !- Hour 20

    0.8486112,               !- Hour 21

    0.7115278,               !- Hour 22

    0.5352778,               !- Hour 23

    0.3720834;               !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay11,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.19375,                 !- Hour 1

    0.11625,                 !- Hour 2

    0.07750001,              !- Hour 3

    0.07750001,              !- Hour 4

    0.07750001,              !- Hour 5

    0.08525001,              !- Hour 6

    0.14725,                 !- Hour 7

    0.28675,                 !- Hour 8

    0.279,                   !- Hour 9

    0.155,                   !- Hour 10

    0.13175,                 !- Hour 11

    0.13175,                 !- Hour 12

    0.13175,                 !- Hour 13

    0.13175,                 !- Hour 14

    0.14725,                 !- Hour 15

    0.20925,                 !- Hour 16

    0.37975,                 !- Hour 17

    0.6742501,               !- Hour 18

    0.9222501,               !- Hour 19

    0.9222501,               !- Hour 20

    0.8525001,               !- Hour 21

    0.72075,                 !- Hour 22

    0.53475,                 !- Hour 23

    0.372;                   !- Hour 24

 

Schedule:Day:Hourly,

    InteriorLightingProfileDay12,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1916667,               !- Hour 1

    0.1166667,               !- Hour 2

    0.075,                   !- Hour 3

    0.075,                   !- Hour 4

    0.075,                   !- Hour 5

    0.08333334,              !- Hour 6

    0.175,                   !- Hour 7

    0.3583333,               !- Hour 8

    0.35,                    !- Hour 9

    0.1916667,               !- Hour 10

    0.1583333,               !- Hour 11

    0.1583333,               !- Hour 12

    0.1583333,               !- Hour 13

    0.1583333,               !- Hour 14

    0.175,                   !- Hour 15

    0.2416667,               !- Hour 16

    0.4333334,               !- Hour 17

    0.7583334,               !- Hour 18

    1,                       !- Hour 19

    0.9333334,               !- Hour 20

    0.8500001,               !- Hour 21

    0.7166667,               !- Hour 22

    0.5333334,               !- Hour 23

    0.375;                   !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay1,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1127778,               !- Hour 2

    0.08055555,              !- Hour 3

    0.08055555,              !- Hour 4

    0.08055555,              !- Hour 5

    0.08055555,              !- Hour 6

    0.1852778,               !- Hour 7

    0.3786111,               !- Hour 8

    0.3625,                  !- Hour 9

    0.1852778,               !- Hour 10

    0.1530555,               !- Hour 11

    0.1530555,               !- Hour 12

    0.1530555,               !- Hour 13

    0.1530555,               !- Hour 14

    0.1611111,               !- Hour 15

    0.2013889,               !- Hour 16

    0.3383333,               !- Hour 17

    0.6283333,               !- Hour 18

    0.9344444,               !- Hour 19

    0.9908333,               !- Hour 20

    0.8538889,               !- Hour 21

    0.7169444,               !- Hour 22

    0.5397222,               !- Hour 23

    0.3705555;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay2,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1909821,               !- Hour 1

    0.1131746,               !- Hour 2

    0.07780754,              !- Hour 3

    0.07780754,              !- Hour 4

    0.07780754,              !- Hour 5

    0.08488095,              !- Hour 6

    0.1626885,               !- Hour 7

    0.325377,                !- Hour 8

    0.2900099,               !- Hour 9

    0.1414683,               !- Hour 10

    0.1131746,               !- Hour 11

    0.1131746,               !- Hour 12

    0.1131746,               !- Hour 13

    0.1131746,               !- Hour 14

    0.120248,                !- Hour 15

    0.1414683,               !- Hour 16

    0.2192758,               !- Hour 17

    0.4244047,               !- Hour 18

    0.7285615,               !- Hour 19

    0.9336904,               !- Hour 20

    0.8700297,               !- Hour 21

    0.7214881,               !- Hour 22

    0.5375794,               !- Hour 23

    0.3748909;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay3,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1911111,               !- Hour 1

    0.1134722,               !- Hour 2

    0.07763889,              !- Hour 3

    0.07763889,              !- Hour 4

    0.07763889,              !- Hour 5

    0.08361111,              !- Hour 6

    0.1313889,               !- Hour 7

    0.2329167,               !- Hour 8

    0.1851389,               !- Hour 9

    0.09555555,              !- Hour 10

    0.07763889,              !- Hour 11

    0.07763889,              !- Hour 12

    0.07763889,              !- Hour 13

    0.07763889,              !- Hour 14

    0.07763889,              !- Hour 15

    0.08958333,              !- Hour 16

    0.1373611,               !- Hour 17

    0.2747222,               !- Hour 18

    0.5315278,               !- Hour 19

    0.7943055,               !- Hour 20

    0.8540277,               !- Hour 21

    0.7166666,               !- Hour 22

    0.5375,                  !- Hour 23

    0.37625;                 !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay4,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1903055,               !- Hour 1

    0.1171111,               !- Hour 2

    0.07807407,              !- Hour 3

    0.07807407,              !- Hour 4

    0.07807407,              !- Hour 5

    0.0829537,               !- Hour 6

    0.1366296,               !- Hour 7

    0.2537407,               !- Hour 8

    0.2049444,               !- Hour 9

    0.09759259,              !- Hour 10

    0.07807407,              !- Hour 11

    0.07807407,              !- Hour 12

    0.07807407,              !- Hour 13

    0.07807407,              !- Hour 14

    0.07807407,              !- Hour 15

    0.07807407,              !- Hour 16

    0.0829537,               !- Hour 17

    0.1122315,               !- Hour 18

    0.2049444,               !- Hour 19

    0.4050092,               !- Hour 20

    0.6636296,               !- Hour 21

    0.7173055,               !- Hour 22

    0.5367593,               !- Hour 23

    0.3708518;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay5,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.190625,                !- Hour 1

    0.114375,                !- Hour 2

    0.07624999,              !- Hour 3

    0.07624999,              !- Hour 4

    0.07624999,              !- Hour 5

    0.08048611,              !- Hour 6

    0.114375,                !- Hour 7

    0.190625,                !- Hour 8

    0.1440278,               !- Hour 9

    0.07624999,              !- Hour 10

    0.06354167,              !- Hour 11

    0.06354167,              !- Hour 12

    0.06354167,              !- Hour 13

    0.06354167,              !- Hour 14

    0.06354167,              !- Hour 15

    0.06354167,              !- Hour 16

    0.06777778,              !- Hour 17

    0.08472222,              !- Hour 18

    0.1482639,               !- Hour 19

    0.2965278,               !- Hour 20

    0.5210416,               !- Hour 21

    0.6820139,               !- Hour 22

    0.53375,                 !- Hour 23

    0.3727778;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay6,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1894444,               !- Hour 1

    0.114456,                !- Hour 2

    0.07498842,              !- Hour 3

    0.07498842,              !- Hour 4

    0.07498842,              !- Hour 5

    0.07893518,              !- Hour 6

    0.1065625,               !- Hour 7

    0.1697106,               !- Hour 8

    0.1262963,               !- Hour 9

    0.07104167,              !- Hour 10

    0.06314815,              !- Hour 11

    0.05920139,              !- Hour 12

    0.05920139,              !- Hour 13

    0.05920139,              !- Hour 14

    0.05920139,              !- Hour 15

    0.06314815,              !- Hour 16

    0.06314815,              !- Hour 17

    0.07893518,              !- Hour 18

    0.1262963,               !- Hour 19

    0.2446991,               !- Hour 20

    0.4380903,               !- Hour 21

    0.6354282,               !- Hour 22

    0.5328125,               !- Hour 23

    0.3709954;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay7,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1168056,               !- Hour 2

    0.07652777,              !- Hour 3

    0.07652777,              !- Hour 4

    0.07652777,              !- Hour 5

    0.08055555,              !- Hour 6

    0.1127778,               !- Hour 7

    0.1852778,               !- Hour 8

    0.1409722,               !- Hour 9

    0.07652777,              !- Hour 10

    0.06444445,              !- Hour 11

    0.06444445,              !- Hour 12

    0.06444445,              !- Hour 13

    0.06444445,              !- Hour 14

    0.06444445,              !- Hour 15

    0.06444445,              !- Hour 16

    0.06847222,              !- Hour 17

    0.08055555,              !- Hour 18

    0.1288889,               !- Hour 19

    0.2456944,               !- Hour 20

    0.4430555,               !- Hour 21

    0.6404166,               !- Hour 22

    0.5356944,               !- Hour 23

    0.3705555;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay8,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1895833,               !- Hour 1

    0.1128472,               !- Hour 2

    0.07673611,              !- Hour 3

    0.07673611,              !- Hour 4

    0.07673611,              !- Hour 5

    0.08125,                 !- Hour 6

    0.1309028,               !- Hour 7

    0.2302083,               !- Hour 8

    0.1805556,               !- Hour 9

    0.09027778,              !- Hour 10

    0.07222222,              !- Hour 11

    0.07222222,              !- Hour 12

    0.07222222,              !- Hour 13

    0.07222222,              !- Hour 14

    0.07222222,              !- Hour 15

    0.07222222,              !- Hour 16

    0.07673611,              !- Hour 17

    0.09930556,              !- Hour 18

    0.1670139,               !- Hour 19

    0.325,                   !- Hour 20

    0.5552083,               !- Hour 21

    0.7131944,               !- Hour 22

    0.5326388,               !- Hour 23

    0.3701389;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay9,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1908796,               !- Hour 1

    0.1145278,               !- Hour 2

    0.07635185,              !- Hour 3

    0.07635185,              !- Hour 4

    0.07635185,              !- Hour 5

    0.08180555,              !- Hour 6

    0.1527037,               !- Hour 7

    0.2890463,               !- Hour 8

    0.239963,                !- Hour 9

    0.1199815,               !- Hour 10

    0.09271296,              !- Hour 11

    0.09271296,              !- Hour 12

    0.09271296,              !- Hour 13

    0.09271296,              !- Hour 14

    0.09271296,              !- Hour 15

    0.09271296,              !- Hour 16

    0.1036204,               !- Hour 17

    0.1527037,               !- Hour 18

    0.2835926,               !- Hour 19

    0.5181018,               !- Hour 20

    0.7744259,               !- Hour 21

    0.7198889,               !- Hour 22

    0.5399166,               !- Hour 23

    0.3763056;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay10,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1893055,               !- Hour 1

    0.1175,                  !- Hour 2

    0.07833333,              !- Hour 3

    0.07833333,              !- Hour 4

    0.07833333,              !- Hour 5

    0.08486111,              !- Hour 6

    0.17625,                 !- Hour 7

    0.3590278,               !- Hour 8

    0.3198611,               !- Hour 9

    0.1566667,               !- Hour 10

   0.1240278,               !- Hour 11

    0.1240278,               !- Hour 12

    0.1240278,               !- Hour 13

    0.1240278,               !- Hour 14

    0.1240278,               !- Hour 15

    0.1305556,               !- Hour 16

    0.1631944,               !- Hour 17

    0.2676389,               !- Hour 18

    0.4895833,               !- Hour 19

    0.7702777,               !- Hour 20

    0.8486111,               !- Hour 21

    0.7115278,               !- Hour 22

    0.5352778,               !- Hour 23

    0.3720833;               !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay11,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.19375,                 !- Hour 1

    0.11625,                 !- Hour 2

    0.0775,                  !- Hour 3

    0.0775,                  !- Hour 4

    0.0775,                  !- Hour 5

    0.08525,                 !- Hour 6

    0.14725,                 !- Hour 7

    0.28675,                 !- Hour 8

    0.279,                   !- Hour 9

    0.155,                   !- Hour 10

    0.13175,                 !- Hour 11

    0.13175,                 !- Hour 12

    0.13175,                 !- Hour 13

    0.13175,                 !- Hour 14

    0.14725,                 !- Hour 15

    0.20925,                 !- Hour 16

    0.37975,                 !- Hour 17

    0.67425,                 !- Hour 18

    0.92225,                 !- Hour 19

    0.92225,                 !- Hour 20

    0.8525,                  !- Hour 21

    0.72075,                 !- Hour 22

    0.53475,                 !- Hour 23

    0.372;                   !- Hour 24

 

Schedule:Day:Hourly,

    GarageLightingProfileDay12,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1916667,               !- Hour 1

    0.1166667,               !- Hour 2

    0.075,                   !- Hour 3

    0.075,                   !- Hour 4

    0.075,                   !- Hour 5

    0.08333333,              !- Hour 6

    0.175,                   !- Hour 7

    0.3583333,               !- Hour 8

    0.35,                    !- Hour 9

    0.1916667,               !- Hour 10

    0.1583333,               !- Hour 11

    0.1583333,               !- Hour 12

    0.1583333,               !- Hour 13

   0.1583333,               !- Hour 14

    0.175,                   !- Hour 15

    0.2416667,               !- Hour 16

    0.4333333,               !- Hour 17

    0.7583333,               !- Hour 18

    0.9999999,               !- Hour 19

    0.9333333,               !- Hour 20

    0.85,                    !- Hour 21

    0.7166666,               !- Hour 22

    0.5333333,               !- Hour 23

    0.375;                   !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay1,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1127778,               !- Hour 2

    0.08055556,              !- Hour 3

    0.08055556,              !- Hour 4

    0.08055556,              !- Hour 5

    0.08055556,              !- Hour 6

    0.1852778,               !- Hour 7

    0.3786111,               !- Hour 8

    0.3625,                  !- Hour 9

    0.1852778,               !- Hour 10

    0.1530556,               !- Hour 11

    0.1530556,               !- Hour 12

    0.1530556,               !- Hour 13

    0.1530556,               !- Hour 14

    0.1611111,               !- Hour 15

    0.2013889,               !- Hour 16

    0.3383334,               !- Hour 17

    0.6283334,               !- Hour 18

    0.9344445,               !- Hour 19

    0.9908334,               !- Hour 20

    0.8538889,               !- Hour 21

    0.7169445,               !- Hour 22

    0.5397223,               !- Hour 23

    0.3705556;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay2,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1909821,               !- Hour 1

    0.1131746,               !- Hour 2

    0.07780755,              !- Hour 3

    0.07780755,              !- Hour 4

    0.07780755,              !- Hour 5

    0.08488096,              !- Hour 6

    0.1626885,               !- Hour 7

    0.325377,                !- Hour 8

    0.2900099,               !- Hour 9

    0.1414683,               !- Hour 10

    0.1131746,               !- Hour 11

    0.1131746,               !- Hour 12

    0.1131746,               !- Hour 13

    0.1131746,               !- Hour 14

    0.120248,                !- Hour 15

    0.1414683,               !- Hour 16

    0.2192758,               !- Hour 17

    0.4244048,               !- Hour 18

    0.7285616,               !- Hour 19

    0.9336905,               !- Hour 20

    0.8700298,               !- Hour 21

    0.7214881,               !- Hour 22

    0.5375794,               !- Hour 23

    0.3748909;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay3,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1911111,               !- Hour 1

    0.1134722,               !- Hour 2

    0.07763889,              !- Hour 3

    0.07763889,              !- Hour 4

    0.07763889,              !- Hour 5

    0.08361112,              !- Hour 6

    0.1313889,               !- Hour 7

    0.2329167,               !- Hour 8

    0.1851389,               !- Hour 9

    0.09555556,              !- Hour 10

    0.07763889,              !- Hour 11

    0.07763889,              !- Hour 12

    0.07763889,              !- Hour 13

    0.07763889,              !- Hour 14

    0.07763889,              !- Hour 15

    0.08958334,              !- Hour 16

    0.1373611,               !- Hour 17

    0.2747222,               !- Hour 18

    0.5315278,               !- Hour 19

    0.7943056,               !- Hour 20

    0.8540278,               !- Hour 21

    0.7166667,               !- Hour 22

    0.5375,                  !- Hour 23

    0.37625;                 !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay4,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1903056,               !- Hour 1

    0.1171111,               !- Hour 2

    0.07807408,              !- Hour 3

    0.07807408,              !- Hour 4

    0.07807408,              !- Hour 5

    0.08295371,              !- Hour 6

    0.1366296,               !- Hour 7

    0.2537408,               !- Hour 8

    0.2049445,               !- Hour 9

    0.0975926,               !- Hour 10

    0.07807408,              !- Hour 11

    0.07807408,              !- Hour 12

    0.07807408,              !- Hour 13

   0.07807408,              !- Hour 14

    0.07807408,              !- Hour 15

    0.07807408,              !- Hour 16

    0.08295371,              !- Hour 17

    0.1122315,               !- Hour 18

    0.2049445,               !- Hour 19

    0.4050093,               !- Hour 20

    0.6636297,               !- Hour 21

    0.7173056,               !- Hour 22

    0.5367593,               !- Hour 23

    0.3708519;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay5,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.190625,                !- Hour 1

    0.114375,                !- Hour 2

    0.07625,                 !- Hour 3

    0.07625,                 !- Hour 4

    0.07625,                 !- Hour 5

    0.08048612,              !- Hour 6

    0.114375,                !- Hour 7

    0.190625,                !- Hour 8

    0.1440278,               !- Hour 9

    0.07625,                 !- Hour 10

    0.06354167,              !- Hour 11

    0.06354167,              !- Hour 12

    0.06354167,              !- Hour 13

    0.06354167,              !- Hour 14

    0.06354167,              !- Hour 15

    0.06354167,              !- Hour 16

    0.06777778,              !- Hour 17

    0.08472223,              !- Hour 18

    0.1482639,               !- Hour 19

    0.2965278,               !- Hour 20

    0.5210417,               !- Hour 21

    0.6820139,               !- Hour 22

    0.5337501,               !- Hour 23

    0.3727778;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay6,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1894445,               !- Hour 1

    0.114456,                !- Hour 2

    0.07498843,              !- Hour 3

    0.07498843,              !- Hour 4

    0.07498843,              !- Hour 5

    0.07893519,              !- Hour 6

    0.1065625,               !- Hour 7

    0.1697107,               !- Hour 8

    0.1262963,               !- Hour 9

    0.07104167,              !- Hour 10

    0.06314816,              !- Hour 11

    0.05920139,              !- Hour 12

    0.05920139,              !- Hour 13

    0.05920139,              !- Hour 14

    0.05920139,              !- Hour 15

    0.06314816,              !- Hour 16

    0.06314816,              !- Hour 17

    0.07893519,              !- Hour 18

    0.1262963,               !- Hour 19

    0.2446991,               !- Hour 20

    0.4380903,               !- Hour 21

    0.6354283,               !- Hour 22

    0.5328125,               !- Hour 23

    0.3709954;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay7,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1933333,               !- Hour 1

    0.1168056,               !- Hour 2

    0.07652778,              !- Hour 3

    0.07652778,              !- Hour 4

    0.07652778,              !- Hour 5

    0.08055556,              !- Hour 6

    0.1127778,               !- Hour 7

    0.1852778,               !- Hour 8

    0.1409722,               !- Hour 9

    0.07652778,              !- Hour 10

    0.06444445,              !- Hour 11

    0.06444445,              !- Hour 12

    0.06444445,              !- Hour 13

    0.06444445,              !- Hour 14

    0.06444445,              !- Hour 15

    0.06444445,              !- Hour 16

    0.06847223,              !- Hour 17

    0.08055556,              !- Hour 18

    0.1288889,               !- Hour 19

    0.2456945,               !- Hour 20

    0.4430556,               !- Hour 21

    0.6404167,               !- Hour 22

    0.5356945,               !- Hour 23

    0.3705556;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay8,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1895833,               !- Hour 1

    0.1128472,               !- Hour 2

    0.07673611,              !- Hour 3

    0.07673611,              !- Hour 4

    0.07673611,              !- Hour 5

    0.08125,                 !- Hour 6

    0.1309028,               !- Hour 7

    0.2302084,               !- Hour 8

    0.1805556,               !- Hour 9

    0.09027778,              !- Hour 10

    0.07222223,              !- Hour 11

    0.07222223,              !- Hour 12

    0.07222223,              !- Hour 13

    0.07222223,              !- Hour 14

    0.07222223,              !- Hour 15

    0.07222223,              !- Hour 16

    0.07673611,              !- Hour 17

    0.09930556,              !- Hour 18

    0.1670139,               !- Hour 19

    0.325,                   !- Hour 20

    0.5552084,               !- Hour 21

    0.7131945,               !- Hour 22

    0.5326389,               !- Hour 23

    0.3701389;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay9,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1908796,               !- Hour 1

    0.1145278,               !- Hour 2

    0.07635186,              !- Hour 3

    0.07635186,              !- Hour 4

    0.07635186,              !- Hour 5

    0.08180556,              !- Hour 6

    0.1527037,               !- Hour 7

    0.2890463,               !- Hour 8

    0.239963,                !- Hour 9

    0.1199815,               !- Hour 10

    0.09271297,              !- Hour 11

    0.09271297,              !- Hour 12

    0.09271297,              !- Hour 13

    0.09271297,              !- Hour 14

    0.09271297,              !- Hour 15

    0.09271297,              !- Hour 16

    0.1036204,               !- Hour 17

    0.1527037,               !- Hour 18

    0.2835926,               !- Hour 19

    0.5181019,               !- Hour 20

    0.774426,                !- Hour 21

    0.7198889,               !- Hour 22

    0.5399167,               !- Hour 23

    0.3763056;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay10,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1893056,               !- Hour 1

    0.1175,                  !- Hour 2

    0.07833334,              !- Hour 3

    0.07833334,              !- Hour 4

    0.07833334,              !- Hour 5

    0.08486111,              !- Hour 6

    0.17625,                 !- Hour 7

    0.3590278,               !- Hour 8

    0.3198611,               !- Hour 9

    0.1566667,               !- Hour 10

    0.1240278,               !- Hour 11

    0.1240278,               !- Hour 12

    0.1240278,               !- Hour 13

    0.1240278,               !- Hour 14

    0.1240278,               !- Hour 15

    0.1305556,               !- Hour 16

    0.1631944,               !- Hour 17

    0.2676389,               !- Hour 18

    0.4895834,               !- Hour 19

    0.7702778,               !- Hour 20

    0.8486112,               !- Hour 21

    0.7115278,               !- Hour 22

    0.5352778,               !- Hour 23

    0.3720834;               !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay11,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.19375,                 !- Hour 1

    0.11625,                 !- Hour 2

    0.07750001,              !- Hour 3

    0.07750001,              !- Hour 4

    0.07750001,              !- Hour 5

    0.08525001,              !- Hour 6

    0.14725,                 !- Hour 7

    0.28675,                 !- Hour 8

    0.279,                   !- Hour 9

    0.155,                   !- Hour 10

    0.13175,                 !- Hour 11

    0.13175,                 !- Hour 12

    0.13175,                 !- Hour 13

    0.13175,                 !- Hour 14

    0.14725,                 !- Hour 15

    0.20925,                 !- Hour 16

    0.37975,                 !- Hour 17

    0.6742501,               !- Hour 18

    0.92225,                 !- Hour 19

    0.92225,                 !- Hour 20

    0.8525001,               !- Hour 21

    0.72075,                 !- Hour 22

    0.53475,                 !- Hour 23

    0.372;                   !- Hour 24

 

Schedule:Day:Hourly,

    ExteriorLightingProfileDay12,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0.1916667,               !- Hour 1

    0.1166667,               !- Hour 2

    0.075,                   !- Hour 3

    0.075,                   !- Hour 4

    0.075,                   !- Hour 5

    0.08333334,              !- Hour 6

    0.175,                   !- Hour 7

    0.3583333,               !- Hour 8

    0.35,                    !- Hour 9

    0.1916667,               !- Hour 10

    0.1583333,               !- Hour 11

    0.1583333,               !- Hour 12

    0.1583333,               !- Hour 13

    0.1583333,               !- Hour 14

    0.175,                   !- Hour 15

    0.2416667,               !- Hour 16

    0.4333334,               !- Hour 17

    0.7583334,               !- Hour 18

    1,                       !- Hour 19

    0.9333334,               !- Hour 20

    0.8500001,               !- Hour 21

    0.7166667,               !- Hour 22

    0.5333334,               !- Hour 23

    0.375;                   !- Hour 24

 

Schedule:Day:Hourly,

    RefrigeratorDay,         !- Name

    Fraction,                !- Schedule Type Limits Name

    0.8,                     !- Hour 1

    0.782696177062374,       !- Hour 2

    0.765593561368209,       !- Hour 3

    0.742857142857143,       !- Hour 4

    0.731388329979879,       !- Hour 5

    0.731388329979879,       !- Hour 6

    0.759959758551308,       !- Hour 7

    0.8,                     !- Hour 8

    0.817102615694165,       !- Hour 9

    0.828571428571429,       !- Hour 10

    0.8,                     !- Hour 11

    0.8,                     !- Hour 12

    0.839839034205231,       !- Hour 13

    0.839839034205231,       !- Hour 14

    0.828571428571429,       !- Hour 15

    0.839839034205231,       !- Hour 16

    0.885714285714286,       !- Hour 17

    0.971428571428572,       !- Hour 18

    1,                       !- Hour 19

    0.971428571428572,       !- Hour 20

    0.942857142857143,       !- Hour 21

    0.925553319919517,       !- Hour 22

    0.885714285714286,       !- Hour 23

    0.828571428571429;       !- Hour 24

 

Schedule:Day:Hourly,

    CeilingFanWeekday,       !- Name

    On/Off,                  !- Schedule Type Limits Name

    1,                       !- Hour 1

    1,                       !- Hour 2

    1,                       !- Hour 3

    1,                       !- Hour 4

    1,                       !- Hour 5

    1,                       !- Hour 6

    1,                       !- Hour 7

    1,                       !- Hour 8

    1,                       !- Hour 9

    1,                       !- Hour 10

    1,                       !- Hour 11

    1,                       !- Hour 12

    1,                       !- Hour 13

    1,                       !- Hour 14

    1,                       !- Hour 15

    1,                       !- Hour 16

    1,                       !- Hour 17

    1,                       !- Hour 18

    1,                       !- Hour 19

    1,                       !- Hour 20

    1,                       !- Hour 21

    1,                       !- Hour 22

    1,                       !- Hour 23

    1;                       !- Hour 24

 

Schedule:Day:Hourly,

    CeilingFanWeekend,       !- Name

    On/Off,                  !- Schedule Type Limits Name

    1,                       !- Hour 1

    1,                       !- Hour 2

    1,                       !- Hour 3

    1,                       !- Hour 4

    1,                       !- Hour 5

    1,                       !- Hour 6

    1,                       !- Hour 7

    1,                       !- Hour 8

    1,                       !- Hour 9

    1,                       !- Hour 10

    1,                       !- Hour 11

    1,                       !- Hour 12

    1,                       !- Hour 13

    1,                       !- Hour 14

    1,                       !- Hour 15

    1,                       !- Hour 16

    1,                       !- Hour 17

    1,                       !- Hour 18

    1,                       !- Hour 19

    1,                       !- Hour 20

    1,                       !- Hour 21

    1,                       !- Hour 22

    1,                       !- Hour 23

    1;                       !- Hour 24

 

Schedule:Day:Hourly,

    MiscPlugLoadDay,         !- Name

    Multiplier,              !- Schedule Type Limits Name

    0.607490272373541,       !- Hour 1

    0.559338521400778,       !- Hour 2

    0.552853437094682,       !- Hour 3

    0.545071335927367,       !- Hour 4

    0.524481193255512,       !- Hour 5

    0.585278858625162,       !- Hour 6

    0.676232166018158,       !- Hour 7

    0.718547341115435,       !- Hour 8

    0.607490272373541,       !- Hour 9

    0.517023346303502,       !- Hour 10

    0.529182879377432,       !- Hour 11

    0.529345006485084,       !- Hour 12

    0.520428015564202,       !- Hour 13

    0.538424124513619,       !- Hour 14

    0.568741893644617,       !- Hour 15

    0.600356679636835,       !- Hour 16

    0.71011673151751,        !- Hour 17

    0.862678339818418,       !- Hour 18

    0.936608300907912,       !- Hour 19

    0.966763942931258,       !- Hour 20

    1,                       !- Hour 21

    0.976653696498055,       !- Hour 22

    0.845168612191959,       !- Hour 23

    0.73443579766537;        !- Hour 24

 

Schedule:Day:Hourly,

    CookingRangeDay,         !- Name

    Fraction,                !- Schedule Type Limits Name

    0.04715848452508,        !- Hour 1

    0.04715848452508,        !- Hour 2

    0.0235458911419424,      !- Hour 3

    0.0235458911419424,      !- Hour 4

    0.04715848452508,        !- Hour 5

    0.0707043756670224,      !- Hour 6

    0.165088046958378,       !- Hour 7

    0.283017609391676,       !- Hour 8

    0.306563500533618,       !- Hour 9

    0.320771077908218,       !- Hour 10

    0.283017609391676,       !- Hour 11

    0.330176093916756,       !- Hour 12

    0.377334578441836,       !- Hour 13

    0.306563500533618,       !- Hour 14

    0.292422625400213,       !- Hour 15

    0.377334578441836,       !- Hour 16

    0.613193703308431,       !- Hour 17

    1,                       !- Hour 18

    0.778348452508004,       !- Hour 19

    0.400947171824973,       !- Hour 20

    0.235859124866596,       !- Hour 21

    0.165088046958378,       !- Hour 22

    0.103721985058698,       !- Hour 23

    0.0707043756670224;      !- Hour 24

 

Schedule:Day:Hourly,

    DishwasherWeekday,       !- Name

    Fraction,                !- Schedule Type Limits Name

    0.129162158913331,       !- Hour 1

    0.0573867051328282,      !- Hour 2

    0.0429979564851542,      !- Hour 3

    0.0286933525664145,      !- Hour 4

    0.0286933525664145,      !- Hour 5

    0.0860800576992427,      !- Hour 6

    0.172244260127419,       !- Hour 7

    0.258408462555596,       !- Hour 8

    0.488207717273711,       !- Hour 9

    0.545594422406539,       !- Hour 10

    0.473818968626037,       !- Hour 11

    0.402043514845535,       !- Hour 12

    0.344572664983772,       !- Hour 13

    0.387654766197861,       !- Hour 14

    0.315879312417358,       !- Hour 15

    0.301490563769684,       !- Hour 16

    0.315879312417358,       !- Hour 17

    0.416348118764274,       !- Hour 18

    0.732311575910566,       !- Hour 19

    0.93333333333333,        !- Hour 20

    0.761004928476981,       !- Hour 21

    0.559983171054213,       !- Hour 22

    0.373266017550187,       !- Hour 23

    0.258408462555596;       !- Hour 24

 

Schedule:Day:Hourly,

    DishwasherWeekend,       !- Name

    Fraction,                !- Schedule Type Limits Name

    0.13838802740714,        !- Hour 1

    0.0614857554994591,      !- Hour 2

    0.0460692390912369,      !- Hour 3

    0.0307428777497295,      !- Hour 4

    0.0307428777497295,      !- Hour 5

    0.0922286332491886,      !- Hour 6

    0.184547421565092,       !- Hour 7

    0.276866209880995,       !- Hour 8

    0.523079697078976,       !- Hour 9

    0.584565452578435,       !- Hour 10

    0.507663180670754,       !- Hour 11

    0.430760908763072,       !- Hour 12

    0.369184998196899,       !- Hour 13

    0.41534439235485,        !- Hour 14

    0.338442120447169,       !- Hour 15

    0.323025604038947,       !- Hour 16

    0.338442120447169,       !- Hour 17

    0.44608727010458,        !- Hour 18

    0.784619545618464,       !- Hour 19

    1,                       !- Hour 20

    0.815362423368193,       !- Hour 21

    0.599981968986657,       !- Hour 22

    0.399927875946628,       !- Hour 23

    0.276866209880995;       !- Hour 24

 

Schedule:Day:Hourly,

    DishwasherVacation,      !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesWasherWeekday,    !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0887931470412736,      !- Hour 1

    0.0710155041111689,      !- Hour 2

    0.0354602182509584,      !- Hour 3

    0.0354602182509584,      !- Hour 4

    0.0710155041111689,      !- Hour 5

    0.106570789971378,       !- Hour 6

    0.213141579942758,       !- Hour 7

    0.461933513354977,       !- Hour 8

    0.69294780383709,        !- Hour 9

    0.817391304347826,       !- Hour 10

    0.799613661417722,       !- Hour 11

    0.710725446767196,       !- Hour 12

    0.639614875046775,       !- Hour 13

    0.568599370935607,       !- Hour 14

    0.497488799215186,       !- Hour 15

    0.461933513354977,       !- Hour 16

    0.479711156285081,       !- Hour 17

    0.461933513354977,       !- Hour 18

    0.461933513354977,       !- Hour 19

    0.461933513354977,       !- Hour 20

    0.461933513354977,       !- Hour 21

    0.444155870424871,       !- Hour 22

    0.302029794593282,       !- Hour 23

    0.159903718761693;       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesWasherWeekend,    !- Name

    Fraction,                !- Schedule Type Limits Name

    0.108629913933473,       !- Hour 1

    0.086880669923238,       !- Hour 2

    0.0433821819027681,      !- Hour 3

    0.0433821819027681,      !- Hour 4

    0.086880669923238,       !- Hour 5

    0.130379157943708,       !- Hour 6

    0.260758315887416,       !- Hour 7

    0.565131425913003,       !- Hour 8

    0.847755291928355,       !- Hour 9

    1,                       !- Hour 10

    0.978250755989765,       !- Hour 11

    0.86950453593859,        !- Hour 12

    0.782507559897651,       !- Hour 13

    0.695626889974413,       !- Hour 14

    0.608629913933473,       !- Hour 15

    0.565131425913003,       !- Hour 16

    0.586880669923238,       !- Hour 17

    0.565131425913003,       !- Hour 18

    0.565131425913003,       !- Hour 19

    0.565131425913003,       !- Hour 20

    0.565131425913003,       !- Hour 21

    0.543382181902768,       !- Hour 22

    0.36950453593859,        !- Hour 23

    0.195626889974413;       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesWasherVacation,   !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

   0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesDryerWeekday,     !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0996818663838815,      !- Hour 1

    0.0598091198303289,      !- Hour 2

    0.0398727465535526,      !- Hour 3

    0.0199363732767763,      !- Hour 4

    0.0398727465535526,      !- Hour 5

    0.0598091198303289,      !- Hour 6

    0.15949098621421,        !- Hour 7

    0.31898197242842,        !- Hour 8

    0.486427370202556,       !- Hour 9

    0.685791102970318,       !- Hour 10

    0.785472969354199,       !- Hour 11

    0.817391304347826,       !- Hour 12

    0.745600222800647,       !- Hour 13

    0.677836691410393,       !- Hour 14

    0.610073160020138,       !- Hour 15

    0.578154825026511,       !- Hour 16

    0.558218451749735,       !- Hour 17

    0.546236490032885,       !- Hour 18

    0.518345705196183,       !- Hour 19

    0.510391293636256,       !- Hour 20

    0.526300116756109,       !- Hour 21

    0.546236490032885,       !- Hour 22

    0.438600212089077,       !- Hour 23

    0.239236479321316;       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesDryerWeekend,     !- Name

    Fraction,                !- Schedule Type Limits Name

    0.121951219512195,       !- Hour 1

    0.0731707317073171,      !- Hour 2

    0.0487804878048781,      !- Hour 3

    0.024390243902439,       !- Hour 4

    0.0487804878048781,      !- Hour 5

    0.0731707317073171,      !- Hour 6

    0.195121951219512,       !- Hour 7

    0.390243902439024,       !- Hour 8

    0.59509731460951,        !- Hour 9

    0.8389997536339,         !- Hour 10

    0.960950973146095,       !- Hour 11

    1,                       !- Hour 12

    0.912170485341217,       !- Hour 13

    0.829268292682927,       !- Hour 14

    0.746366100024637,       !- Hour 15

    0.707317073170732,       !- Hour 16

    0.682926829268293,       !- Hour 17

    0.668268046316827,       !- Hour 18

    0.634146341463415,       !- Hour 19

    0.624414880512441,       !- Hour 20

    0.643877802414388,       !- Hour 21

    0.668268046316827,       !- Hour 22

    0.536585365853659,       !- Hour 23

    0.292682926829268;       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesDryerVacation,    !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    SinksWeekday,            !- Name

    Fraction,                !- Schedule Type Limits Name

    0.178431090172197,       !- Hour 1

    0.0855612360359615,      !- Hour 2

    0.0641394243627467,      !- Hour 3

    0.0641394243627467,      !- Hour 4

    0.0855612360359615,      !- Hour 5

    0.228457320962002,       !- Hour 6

    0.535419281173493,       !- Hour 7

    0.785298413808711,       !- Hour 8

    0.828142037155143,       !- Hour 9

    0.778115806365338,       !- Hour 10

    0.685371962886004,       !- Hour 11

    0.628163124652828,       !- Hour 12

    0.613923920422985,       !- Hour 13

    0.571080297076553,       !- Hour 14

    0.521054066286749,       !- Hour 15

    0.542475877959965,       !- Hour 16

    0.606741312979612,       !- Hour 17

    0.82095942971177,        !- Hour 18

    0.942307692307692,       !- Hour 19

    0.870985660501574,       !- Hour 20

    0.713850371345691,       !- Hour 21

    0.606741312979612,       !- Hour 22

    0.499758265270435,       !- Hour 23

    0.342622976114552;       !- Hour 24

 

Schedule:Day:Hourly,

    SinksWeekend,            !- Name

    Fraction,                !- Schedule Type Limits Name

    0.18935544263172,        !- Hour 1

    0.0907996790585718,      !- Hour 2

    0.0680663278951591,      !- Hour 3

    0.0680663278951591,      !- Hour 4

    0.0907996790585718,      !- Hour 5

    0.242444503878042,       !- Hour 6

    0.568200053490238,       !- Hour 7

    0.833377908531693,       !- Hour 8

    0.878844610858518,       !- Hour 9

    0.825755549612196,       !- Hour 10

    0.727333511634127,       !- Hour 11

    0.666622091468307,       !- Hour 12

    0.651511099224392,       !- Hour 13

    0.606044396897566,       !- Hour 14

    0.552955335651244,       !- Hour 15

    0.575688686814656,       !- Hour 16

    0.643888740304894,       !- Hour 17

    0.871222251939021,       !- Hour 18

    1,                       !- Hour 19

    0.924311313185344,       !- Hour 20

    0.757555496121958,       !- Hour 21

    0.643888740304894,       !- Hour 22

    0.53035571008291,        !- Hour 23

    0.363599893019524;       !- Hour 24

 

Schedule:Day:Hourly,

    SinksVacation,           !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    ShowersWeekday,          !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0847763225038272,      !- Hour 1

    0.0384986108748656,      !- Hour 2

    0.0269887169019672,      !- Hour 3

    0.0384986108748656,      !- Hour 4

    0.10795486760787,        !- Hour 5

    0.408799682485684,       !- Hour 6

    0.93333333333333,        !- Hour 7

    0.92563361115836,        !- Hour 8

    0.752112037194534,       !- Hour 9

    0.590100357203606,       !- Hour 10

    0.47436638884164,        !- Hour 11

    0.374111243408743,       !- Hour 12

    0.269966547598798,       !- Hour 13

   0.231388558144809,       !- Hour 14

    0.200510290865794,       !- Hour 15

    0.208210013040766,       !- Hour 16

    0.239088280319782,       !- Hour 17

    0.308544537052787,       !- Hour 18

    0.335533253954754,       !- Hour 19

    0.335533253954754,       !- Hour 20

    0.331643703577706,       !- Hour 21

    0.323943981402733,       !- Hour 22

    0.231388558144809,       !- Hour 23

    0.165821851788853;       !- Hour 24

 

Schedule:Day:Hourly,

    ShowersWeekend,          !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0908317741112434,      !- Hour 1

    0.0412485116516414,      !- Hour 2

    0.0289164823949651,      !- Hour 3

    0.0412485116516414,      !- Hour 4

    0.115665929579861,       !- Hour 5

    0.437999659806089,       !- Hour 6

    1,                       !- Hour 7

    0.991750297669672,       !- Hour 8

    0.805834325565572,       !- Hour 9

    0.632250382718149,       !- Hour 10

    0.508249702330328,       !- Hour 11

    0.400833475080796,       !- Hour 12

    0.289249872427284,       !- Hour 13

    0.24791631229801,        !- Hour 14

    0.214832454499064,       !- Hour 15

    0.223082156829393,       !- Hour 16

    0.256166014628338,       !- Hour 17

    0.330583432556557,       !- Hour 18

    0.359499914951522,       !- Hour 19

    0.359499914951522,       !- Hour 20

    0.355332539547542,       !- Hour 21

    0.347082837217214,       !- Hour 22

    0.24791631229801,        !- Hour 23

    0.177666269773771;       !- Hour 24

 

Schedule:Day:Hourly,

    ShowersVacation,         !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    BathsWeekday,            !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0549341075342269,      !- Hour 1

    0.027467053767114,       !- Hour 2

    0.027467053767114,       !- Hour 3

    0.027467053767114,       !- Hour 4

    0.0549341075342269,      !- Hour 5

    0.137335268835568,       !- Hour 6

    0.329675803375743,       !- Hour 7

    0.412076964677084,       !- Hour 8

    0.467011072211311,       !- Hour 9

    0.412076964677084,       !- Hour 10

    0.329675803375743,       !- Hour 11

    0.247203483904022,       !- Hour 12

    0.219736430136909,       !- Hour 13

    0.164802322602681,       !- Hour 14

    0.164802322602681,       !- Hour 15

    0.164802322602681,       !- Hour 16

    0.274741695841516,       !- Hour 17

    0.329675803375743,       !- Hour 18

    0.549483391683034,       !- Hour 19

    0.714285714285714,       !- Hour 20

    0.714285714285714,       !- Hour 21

    0.549483391683034,       !- Hour 22

    0.467011072211311,       !- Hour 23

    0.274741695841516;       !- Hour 24

 

Schedule:Day:Hourly,

    BathsWeekend,            !- Name

    Fraction,                !- Schedule Type Limits Name

    0.0769077505479179,      !- Hour 1

    0.038453875273959,       !- Hour 2

    0.038453875273959,       !- Hour 3

    0.038453875273959,       !- Hour 4

    0.0769077505479179,      !- Hour 5

    0.192269376369795,       !- Hour 6

    0.461546124726041,       !- Hour 7

    0.576907750547918,       !- Hour 8

    0.653815501095836,       !- Hour 9

    0.576907750547918,       !- Hour 10

    0.461546124726041,       !- Hour 11

    0.346084877465631,       !- Hour 12

    0.307631002191672,       !- Hour 13

   0.230723251643754,       !- Hour 14

    0.230723251643754,       !- Hour 15

    0.230723251643754,       !- Hour 16

    0.384638374178123,       !- Hour 17

    0.461546124726041,       !- Hour 18

    0.769276748356246,       !- Hour 19

    1,                       !- Hour 20

    1,                       !- Hour 21

    0.769276748356246,       !- Hour 22

    0.653815501095836,       !- Hour 23

    0.384638374178123;       !- Hour 24

 

Schedule:Day:Hourly,

    BathsVacation,           !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    DHWDistDay,              !- Name

    Fraction,                !- Schedule Type Limits Name

    0.142553149370226,       !- Hour 1

    0.0764866759550322,      !- Hour 2

    0.0516611840277747,      !- Hour 3

    0.0584039294664903,      !- Hour 4

    0.121469841058603,       !- Hour 5

    0.366180268451559,       !- Hour 6

    0.833258955739606,       !- Hour 7

    0.999999987228391,       !- Hour 8

    0.995483090581232,       !- Hour 9

    0.916474762598139,       !- Hour 10

    0.800898393293271,       !- Hour 11

    0.682564390940485,       !- Hour 12

    0.590066600109555,       !- Hour 13

    0.522371887032053,       !- Hour 14

    0.466005974303267,       !- Hour 15

    0.46573704253214,        !- Hour 16

    0.527514234916123,       !- Hour 17

    0.637905701335668,       !- Hour 18

    0.727588642310272,       !- Hour 19

    0.732551127624518,       !- Hour 20

    0.681468471942116,       !- Hour 21

    0.610804704600985,       !- Hour 22

    0.464292318119835,       !- Hour 23

    0.299867724445383;       !- Hour 24

 

Schedule:Day:Hourly,

    BathExhaustDay,          !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    1,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    RangeHoodDay,            !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    0,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    1,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    ClothesDryerExhaustDay,  !- Name

    Fraction,                !- Schedule Type Limits Name

    0,                       !- Hour 1

    0,                       !- Hour 2

    0,                       !- Hour 3

    0,                       !- Hour 4

    0,                       !- Hour 5

    0,                       !- Hour 6

    0,                       !- Hour 7

    0,                       !- Hour 8

    0,                       !- Hour 9

    0,                       !- Hour 10

    1,                       !- Hour 11

    0,                       !- Hour 12

    0,                       !- Hour 13

    0,                       !- Hour 14

    0,                       !- Hour 15

    0,                       !- Hour 16

    0,                       !- Hour 17

    0,                       !- Hour 18

    0,                       !- Hour 19

    0,                       !- Hour 20

    0,                       !- Hour 21

    0,                       !- Hour 22

    0,                       !- Hour 23

    0;                       !- Hour 24

 

Schedule:Day:Hourly,

    NatVentTempWeekday,      !- Name

    Temperature,             !- Schedule Type Limits Name

    22.2222222222222,        !- Hour 1

    22.2222222222222,        !- Hour 2

    22.2222222222222,        !- Hour 3

    22.2222222222222,        !- Hour 4

    22.2222222222222,        !- Hour 5

    22.2222222222222,        !- Hour 6

    22.2222222222222,        !- Hour 7

    22.2222222222222,        !- Hour 8

    22.2222222222222,        !- Hour 9

    22.2222222222222,        !- Hour 10

    22.2222222222222,        !- Hour 11

    22.2222222222222,        !- Hour 12

    22.2222222222222,        !- Hour 13

    22.2222222222222,        !- Hour 14

    22.2222222222222,        !- Hour 15

    22.2222222222222,        !- Hour 16

    22.2222222222222,        !- Hour 17

    22.2222222222222,        !- Hour 18

    22.2222222222222,        !- Hour 19

    22.2222222222222,        !- Hour 20

    22.2222222222222,        !- Hour 21

    22.2222222222222,        !- Hour 22

    22.2222222222222,        !- Hour 23

    22.2222222222222;        !- Hour 24

 

Schedule:Day:Hourly,

    NatVentTempWeekend,      !- Name

    Temperature,             !- Schedule Type Limits Name

    22.2222222222222,        !- Hour 1

    22.2222222222222,        !- Hour 2

    22.2222222222222,        !- Hour 3

    22.2222222222222,        !- Hour 4

    22.2222222222222,        !- Hour 5

    22.2222222222222,        !- Hour 6

    22.2222222222222,        !- Hour 7

    22.2222222222222,        !- Hour 8

    22.2222222222222,        !- Hour 9

    22.2222222222222,        !- Hour 10

    22.2222222222222,        !- Hour 11

    22.2222222222222,        !- Hour 12

    22.2222222222222,        !- Hour 13

    22.2222222222222,        !- Hour 14

    22.2222222222222,        !- Hour 15

    22.2222222222222,        !- Hour 16

    22.2222222222222,        !- Hour 17

    22.2222222222222,        !- Hour 18

    22.2222222222222,        !- Hour 19

    22.2222222222222,        !- Hour 20

    22.2222222222222,        !- Hour 21

    22.2222222222222,        !- Hour 22

    22.2222222222222,        !- Hour 23

    22.2222222222222;        !- Hour 24

 

Schedule:Day:Hourly,

    WkDayCoolingSP,          !- Name

    Temperature,             !- Schedule Type Limits Name

    200,                     !- Hour 1

    200,                     !- Hour 2

    200,                     !- Hour 3

    200,                     !- Hour 4

    200,                     !- Hour 5

    200,                     !- Hour 6

    200,                     !- Hour 7

    200,                     !- Hour 8

    200,                     !- Hour 9

    200,                     !- Hour 10

    200,                     !- Hour 11

    200,                     !- Hour 12

    200,                     !- Hour 13

    200,                     !- Hour 14

    200,                     !- Hour 15

    200,                     !- Hour 16

    200,                     !- Hour 17

    200,                     !- Hour 18

    200,                     !- Hour 19

    200,                     !- Hour 20

    200,                     !- Hour 21

    200,                     !- Hour 22

    200,                     !- Hour 23

    200;                     !- Hour 24

 

Schedule:Day:Hourly,

    WkEndCoolingSP,          !- Name

    Temperature,             !- Schedule Type Limits Name

    200,                     !- Hour 1

    200,                     !- Hour 2

    200,                     !- Hour 3

    200,                     !- Hour 4

    200,                     !- Hour 5

    200,                     !- Hour 6

    200,                     !- Hour 7

    200,                     !- Hour 8

    200,                     !- Hour 9

    200,                     !- Hour 10

    200,                     !- Hour 11

    200,                     !- Hour 12

    200,                     !- Hour 13

    200,                     !- Hour 14

    200,                     !- Hour 15

    200,                     !- Hour 16

    200,                     !- Hour 17

    200,                     !- Hour 18

    200,                     !- Hour 19

    200,                     !- Hour 20

    200,                     !- Hour 21

    200,                     !- Hour 22

    200,                     !- Hour 23

    200;                     !- Hour 24

 

Schedule:Day:Hourly,

    WkDayHeatingSP,          !- Name

    Temperature,             !- Schedule Type Limits Name

    21.1111111,              !- Hour 1

    21.1111111,              !- Hour 2

    21.1111111,              !- Hour 3

    21.1111111,              !- Hour 4

    21.1111111,              !- Hour 5

    21.1111111,              !- Hour 6

    21.1111111,              !- Hour 7

    21.1111111,              !- Hour 8

    21.1111111,              !- Hour 9

    21.1111111,              !- Hour 10

    21.1111111,              !- Hour 11

    21.1111111,              !- Hour 12

    21.1111111,              !- Hour 13

    21.1111111,              !- Hour 14

    21.1111111,              !- Hour 15

    21.1111111,              !- Hour 16

    21.1111111,              !- Hour 17

    21.1111111,              !- Hour 18

    21.1111111,              !- Hour 19

    21.1111111,              !- Hour 20

    21.1111111,              !- Hour 21

    21.1111111,              !- Hour 22

    21.1111111,              !- Hour 23

    21.1111111;              !- Hour 24

 

Schedule:Day:Hourly,

    WkEndHeatingSP,          !- Name

    Temperature,             !- Schedule Type Limits Name

    21.1111111,              !- Hour 1

    21.1111111,              !- Hour 2

    21.1111111,              !- Hour 3

    21.1111111,              !- Hour 4

    21.1111111,              !- Hour 5

    21.1111111,              !- Hour 6

    21.1111111,              !- Hour 7

    21.1111111,              !- Hour 8

    21.1111111,              !- Hour 9

    21.1111111,              !- Hour 10

    21.1111111,              !- Hour 11

    21.1111111,              !- Hour 12

    21.1111111,              !- Hour 13

    21.1111111,              !- Hour 14

    21.1111111,              !- Hour 15

    21.1111111,              !- Hour 16

    21.1111111,              !- Hour 17

    21.1111111,              !- Hour 18

    21.1111111,              !- Hour 19

    21.1111111,              !- Hour 20

    21.1111111,              !- Hour 21

    21.1111111,              !- Hour 22

    21.1111111,              !- Hour 23

    21.1111111;              !- Hour 24

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:DAY:INTERVAL ===========

 

Schedule:Day:Interval,

    NatVentOn-Day,           !- Name

    Fraction,                !- Schedule Type Limits Name

    ,                        !- Interpolate to Timestep

    Until: 24:00,            !- Time 1 {hh:mm}

    1;                       !- Value Until Time 1

 

Schedule:Day:Interval,

    NatVentOff-Day,          !- Name

    Fraction,                !- Schedule Type Limits Name

    ,                        !- Interpolate to Timestep

    Until: 24:00,            !- Time 1 {hh:mm}

    0;                       !- Value Until Time 1

 

Schedule:Day:Interval,

    HDDHeatingSP,            !- Name

    Temperature,             !- Schedule Type Limits Name

    ,                        !- Interpolate to Timestep

    Until: 24:00,            !- Time 1 {hh:mm}

    21.1111111;              !- Value Until Time 1

 

Schedule:Day:Interval,

    CDDHeatingSP,            !- Name

    Temperature,             !- Schedule Type Limits Name

    ,                        !- Interpolate to Timestep

    Until: 24:00,            !- Time 1 {hh:mm}

    200;                     !- Value Until Time 1

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:WEEK:COMPACT ===========

 

Schedule:Week:Compact,

    OccupancyWeek,           !- Name

    For: CustomDay1,         !- DayType List 1

    OccupancyVacationDay,    !- Schedule:Day Name 1

    For: AllOtherDays,       !- DayType List 2

    OccupancyDay;            !- Schedule:Day Name 2

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek1,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay1;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek2,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay2;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek3,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay3;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek4,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay4;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek5,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay5;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek6,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay6;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek7,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay7;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek8,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay8;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek9,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay9;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek10,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay10;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek11,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay11;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    InteriorLightingProfileWeek12,  !- Name

    For: AllDays,            !- DayType List 1

    InteriorLightingProfileDay12;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek1,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay1;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek2,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay2;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek3,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay3;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek4,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay4;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek5,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay5;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek6,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay6;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek7,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay7;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek8,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay8;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek9,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay9;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek10,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay10;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek11,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay11;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    GarageLightingProfileWeek12,  !- Name

    For: AllDays,            !- DayType List 1

    GarageLightingProfileDay12;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek1,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay1;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek2,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay2;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek3,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay3;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek4,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay4;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek5,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay5;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek6,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay6;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek7,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay7;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek8,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay8;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek9,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay9;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek10,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay10;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

   ExteriorLightingProfileWeek11,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay11;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ExteriorLightingProfileWeek12,  !- Name

    For: AllDays,            !- DayType List 1

    ExteriorLightingProfileDay12;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    RefrigeratorWeek,        !- Name

    For: AllDays,            !- DayType List 1

    RefrigeratorDay;         !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    CeilingFanWeek,          !- Name

    For: Weekdays,           !- DayType List 1

    CeilingFanWeekday,       !- Schedule:Day Name 1

    For: AllOtherDays,       !- DayType List 2

    CeilingFanWeekend;       !- Schedule:Day Name 2

 

Schedule:Week:Compact,

    MiscPlugLoadWeek,        !- Name

    For: AllDays,            !- DayType List 1

    MiscPlugLoadDay;         !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    CookingRangeWeek,        !- Name

    For: AllDays,            !- DayType List 1

    CookingRangeDay;         !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    DishwasherWeek,          !- Name

    For: Weekdays,           !- DayType List 1

    DishwasherWeekday,       !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    DishwasherVacation,      !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    DishwasherWeekend;       !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    ClothesWasherWeek,       !- Name

    For: Weekdays,           !- DayType List 1

    ClothesWasherWeekday,    !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    ClothesWasherVacation,   !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    ClothesWasherWeekend;    !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    ClothesDryerWeek,        !- Name

    For: Weekdays,           !- DayType List 1

    ClothesDryerWeekday,     !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    ClothesDryerVacation,    !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    ClothesDryerWeekend;     !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    SinksWeek,               !- Name

    For: Weekdays,           !- DayType List 1

    SinksWeekday,            !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    SinksVacation,           !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    SinksWeekend;            !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    ShowersWeek,             !- Name

    For: Weekdays,           !- DayType List 1

    ShowersWeekday,          !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    ShowersVacation,         !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    ShowersWeekend;          !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    BathsWeek,               !- Name

    For: Weekdays,           !- DayType List 1

    BathsWeekday,            !- Schedule:Day Name 1

    For: CustomDay1,         !- DayType List 2

    BathsVacation,           !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    BathsWeekend;            !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    DHWDistWeek,             !- Name

    For: AllDays,            !- DayType List 1

    DHWDistDay;              !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    WeekHeatingSP,           !- Name

    For: Weekdays,           !- DayType List 1

    WkDayHeatingSP,          !- Schedule:Day Name 1

    For: WinterDesignDay,    !- DayType List 2

    HDDHeatingSP,            !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    WkEndHeatingSP;          !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    WeekCoolingSP,           !- Name

    For: Weekdays,           !- DayType List 1

    WkDayCoolingSP,          !- Schedule:Day Name 1

    For: SummerDesignDay,    !- DayType List 2

    CDDHeatingSP,            !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    WkEndCoolingSP;          !- Schedule:Day Name 3

 

Schedule:Week:Compact,

    BathExhaustWeek,         !- Name

    For: AllDays,            !- DayType List 1

    BathExhaustDay;          !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    RangeHoodWeek,           !- Name

    For: AllDays,            !- DayType List 1

    RangeHoodDay;            !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    ClothesDryerExhaustWeek, !- Name

    For: AllDays,            !- DayType List 1

    ClothesDryerExhaustDay;  !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    NatVentTempWeek,         !- Name

    For: Weekdays,           !- DayType List 1

    NatVentTempWeekday,      !- Schedule:Day Name 1

    For: AllOtherDays,       !- DayType List 2

    NatVentTempWeekend;      !- Schedule:Day Name 2

 

Schedule:Week:Compact,

    NatVentOffSeason-Week,   !- Name

    For: AllDays,            !- DayType List 1

    NatVentOff-Day;          !- Schedule:Day Name 1

 

Schedule:Week:Compact,

    NatVentOnSeason-Week,    !- Name

    For: Weekdays,           !- DayType List 1

    NatVentOn-Day,           !- Schedule:Day Name 1

    For: Weekends,           !- DayType List 2

    NatVentOn-Day,           !- Schedule:Day Name 2

    For: AllOtherDays,       !- DayType List 3

    NatVentOff-Day;          !- Schedule:Day Name 3

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:YEAR ===========

 

Schedule:Year,

    Occupancy,               !- Name

    Fraction,                !- Schedule Type Limits Name

    OccupancyWeek,           !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    InteriorLightingProfile, !- Name

    Fraction,                !- Schedule Type Limits Name

    InteriorLightingProfileWeek1,  !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    1,                       !- End Month 1

    31,                      !- End Day 1

    InteriorLightingProfileWeek2,  !- Schedule:Week Name 2

    2,                       !- Start Month 2

    1,                       !- Start Day 2

    2,                       !- End Month 2

    28,                      !- End Day 2

    InteriorLightingProfileWeek3,  !- Schedule:Week Name 3

    3,                       !- Start Month 3

    1,                       !- Start Day 3

    3,                       !- End Month 3

    31,                      !- End Day 3

    InteriorLightingProfileWeek4,  !- Schedule:Week Name 4

    4,                       !- Start Month 4

    1,                       !- Start Day 4

    4,                       !- End Month 4

    30,                      !- End Day 4

    InteriorLightingProfileWeek5,  !- Schedule:Week Name 5

    5,                       !- Start Month 5

    1,                       !- Start Day 5

    5,                       !- End Month 5

    31,                      !- End Day 5

    InteriorLightingProfileWeek6,  !- Schedule:Week Name 6

    6,                       !- Start Month 6

    1,                       !- Start Day 6

    6,                       !- End Month 6

    30,                      !- End Day 6

    InteriorLightingProfileWeek7,  !- Schedule:Week Name 7

    7,                       !- Start Month 7

    1,                       !- Start Day 7

    7,                       !- End Month 7

    31,                      !- End Day 7

    InteriorLightingProfileWeek8,  !- Schedule:Week Name 8

    8,                       !- Start Month 8

    1,                       !- Start Day 8

    8,                       !- End Month 8

    31,                      !- End Day 8

    InteriorLightingProfileWeek9,  !- Schedule:Week Name 9

    9,                       !- Start Month 9

    1,                       !- Start Day 9

    9,                       !- End Month 9

    30,                      !- End Day 9

    InteriorLightingProfileWeek10,  !- Schedule:Week Name 10

    10,                      !- Start Month 10

    1,                       !- Start Day 10

    10,                      !- End Month 10

    31,                      !- End Day 10

    InteriorLightingProfileWeek11,  !- Schedule:Week Name 11

    11,                      !- Start Month 11

    1,                       !- Start Day 11

    11,                      !- End Month 11

    30,                      !- End Day 11

    InteriorLightingProfileWeek12,  !- Schedule:Week Name 12

    12,                      !- Start Month 12

    1,                       !- Start Day 12

    12,                      !- End Month 12

    31;                      !- End Day 12

 

Schedule:Year,

    GarageLightingProfile,   !- Name

    Fraction,                !- Schedule Type Limits Name

    GarageLightingProfileWeek1,  !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    1,                       !- End Month 1

    31,                      !- End Day 1

    GarageLightingProfileWeek2,  !- Schedule:Week Name 2

    2,                       !- Start Month 2

    1,                       !- Start Day 2

    2,                       !- End Month 2

    28,                      !- End Day 2

    GarageLightingProfileWeek3,  !- Schedule:Week Name 3

    3,                       !- Start Month 3

    1,                       !- Start Day 3

    3,                       !- End Month 3

    31,                      !- End Day 3

    GarageLightingProfileWeek4,  !- Schedule:Week Name 4

    4,                       !- Start Month 4

    1,                       !- Start Day 4

    4,                       !- End Month 4

    30,                      !- End Day 4

    GarageLightingProfileWeek5,  !- Schedule:Week Name 5

    5,                       !- Start Month 5

    1,                       !- Start Day 5

    5,                       !- End Month 5

    31,                      !- End Day 5

    GarageLightingProfileWeek6,  !- Schedule:Week Name 6

    6,                       !- Start Month 6

    1,                       !- Start Day 6

    6,                       !- End Month 6

    30,                      !- End Day 6

    GarageLightingProfileWeek7,  !- Schedule:Week Name 7

    7,                       !- Start Month 7

    1,                       !- Start Day 7

    7,                       !- End Month 7

    31,                      !- End Day 7

    GarageLightingProfileWeek8,  !- Schedule:Week Name 8

    8,                       !- Start Month 8

    1,                       !- Start Day 8

    8,                       !- End Month 8

    31,                      !- End Day 8

    GarageLightingProfileWeek9,  !- Schedule:Week Name 9

    9,                       !- Start Month 9

    1,                       !- Start Day 9

    9,                       !- End Month 9

    30,                      !- End Day 9

    GarageLightingProfileWeek10,  !- Schedule:Week Name 10

    10,                      !- Start Month 10

    1,                       !- Start Day 10

    10,                      !- End Month 10

    31,                      !- End Day 10

    GarageLightingProfileWeek11,  !- Schedule:Week Name 11

    11,                      !- Start Month 11

    1,                       !- Start Day 11

    11,                      !- End Month 11

    30,                      !- End Day 11

    GarageLightingProfileWeek12,  !- Schedule:Week Name 12

    12,                      !- Start Month 12

    1,                       !- Start Day 12

    12,                      !- End Month 12

    31;                      !- End Day 12

 

Schedule:Year,

    ExteriorLightingProfile, !- Name

    Fraction,                !- Schedule Type Limits Name

    ExteriorLightingProfileWeek1,  !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    1,                       !- End Month 1

    31,                      !- End Day 1

    ExteriorLightingProfileWeek2,  !- Schedule:Week Name 2

    2,                       !- Start Month 2

    1,                       !- Start Day 2

    2,                       !- End Month 2

    28,                      !- End Day 2

    ExteriorLightingProfileWeek3,  !- Schedule:Week Name 3

    3,                       !- Start Month 3

    1,                       !- Start Day 3

    3,                       !- End Month 3

    31,                      !- End Day 3

    ExteriorLightingProfileWeek4,  !- Schedule:Week Name 4

    4,                       !- Start Month 4

    1,                       !- Start Day 4

    4,                       !- End Month 4

    30,                      !- End Day 4

    ExteriorLightingProfileWeek5,  !- Schedule:Week Name 5

    5,                       !- Start Month 5

    1,                       !- Start Day 5

    5,                       !- End Month 5

    31,                      !- End Day 5

    ExteriorLightingProfileWeek6,  !- Schedule:Week Name 6

    6,                       !- Start Month 6

    1,                       !- Start Day 6

    6,                       !- End Month 6

    30,                      !- End Day 6

    ExteriorLightingProfileWeek7,  !- Schedule:Week Name 7

    7,                       !- Start Month 7

    1,                       !- Start Day 7

    7,                       !- End Month 7

    31,                      !- End Day 7

    ExteriorLightingProfileWeek8,  !- Schedule:Week Name 8

    8,                       !- Start Month 8

    1,                       !- Start Day 8

    8,                       !- End Month 8

    31,                      !- End Day 8

    ExteriorLightingProfileWeek9,  !- Schedule:Week Name 9

    9,                       !- Start Month 9

    1,                       !- Start Day 9

    9,                       !- End Month 9

    30,                      !- End Day 9

    ExteriorLightingProfileWeek10,  !- Schedule:Week Name 10

    10,                      !- Start Month 10

    1,                       !- Start Day 10

    10,                      !- End Month 10

    31,                      !- End Day 10

    ExteriorLightingProfileWeek11,  !- Schedule:Week Name 11

    11,                      !- Start Month 11

    1,                       !- Start Day 11

    11,                      !- End Month 11

    30,                      !- End Day 11

    ExteriorLightingProfileWeek12,  !- Schedule:Week Name 12

    12,                      !- Start Month 12

    1,                       !- Start Day 12

    12,                      !- End Month 12

    31;                      !- End Day 12

 

Schedule:Year,

    Refrigerator,            !- Name

    Fraction,                !- Schedule Type Limits Name

    RefrigeratorWeek,        !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    CeilingFansSetup,        !- Name

    On/Off,                  !- Schedule Type Limits Name

    CeilingFanWeek,          !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    MiscPlugLoad,            !- Name

    Multiplier,              !- Schedule Type Limits Name

    MiscPlugLoadWeek,        !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    CookingRange,            !- Name

    Fraction,                !- Schedule Type Limits Name

    CookingRangeWeek,        !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    Dishwasher,              !- Name

    Fraction,                !- Schedule Type Limits Name

    DishwasherWeek,          !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    ClothesWasher,           !- Name

    Fraction,                !- Schedule Type Limits Name

    ClothesWasherWeek,       !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    ClothesDryer,            !- Name

    Fraction,                !- Schedule Type Limits Name

    ClothesDryerWeek,        !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    Sinks,                   !- Name

    Fraction,                !- Schedule Type Limits Name

    SinksWeek,               !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    Showers,                 !- Name

    Fraction,                !- Schedule Type Limits Name

    ShowersWeek,             !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    Baths,                   !- Name

    Fraction,                !- Schedule Type Limits Name

    BathsWeek,               !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    DHWDist,                 !- Name

    Fraction,                !- Schedule Type Limits Name

    DHWDistWeek,             !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    HeatingSetPoint,         !- Name

    Temperature,             !- Schedule Type Limits Name

    WeekHeatingSP,           !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    CoolingSetPoint,         !- Name

    Temperature,             !- Schedule Type Limits Name

    WeekCoolingSP,           !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    BathExhaust,             !- Name

    Fraction,                !- Schedule Type Limits Name

    BathExhaustWeek,         !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    RangeHood,               !- Name

    Fraction,                !- Schedule Type Limits Name

    RangeHoodWeek,           !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    ClothesDryerExhaust,     !- Name

    Fraction,                !- Schedule Type Limits Name

    ClothesDryerExhaustWeek, !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    NatVentTemp,             !- Name

    Temperature,             !- Schedule Type Limits Name

    NatVentTempWeek,         !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    12,                      !- End Month 1

    31;                      !- End Day 1

 

Schedule:Year,

    NatVentAvailability,     !- Name

    Fraction,                !- Schedule Type Limits Name

    NatVentOffSeason-Week,   !- Schedule:Week Name 1

    1,                       !- Start Month 1

    1,                       !- Start Day 1

    5,                       !- End Month 1

    31,                      !- End Day 1

    NatVentOnSeason-Week,    !- Schedule:Week Name 2

    6,                       !- Start Month 2

    1,                       !- Start Day 2

    9,                       !- End Month 2

    30,                      !- End Day 2

    NatVentOffSeason-Week,   !- Schedule:Week Name 3

    10,                      !- Start Month 3

    1,                       !- Start Day 3

    12,                      !- End Month 3

    31;                      !- End Day 3

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========

 

Schedule:Compact,

    WindowShadingSchedule,   !- Name

    Fraction,                !- Schedule Type Limits Name

    Through: Jan 31,         !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 0,         !- Field 4

    Through: Feb 28,         !- Field 5

    For: AllDays,            !- Field 6

    Until: 24:00, 0,         !- Field 8

    Through: Mar 31,         !- Field 9

    For: AllDays,            !- Field 10

    Until: 24:00, 0,         !- Field 12

    Through: Apr 30,         !- Field 13

    For: AllDays,            !- Field 14

    Until: 24:00, 0,         !- Field 16

    Through: May 31,         !- Field 17

    For: AllDays,            !- Field 18

    Until: 24:00, 0,         !- Field 20

    Through: Jun 30,         !- Field 21

    For: AllDays,            !- Field 22

    Until: 24:00, 1,         !- Field 24

    Through: Jul 31,         !- Field 25

    For: AllDays,            !- Field 26

    Until: 24:00, 1,         !- Field 28

    Through: Aug 31,         !- Field 29

    For: AllDays,            !- Field 30

    Until: 24:00, 1,         !- Field 32

    Through: Sep 30,         !- Field 33

    For: AllDays,            !- Field 34

    Until: 24:00, 1,         !- Field 36

    Through: Oct 31,         !- Field 37

    For: AllDays,            !- Field 38

    Until: 24:00, 1,         !- Field 40

    Through: Nov 30,         !- Field 41

    For: AllDays,            !- Field 42

    Until: 24:00, 0,         !- Field 44

    Through:Dec 31,          !- Field 45

    For: AllDays,            !- Field 46

    Until: 24:00, 0;         !- Field 48

 

Schedule:Compact,

    CoolingSeasonSchedule,   !- Name

    On/Off,                  !- Schedule Type Limits Name

    Through: Jan 31,         !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 0,         !- Field 4

    Through: Feb 28,         !- Field 5

    For: AllDays,            !- Field 6

    Until: 24:00, 0,         !- Field 8

    Through: Mar 31,         !- Field 9

    For: AllDays,            !- Field 10

    Until: 24:00, 0,         !- Field 12

    Through: Apr 30,         !- Field 13

    For: AllDays,            !- Field 14

    Until: 24:00, 0,         !- Field 16

    Through: May 31,         !- Field 17

    For: AllDays,            !- Field 18

    Until: 24:00, 0,         !- Field 20

    Through: Jun 30,         !- Field 21

    For: AllDays,            !- Field 22

    Until: 24:00, 1,         !- Field 24

    Through: Jul 31,         !- Field 25

    For: AllDays,            !- Field 26

    Until: 24:00, 1,         !- Field 28

    Through: Aug 31,         !- Field 29

    For: AllDays,            !- Field 30

    Until: 24:00, 1,         !- Field 32

    Through: Sep 30,         !- Field 33

    For: AllDays,            !- Field 34

    Until: 24:00, 1,         !- Field 36

    Through: Oct 31,         !- Field 37

    For: AllDays,            !- Field 38

    Until: 24:00, 1,         !- Field 40

    Through: Nov 30,         !- Field 41

    For: AllDays,            !- Field 42

    Until: 24:00, 0,         !- Field 44

    Through:Dec 31,          !- Field 45

    For: AllDays,            !- Field 46

    Until: 24:00, 0;         !- Field 48

 

Schedule:Compact,

    HeatingSeasonSchedule,   !- Name

    On/Off,                  !- Schedule Type Limits Name

    Through: Jan 31,         !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 1,         !- Field 4

   Through: Feb 28,         !- Field 5

    For: AllDays,            !- Field 6

    Until: 24:00, 1,         !- Field 8

    Through: Mar 31,         !- Field 9

    For: AllDays,            !- Field 10

    Until: 24:00, 1,         !- Field 12

    Through: Apr 30,         !- Field 13

    For: AllDays,            !- Field 14

    Until: 24:00, 1,         !- Field 16

    Through: May 31,         !- Field 17

    For: AllDays,            !- Field 18

    Until: 24:00, 1,         !- Field 20

    Through: Jun 30,         !- Field 21

    For: AllDays,            !- Field 22

    Until: 24:00, 1,         !- Field 24

    Through: Jul 31,         !- Field 25

    For: AllDays,            !- Field 26

    Until: 24:00, 1,         !- Field 28

    Through: Aug 31,         !- Field 29

    For: AllDays,            !- Field 30

    Until: 24:00, 0,         !- Field 32

    Through: Sep 30,         !- Field 33

    For: AllDays,            !- Field 34

    Until: 24:00, 0,         !- Field 36

    Through: Oct 31,         !- Field 37

    For: AllDays,            !- Field 38

    Until: 24:00, 1,         !- Field 40

    Through: Nov 30,         !- Field 41

    For: AllDays,            !- Field 42

    Until: 24:00, 1,         !- Field 44

    Through:Dec 31,          !- Field 45

    For: AllDays,            !- Field 46

    Until: 24:00, 1;         !- Field 48

 

Schedule:Compact,

    RelativeHumiditySetpoint,!- Name

    RelativeHumidity,        !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For:AllDays,             !- Field 2

    Until: 24:00, 55;        !- Field 4

 

Schedule:Compact,

    Work Eff Sch,            !- Name

    AnyNumber,               !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 0.0;       !- Field 4

 

Schedule:Compact,

    Clothing Sch,            !- Name

    AnyNumber,               !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 1.0;       !- Field 4

 

Schedule:Compact,

    Air Velo Sch,            !- Name

    AnyNumber,               !- Schedule Type Limits Name

    Through: 12/31,          !- Field 1

    For: AllDays,            !- Field 2

    Until: 24:00, 0.137;     !- Field 4

 

 

!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:CONSTANT ===========

 

Schedule:Constant,Occupant Activity,Multiplier,112.5504;

Schedule:Constant,CeilingFansMaster,On/Off,1;

Schedule:Constant,DWWaterTempSchedule,Temperature,54.4444444444445;

Schedule:Constant,CWWaterTempSchedule,Temperature,33.6111111111111;

Schedule:Constant,SinkSensSchedule,Fraction,0.687777777777778;

Schedule:Constant,SinkLatSchedule,Fraction,0.312222222222222;

Schedule:Constant,ShowerSensSchedule,Fraction,0.51280276816609;

Schedule:Constant,ShowerLatSchedule,Fraction,0.48719723183391;

Schedule:Constant,BathSensSchedule,Fraction,1;

Schedule:Constant,BathLatSchedule,Fraction,0;

Schedule:Constant,SSBWaterTempSchedule,Temperature,43.3333333333334;

Schedule:Constant,LivingZoneControl,Multiplier,4;

Schedule:Constant,SupplyFanOperation,Multiplier,0;

Schedule:Constant,SupplyFanAvailability,Fraction,1.0;

Schedule:Constant,WaterHeaterSP1Schedule,Temperature,54.4444444444445;

Schedule:Constant,WaterHeaterSP2Schedule,Temperature,54.4444444444445;

Schedule:Constant,DHWSupplySetpoint,Temperature,54.4444444444445;

Schedule:Constant,AlwaysOff,Fraction,0.0;

Schedule:Constant,AlwaysOn,Fraction,1.0;

 

!-   ===========  ALL OBJECTS IN CLASS: MATERIAL ===========

 

 

Material,

    Soil-12in,               !- Name

    Rough,                   !- Roughness

    0.3048,                  !- Thickness {m}

    1.731,                   !- Conductivity {W/m-K}

    1842.3,                  !- Density {kg/m3}

    232.6;                   !- Specific Heat {J/kg-K}

 

Material,

    Concrete-4in,            !- Name

    Rough,                   !- Roughness

    0.1016,                  !- Thickness {m}

    1.3114056,               !- Conductivity {W/m-K}

    2242.8,                  !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9;                     !- Thermal Absorptance

 

Material,

    Concrete-8in,            !- Name

    Rough,                   !- Roughness

    0.1016,                  !- Thickness {m}

    1.3114056,               !- Conductivity {W/m-K}

    2242.8,                  !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9;                     !- Thermal Absorptance

 

Material,

    Plywood-3_4in,           !- Name

    Rough,                   !- Roughness

    0.01905,                 !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    Plywood-1_2in,           !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    WoodFlooring,            !- Name

    Rough,                   !- Roughness

    0.01905,                 !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54,                  !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.6;                     !- Solar Absorptance

 

Material,

    StudandAirWall,          !- Name

    Rough,                   !- Roughness

    0.0889000000000001,      !- Thickness {m}

    0.442568232,             !- Conductivity {W/m-K}

    49.1353302765878,        !- Density {kg/m3}

    569.143125;              !- Specific Heat {J/kg-K}

 

Material,

    ExteriorFinish,          !- Name

    Rough,                   !- Roughness

    0.0254,                  !- Thickness {m}

    0.649125,                !- Conductivity {W/m-K}

    1281.6,                  !- Density {kg/m3}

    488.46,                  !- Specific Heat {J/kg-K}

    0.90,                    !- Thermal Absorptance

    0.75,                    !- Solar Absorptance

    0.75;                    !- Visible Absorptance

 

Material,

    GypsumBoard-1_2in,       !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.1602906,               !- Conductivity {W/m-K}

    801,                     !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.5,                     !- Solar Absorptance

    0.1;                     !- Visible Absorptance

 

Material,

    GypsumBoard-ExtWall,     !- Name

    Rough,                   !- Roughness

    0.01271016,              !- Thickness {m}

    0.1602906,               !- Conductivity {W/m-K}

    801,                     !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.5,                     !- Solar Absorptance

    0.1;                     !- Visible Absorptance

 

Material,

    GypsumBoard-Ceiling,     !- Name

    Rough,                   !- Roughness

    0.01271016,              !- Thickness {m}

    0.1602906,               !- Conductivity {W/m-K}

    801,                     !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.3,                     !- Solar Absorptance

    0.1;                     !- Visible Absorptance

 

Material,

    PartitionWallMass,       !- Name

    Rough,                   !- Roughness

    0.01271016,              !- Thickness {m}

    0.1602906,               !- Conductivity {W/m-K}

    801,                     !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.5,                     !- Solar Absorptance

    0.1;                     !- Visible Absorptance

 

Material,

    FloorMass,               !- Name

    Rough,                   !- Roughness

    0.015875,                !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    544.68,                  !- Density {kg/m3}

    674.54,                  !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.6;                     !- Solar Absorptance

 

Material,

    RadiantBarrier,          !- Name

    Rough,                   !- Roughness

    0.00021336,              !- Thickness {m}

    235.0698,                !- Conductivity {W/m-K}

    2700.972,                !- Density {kg/m3}

    511.72,                  !- Specific Heat {J/kg-K}

    0.05,                    !- Thermal Absorptance

    0.05,                    !- Solar Absorptance

    0.05;                    !- Visible Absorptance

 

Material,

    RoofingMaterial,         !- Name

    Rough,                   !- Roughness

    0.0094488,               !- Thickness {m}

    0.162714,                !- Conductivity {W/m-K}

    1121.4,                  !- Density {kg/m3}

    814.1,                   !- Specific Heat {J/kg-K}

    0.93,                    !- Thermal Absorptance

    0.30,                    !- Solar Absorptance

    0.30;                    !- Visible Absorptance

 

Material,

    ExtSheathing,            !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.827418,                !- Conductivity {W/m-K}

    1602,                    !- Density {kg/m3}

    465.2;                   !- Specific Heat {J/kg-K}

 

Material,

    SplineLayer,             !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.0390513731568347,      !- Conductivity {W/m-K}

    147.0636,                !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    WallIns,                 !- Name

    Rough,                   !- Roughness

    0.482599999999999,       !- Thickness {m}

    0.0424831599939698,      !- Conductivity {W/m-K}

    107.0136,                !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    IntSheathing,            !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.827418,                !- Conductivity {W/m-K}

    1602,                    !- Density {kg/m3}

    465.2;                   !- Specific Heat {J/kg-K}

 

Material,

    IntWallIns,              !- Name

    Rough,                   !- Roughness

    0.1397,                  !- Thickness {m}

    0.0561349688826466,      !- Conductivity {W/m-K}

    124.53147,               !- Density {kg/m3}

    601.82924;               !- Specific Heat {J/kg-K}

 

Material,

    StudandAirFloor,         !- Name

    Rough,                   !- Roughness

    0.0889000000000001,      !- Thickness {m}

    0.448792750636365,       !- Conductivity {W/m-K}

    67.6755170655243,        !- Density {kg/m3}

    573.359;                 !- Specific Heat {J/kg-K}

 

Material,

    IntFloorIns,             !- Name

    Rough,                   !- Roughness

    0.1397,                  !- Thickness {m}

    0.0508287148038404,      !- Conductivity {W/m-K}

    80.5806,                 !- Density {kg/m3}

    593.5952;                !- Specific Heat {J/kg-K}

 

Material,

    AddforCTFCalc,           !- Name

    Rough,                   !- Roughness

    0.0127,                  !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    UARoofIns,               !- Name

    Rough,                   !- Roughness

    0.2413,                  !- Thickness {m}

    0.0288500000000001,      !- Conductivity {W/m-K}

    16.02,                   !- Density {kg/m3}

    581.5;                   !- Specific Heat {J/kg-K}

 

Material,

    RoofIns,                 !- Name

    Rough,                   !- Roughness

    0.1397,                  !- Thickness {m}

    0.808833375978492,       !- Conductivity {W/m-K}

    45.8172,                 !- Density {kg/m3}

    587.0824;                !- Specific Heat {J/kg-K}

 

Material,

    StudandAirRoof,          !- Name

    Rough,                   !- Roughness

    0.0889000000000001,      !- Thickness {m}

    0.412591379855094,       !- Conductivity {W/m-K}

    57.446448492318,         !- Density {kg/m3}

   571.033;                 !- Specific Heat {J/kg-K}

 

Material,

    GrgRoofStudandAir,       !- Name

    Rough,                   !- Roughness

    0.0889000000000001,      !- Thickness {m}

    2.97789889242416,        !- Conductivity {W/m-K}

    57.446448492318,         !- Density {kg/m3}

    571.033;                 !- Specific Heat {J/kg-K}

 

Material,

    DoorMaterial,            !- Name

    Rough,                   !- Roughness

    0.0633984,               !- Thickness {m}

    0.0873267038564154,      !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    GarageDoorMaterial,      !- Name

    Rough,                   !- Roughness

    0.0633984,               !- Thickness {m}

    0.0873267038564154,      !- Conductivity {W/m-K}

    512.64,                  !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    Mat-Fic-Slab,            !- Name

    Rough,                   !- Roughness

    0.0254,                  !- Thickness {m}

    0.0289710585028547,      !- Conductivity {W/m-K}

    40.05,                   !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

Material,

    SlabMass,                !- Name

    Rough,                   !- Roughness

    0.1016,                  !- Thickness {m}

    0.40010334,              !- Conductivity {W/m-K}

    2242.8,                  !- Density {kg/m3}

    465.2,                   !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.6;                     !- Solar Absorptance

 

Material,

    SlabSoil-12in,           !- Name

    Rough,                   !- Roughness

    0.3048,                  !- Thickness {m}

    1.731,                   !- Conductivity {W/m-K}

    1842.3,                  !- Density {kg/m3}

    232.6;                   !- Specific Heat {J/kg-K}

 

Material,

    LivingFurnitureMaterial, !- Name

    Rough,                   !- Roughness

    0.1524,                  !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    640.8,                   !- Density {kg/m3}

    674.54,                  !- Specific Heat {J/kg-K}

    0.9,                     !- Thermal Absorptance

    0.6,                     !- Solar Absorptance

    0.1;                     !- Visible Absorptance

 

Material,

    GarageFurnitureMaterial, !- Name

    Rough,                   !- Roughness

    0.1524,                  !- Thickness {m}

    0.1154577,               !- Conductivity {W/m-K}

    640.8,                   !- Density {kg/m3}

    674.54;                  !- Specific Heat {J/kg-K}

 

 

!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========

 

Material:NoMass,

    Adiabatic,               !- Name

    Rough,                   !- Roughness

    176.1;                   !- Thermal Resistance {m2-K/W}

 

 

!-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:SIMPLEGLAZINGSYSTEM ===========

 

WindowMaterial:SimpleGlazingSystem,

    Built-Up-Window,         !- Name

    0.79492,                 !- U-Factor {W/m2-K}

    0.17;                    !- Solar Heat Gain Coefficient

 

 

!-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:SHADE ===========

 

WindowMaterial:Shade,

    CoolingShade,            !- Name

    0.713571428571429,       !- Solar Transmittance

    0.286418571428571,       !- Solar Reflectance

    0.713571428571429,       !- Visible Transmittance

    0.286418571428571,       !- Visible Reflectance

    0.00001,                 !- Thermal Hemispherical Emissivity

    0.713571428571429,       !- Thermal Transmittance

    0.0001,                  !- Thickness {m}

    10000,                   !- Conductivity {W/m-K}

    0.001,                   !- Shade to Glass Distance {m}

    0,                       !- Top Opening Multiplier

    0,                       !- Bottom Opening Multiplier

    0,                       !- Left-Side Opening Multiplier

    0,                       !- Right-Side Opening Multiplier

    0;                       !- Airflow Permeability

 

 

!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========

 

Construction,

    Slab,                    !- Name

    Mat-Fic-Slab,            !- Outside Layer

    SlabSoil-12in,           !- Layer 2

    SlabMass;                !- Layer 3

 

Construction,

    GrndUninsUnfinGFloor,    !- Name

    Adiabatic,               !- Outside Layer

    Soil-12in,               !- Layer 2

    Concrete-4in;            !- Layer 3

 

Construction,

    ExtInsFinWall,           !- Name

    ExteriorFinish,          !- Outside Layer

    ExtSheathing,            !- Layer 2

    SplineLayer,             !- Layer 3

    WallIns,                 !- Layer 4

    SplineLayer,             !- Layer 5

    IntSheathing,            !- Layer 6

    GypsumBoard-ExtWall;     !- Layer 7

 

Construction,

    ExtInsUnfinWall,         !- Name

    ExteriorFinish,          !- Outside Layer

    ExtSheathing,            !- Layer 2

    SplineLayer,             !- Layer 3

    WallIns,                 !- Layer 4

    SplineLayer,             !- Layer 5

    IntSheathing;            !- Layer 6

 

Construction,

    UnfinInsFinWall,         !- Name

    IntWallIns,              !- Outside Layer

    PartitionWallMass;       !- Layer 2

 

Construction,

    RevUnfinInsFinWall,      !- Name

    PartitionWallMass,       !- Outside Layer

    IntWallIns;              !- Layer 2

 

Construction,

    UnfinInsUnfinWall,       !- Name

    IntWallIns;              !- Outside Layer

 

Construction,

    RevUnfinInsUnfinWall,    !- Name

    IntWallIns;              !- Outside Layer

 

Construction,

    ExtUninsUnfinWall,       !- Name

    ExteriorFinish,          !- Outside Layer

    Plywood-1_2in,           !- Layer 2

    StudandAirWall;          !- Layer 3

 

Construction,

    FinUninsFinWall,         !- Name

    PartitionWallMass,       !- Outside Layer

    StudandAirWall,          !- Layer 2

    PartitionWallMass;       !- Layer 3

 

Construction,

    RevFinUninsFinWall,      !- Name

    PartitionWallMass,       !- Outside Layer

    StudandAirWall,          !- Layer 2

    PartitionWallMass;       !- Layer 3

 

Construction,

    UnfinUninsFinWall,       !- Name

    StudandAirWall,          !- Outside Layer

    PartitionWallMass;       !- Layer 2

 

Construction,

    RevUnfinUninsFinWall,    !- Name

    PartitionWallMass,       !- Outside Layer

    StudandAirWall;          !- Layer 2

 

Construction,

    UnfinUninsUnfinWall,     !- Name

    StudandAirWall,          !- Outside Layer

    Plywood-1_2in;           !- Layer 2

 

Construction,

    RevUnfinUninsUnfinWall,  !- Name

    Plywood-1_2in,           !- Outside Layer

    StudandAirWall;          !- Layer 2

 

Construction,

    FinUninsFinFloor,        !- Name

    GypsumBoard-Ceiling,     !- Outside Layer

   StudandAirFloor,         !- Layer 2

    Plywood-3_4in,           !- Layer 3

    FloorMass;               !- Layer 4

 

Construction,

    RevFinUninsFinFloor,     !- Name

    FloorMass,               !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    StudandAirFloor,         !- Layer 3

    GypsumBoard-Ceiling;     !- Layer 4

 

Construction,

    UnfinUninsUnfinFloor,    !- Name

    StudandAirFloor,         !- Outside Layer

    Plywood-3_4in;           !- Layer 2

 

Construction,

    RevUnfinUninsUnfinFloor, !- Name

    Plywood-3_4in,           !- Outside Layer

    StudandAirFloor;         !- Layer 2

 

Construction,

    UnfinInsFinFloor,        !- Name

    IntFloorIns,             !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    FloorMass;               !- Layer 3

 

Construction,

    RevUnfinInsFinFloor,     !- Name

    FloorMass,               !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    IntFloorIns;             !- Layer 3

 

Construction,

    UnfinInsUnfinFloor,      !- Name

    IntFloorIns,             !- Outside Layer

    Plywood-3_4in;           !- Layer 2

 

Construction,

    RevUnfinInsUnfinFloor,   !- Name

    Plywood-3_4in,           !- Outside Layer

    IntFloorIns;             !- Layer 2

 

Construction,

    FinInsUnfinUAFloor,      !- Name

    GypsumBoard-Ceiling,     !- Outside Layer

    AddforCTFCalc;           !- Layer 2

 

Construction,

    RevFinInsUnfinUAFloor,   !- Name

    AddforCTFCalc,           !- Outside Layer

    GypsumBoard-Ceiling;     !- Layer 2

 

Construction,

    UnfinInsExtRoof,         !- Name

    RoofingMaterial,         !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    UARoofIns,               !- Layer 3

    RadiantBarrier;          !- Layer 4

 

Construction,

    FinInsExtRoof,           !- Name

    RoofingMaterial,         !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    RoofIns,                 !- Layer 3

    GypsumBoard-Ceiling;     !- Layer 4

 

Construction,

    UnfinUninsExtRoof,       !- Name

    RoofingMaterial,         !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    StudandAirRoof,          !- Layer 3

    RadiantBarrier;          !- Layer 4

 

Construction,

    UnfinUninsExtGrgRoof,    !- Name

   RoofingMaterial,         !- Outside Layer

    Plywood-3_4in,           !- Layer 2

    GrgRoofStudandAir,       !- Layer 3

    RadiantBarrier;          !- Layer 4

 

Construction,

    AdiabaticConst,          !- Name

    Adiabatic;               !- Outside Layer

 

Construction,

    Windows,                 !- Name

    Built-Up-Window;         !- Outside Layer

 

Construction,

    Doors,                   !- Name

    DoorMaterial;            !- Outside Layer

 

Construction,

    GarageDoor,              !- Name

    GarageDoorMaterial;      !- Outside Layer

 

Construction,

    LivingFurniture,         !- Name

    LivingFurnitureMaterial; !- Outside Layer

 

Construction,

    GarageFurniture,         !- Name

    GarageFurnitureMaterial; !- Outside Layer

 

 

!-   ===========  ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========

 

GlobalGeometryRules,

    LowerLeftCorner,         !- Starting Vertex Position

    CounterClockWise,        !- Vertex Entry Direction

    Relative;                !- Coordinate System

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========

 

Zone,

    Living,                  !- Name

    0,                       !- Direction of Relative North {deg}

    -5.334, -5.334, 0,                  !- X,Y,Z  {m}

    1,                       !- Type

    1,                       !- Multiplier

    5.4864,                  !- Ceiling Height {m}

    577.55808;               !- Volume {m3}

 

Zone,

    Garage,                  !- Name

    0,                       !- Direction of Relative North {deg}

    -5.334, 2.286, 0,                   !- X,Y,Z  {m}

    1,                       !- Type

    1,                       !- Multiplier

    4.2038016,               !- Ceiling Height {m}

    160.5744;                !- Volume {m3}

 

Zone,

    UnfinishedAttic,         !- Name

    0,                       !- Direction of Relative North {deg}

    -5.334, -5.334, 5.4864,             !- X,Y,Z  {m}

    ,                        !- Type

    ,                        !- Multiplier

    1.7145,                  !- Ceiling Height {m}

    85.38981264;             !- Volume {m3}

 

Zone,

    Dummy,                   !- Name

    0,                       !- Direction of Relative North {deg}

    0, 0, 0,                            !- X,Y,Z  {m}

    ,                        !- Type

    ,                        !- Multiplier

    0,                       !- Ceiling Height {m}

    0;                       !- Volume {m3}

 

Zone,

    RA Duct Zone,            !- Name

    0,                       !- Direction of Relative North {deg}

    0, 0, 0,                            !- X,Y,Z  {m}

    ,                        !- Type

    ,                        !- Multiplier

    0,                       !- Ceiling Height {m}

    0;                       !- Volume {m3}

 

 

!-   ===========  ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========

 

BuildingSurface:Detailed,

    Wall1,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 7.62, 0,                         !- X,Y,Z  1 {m}

    0, 0, 0,                            !- X,Y,Z  2 {m}

    0, 0, 2.7432,                       !- X,Y,Z  3 {m}

    0, 7.62, 2.7432;                    !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall2,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 0, 0,                            !- X,Y,Z  1 {m}

    3.9624, 0, 0,                       !- X,Y,Z  2 {m}

    3.9624, 0, 2.7432,                  !- X,Y,Z  3 {m}

    0, 0, 2.7432;                       !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall3,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    3.9624, 0, 0,                       !- X,Y,Z  1 {m}

    3.9624, -1.8288, 0,                 !- X,Y,Z  2 {m}

    3.9624, -1.8288, 2.7432,            !- X,Y,Z  3 {m}

    3.9624, 0, 2.7432;                  !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall4,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    3.9624, -1.8288, 0,                 !- X,Y,Z  1 {m}

    10.668, -1.8288, 0,                 !- X,Y,Z  2 {m}

    10.668, -1.8288, 2.7432,            !- X,Y,Z  3 {m}

    3.9624, -1.8288, 2.7432;            !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall5,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    10.668, -1.8288, 0,                 !- X,Y,Z  1 {m}

    10.668, 7.62, 0,                    !- X,Y,Z  2 {m}

    10.668, 7.62, 2.7432,               !- X,Y,Z  3 {m}

    10.668, -1.8288, 2.7432;            !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall6,                   !- Name

    Wall,                    !- Surface Type

    UnfinInsFinWall,         !- Construction Name

    Living,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    IntWall6,                !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 7.62, 0,                    !- X,Y,Z  1 {m}

    0, 7.62, 0,                         !- X,Y,Z  2 {m}

    0, 7.62, 2.7432,                    !- X,Y,Z  3 {m}

    6.4008, 7.62, 2.7432;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    IntWall6,                !- Name

    Wall,                    !- Surface Type

    RevUnfinInsFinWall,      !- Construction Name

    Garage,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    Wall6,                   !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 0, 0,                            !- X,Y,Z  1 {m}

    6.4008, 0, 0,                       !- X,Y,Z  2 {m}

    6.4008, 0, 2.7432,                  !- X,Y,Z  3 {m}

    0, 0, 2.7432;                       !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall7,                   !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    10.668, 7.62, 0,                    !- X,Y,Z  1 {m}

    6.4008, 7.62, 0,                    !- X,Y,Z  2 {m}

    6.4008, 7.62, 2.7432,               !- X,Y,Z  3 {m}

    10.668, 7.62, 2.7432;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall8,                   !- Name

    Wall,                    !- Surface Type

    ExtUninsUnfinWall,       !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 6.4008, 0,                       !- X,Y,Z  1 {m}

    0, 0, 0,                            !- X,Y,Z  2 {m}

    0, 0, 2.7432,                       !- X,Y,Z  3 {m}

    0, 6.4008, 2.7432;                  !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall9,                   !- Name

    Wall,                    !- Surface Type

    ExtUninsUnfinWall,       !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 0, 0,                       !- X,Y,Z  1 {m}

    6.4008, 6.4008, 0,                  !- X,Y,Z  2 {m}

    6.4008, 6.4008, 2.7432,             !- X,Y,Z  3 {m}

    6.4008, 0, 2.7432;                  !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall10,                  !- Name

    Wall,                    !- Surface Type

    ExtUninsUnfinWall,       !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 6.4008, 0,                  !- X,Y,Z  1 {m}

    0, 6.4008, 0,                       !- X,Y,Z  2 {m}

    0, 6.4008, 2.7432,                  !- X,Y,Z  3 {m}

    6.4008, 6.4008, 2.7432;             !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall11,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    5,                       !- Number of Vertices

    3.9624, 0, 2.7432,                  !- X,Y,Z  1 {m}

    3.9624, -1.8288, 2.7432,            !- X,Y,Z  2 {m}

    3.9624, -1.8288, 2.8703016,         !- X,Y,Z  3 {m}

    3.9624, -0.9144, 3.2513016,         !- X,Y,Z  4 {m}

    3.9624, 0, 2.8703016;               !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    Wall12,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 0, 2.7432,                       !- X,Y,Z  1 {m}

    3.9624, 0, 2.7432,                  !- X,Y,Z  2 {m}

    3.9624, 0, 2.8703016,               !- X,Y,Z  3 {m}

    0, 0, 2.8703016;                    !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall13,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 11.2776, 2.7432,                 !- X,Y,Z  1 {m}

    0, 0, 2.7432,                       !- X,Y,Z  2 {m}

    0, 0, 5.4864,                       !- X,Y,Z  3 {m}

    0, 11.2776, 5.4864;                 !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall14,                  !- Name

    Wall,                    !- Surface Type

    FinUninsFinWall,         !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    3.9624, 0, 2.7432,                  !- X,Y,Z  1 {m}

    7.0104, 0, 2.7432,                  !- X,Y,Z  2 {m}

    7.0104, 0, 2.8703016,               !- X,Y,Z  3 {m}

    3.9624, 0, 2.8703016;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    IntWall14,               !- Name

    Wall,                    !- Surface Type

    RevFinUninsFinWall,      !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    7.0104, 0, 2.7432,                  !- X,Y,Z  1 {m}

    3.9624, 0, 2.7432,                  !- X,Y,Z  2 {m}

    3.9624, 0, 2.8703016,               !- X,Y,Z  3 {m}

    7.0104, 0, 2.8703016;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall15,                  !- Name

    Wall,                    !- Surface Type

    FinUninsFinWall,         !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    5,                       !- Number of Vertices

    7.0104, 0, 2.7432,                  !- X,Y,Z  1 {m}

    7.0104, -1.8288, 2.7432,            !- X,Y,Z  2 {m}

    7.0104, -1.8288, 2.8703016,         !- X,Y,Z  3 {m}

    7.0104, -0.9144, 3.2513016,         !- X,Y,Z  4 {m}

    7.0104, 0, 2.8703016;               !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    IntWall15,               !- Name

    Wall,                    !- Surface Type

    RevFinUninsFinWall,      !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    5,                       !- Number of Vertices

    7.0104, -1.8288, 2.7432,            !- X,Y,Z  1 {m}

    7.0104, 0, 2.7432,                  !- X,Y,Z  2 {m}

    7.0104, 0, 2.8703016,               !- X,Y,Z  3 {m}

    7.0104, -0.9144, 3.2513016,         !- X,Y,Z  4 {m}

    7.0104, -1.8288, 2.8703016;         !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    Wall16,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    7.0104, -1.8288, 2.7432,            !- X,Y,Z  1 {m}

    10.668, -1.8288, 2.7432,            !- X,Y,Z  2 {m}

    10.668, -1.8288, 5.4864,            !- X,Y,Z  3 {m}

    7.0104, -1.8288, 5.4864;            !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall17,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    10.668, -1.8288, 2.7432,            !- X,Y,Z  1 {m}

    10.668, 7.62, 2.7432,               !- X,Y,Z  2 {m}

    10.668, 7.62, 5.4864,               !- X,Y,Z  3 {m}

    10.668, -1.8288, 5.4864;            !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall18,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    10.668, 7.62, 2.7432,               !- X,Y,Z  1 {m}

    6.4008, 7.62, 2.7432,               !- X,Y,Z  2 {m}

    6.4008, 7.62, 5.4864,               !- X,Y,Z  3 {m}

    10.668, 7.62, 5.4864;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall19,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 7.62, 2.7432,               !- X,Y,Z  1 {m}

    6.4008, 11.2776, 2.7432,            !- X,Y,Z  2 {m}

    6.4008, 11.2776, 5.4864,            !- X,Y,Z  3 {m}

    6.4008, 7.62, 5.4864;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall20,                  !- Name

    Wall,                    !- Surface Type

   UnfinInsFinWall,         !- Construction Name

    Living,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    IntWall20,               !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    5,                       !- Number of Vertices

    6.4008, 11.2776, 2.7432,            !- X,Y,Z  1 {m}

    0, 11.2776, 2.7432,                 !- X,Y,Z  2 {m}

    0, 11.2776, 2.8703016,              !- X,Y,Z  3 {m}

    3.2004, 11.2776, 4.2038016,         !- X,Y,Z  4 {m}

    6.4008, 11.2776, 2.8703016;         !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    IntWall20,               !- Name

    Wall,                    !- Surface Type

    RevUnfinInsFinWall,      !- Construction Name

    Garage,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    Wall20,                  !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    5,                       !- Number of Vertices

    0, 3.6576, 2.7432,                  !- X,Y,Z  1 {m}

    6.4008, 3.6576, 2.7432,             !- X,Y,Z  2 {m}

    6.4008, 3.6576, 2.8703016,          !- X,Y,Z  3 {m}

    3.2004, 3.6576, 4.2038016,          !- X,Y,Z  4 {m}

    0, 3.6576, 2.8703016;               !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    Wall22,                  !- Name

    Wall,                    !- Surface Type

    ExtUninsUnfinWall,       !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    6.7056, 6.4008, 2.7432,             !- X,Y,Z  1 {m}

    -0.3048, 6.4008, 2.7432,            !- X,Y,Z  2 {m}

    3.2004, 6.4008, 4.2038016;          !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Wall23,                  !- Name

    Wall,                    !- Surface Type

    ExtInsUnfinWall,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    6.7056, -1.8288, 0,                 !- X,Y,Z  1 {m}

    10.9728, -1.8288, 0,                !- X,Y,Z  2 {m}

    8.8392, -1.8288, 0.8891016;         !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Wall24,                  !- Name

    Wall,                    !- Surface Type

    ExtInsUnfinWall,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    6.7056, 11.2776, 0,                 !- X,Y,Z  1 {m}

    -0.3048, 11.2776, 0,                !- X,Y,Z  2 {m}

    3.2004, 11.2776, 1.4606016;         !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Wall25,                  !- Name

    Wall,                    !- Surface Type

    ExtInsUnfinWall,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    10.668, -0.3048, 0,                 !- X,Y,Z  1 {m}

    10.668, 7.9248, 0,                  !- X,Y,Z  2 {m}

    10.668, 3.81, 1.7145;               !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Wall26,                  !- Name

    Wall,                    !- Surface Type

    ExtInsUnfinWall,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    0, 7.9248, 0,                       !- X,Y,Z  1 {m}

    0, -0.3048, 0,                      !- X,Y,Z  2 {m}

    0, 3.81, 1.7145;                    !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Wall27,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    3.9624, 0, 2.8703016,               !- X,Y,Z  1 {m}

    3.9624, 0, 5.4864,                  !- X,Y,Z  2 {m}

    0, 0, 5.4864,                       !- X,Y,Z  3 {m}

    0, 0, 2.8703016;                    !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall28,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    7.0104, 0, 2.8703016,               !- X,Y,Z  1 {m}

    7.0104, 0, 5.4864,                  !- X,Y,Z  2 {m}

    3.9624, 0, 5.4864,                  !- X,Y,Z  3 {m}

    3.9624, 0, 2.8703016;               !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Wall29,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    5,                       !- Number of Vertices

    7.0104, -1.8288, 2.8703016,         !- X,Y,Z  1 {m}

    7.0104, -1.8288, 5.4864,            !- X,Y,Z  2 {m}

    7.0104, 0, 5.4864,                  !- X,Y,Z  3 {m}

    7.0104, 0, 2.8703016,               !- X,Y,Z  4 {m}

    7.0104, -0.9144, 3.2513016;         !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    Wall30,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    5,                       !- Number of Vertices

    0, 11.2776, 2.8703016,              !- X,Y,Z  1 {m}

    0, 11.2776, 5.4864,                 !- X,Y,Z  2 {m}

    6.4008, 11.2776, 5.4864,            !- X,Y,Z  3 {m}

    6.4008, 11.2776, 2.8703016,         !- X,Y,Z  4 {m}

    3.2004, 11.2776, 4.2038016;         !- X,Y,Z  5 {m}

 

BuildingSurface:Detailed,

    Wall31,                  !- Name

    Wall,                    !- Surface Type

    ExtInsFinWall,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    3,                       !- Number of Vertices

    0, 0.3048, 2.7432,                  !- X,Y,Z  1 {m}

    0, 0, 2.7432,                       !- X,Y,Z  2 {m}

    0, 0, 2.8703016;                    !- X,Y,Z  3 {m}

 

BuildingSurface:Detailed,

    Floor1,                  !- Name

    Floor,                   !- Surface Type

    Slab,                    !- Construction Name

    Living,                  !- Zone Name

    Ground,                  !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    6,                       !- Number of Vertices

    0, 7.62, 0,                         !- X,Y,Z  1 {m}

    10.668, 7.62, 0,                    !- X,Y,Z  2 {m}

    10.668, -1.8288, 0,                 !- X,Y,Z  3 {m}

    3.9624, -1.8288, 0,                 !- X,Y,Z  4 {m}

    3.9624, 0, 0,                       !- X,Y,Z  5 {m}

    0, 0, 0;                            !- X,Y,Z  6 {m}

 

BuildingSurface:Detailed,

    Floor2,                  !- Name

    Floor,                   !- Surface Type

    GrndUninsUnfinGFloor,    !- Construction Name

    Garage,                  !- Zone Name

    Ground,                  !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 6.4008, 0,                       !- X,Y,Z  1 {m}

    6.4008, 6.4008, 0,                  !- X,Y,Z  2 {m}

    6.4008, 0, 0,                       !- X,Y,Z  3 {m}

    0, 0, 0;                            !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Floor4,                  !- Name

    Floor,                   !- Surface Type

    FinUninsFinFloor,        !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    6,                       !- Number of Vertices

    0, 7.62, 2.7432,                    !- X,Y,Z  1 {m}

    10.668, 7.62, 2.7432,               !- X,Y,Z  2 {m}

    10.668, -1.8288, 2.7432,            !- X,Y,Z  3 {m}

    7.0104, -1.8288, 2.7432,            !- X,Y,Z  4 {m}

    7.0104, 0, 2.7432,                  !- X,Y,Z  5 {m}

    0, 0, 2.7432;                       !- X,Y,Z  6 {m}

 

BuildingSurface:Detailed,

    IntFloor4,               !- Name

    Ceiling,                 !- Surface Type

    RevFinUninsFinFloor,     !- Construction Name

    Living,                  !- Zone Name

    Adiabatic,               !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    6,                       !- Number of Vertices

    10.668, 7.62, 2.7432,               !- X,Y,Z  1 {m}

    0, 7.62, 2.7432,                    !- X,Y,Z  2 {m}

    0, 0, 2.7432,                       !- X,Y,Z  3 {m}

    7.0104, 0, 2.7432,                  !- X,Y,Z  4 {m}

    7.0104, -1.8288, 2.7432,            !- X,Y,Z  5 {m}

    10.668, -1.8288, 2.7432;            !- X,Y,Z  6 {m}

 

BuildingSurface:Detailed,

    Floor5,                  !- Name

    Floor,                   !- Surface Type

    UnfinInsFinFloor,        !- Construction Name

    Living,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    IntFloor5,               !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 11.2776, 2.7432,                 !- X,Y,Z  1 {m}

    6.4008, 11.2776, 2.7432,            !- X,Y,Z  2 {m}

    6.4008, 7.62, 2.7432,               !- X,Y,Z  3 {m}

    0, 7.62, 2.7432;                    !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    IntFloor5,               !- Name

    Ceiling,                 !- Surface Type

    RevUnfinInsFinFloor,     !- Construction Name

    Garage,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    Floor5,                  !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 3.6576, 2.7432,             !- X,Y,Z  1 {m}

    0, 3.6576, 2.7432,                  !- X,Y,Z  2 {m}

    0, 0, 2.7432,                       !- X,Y,Z  3 {m}

    6.4008, 0, 2.7432;                  !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Floor6,                  !- Name

    Floor,                   !- Surface Type

    FinInsUnfinUAFloor,      !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Surface,                 !- Outside Boundary Condition

    IntFloor6,               !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    8,                       !- Number of Vertices

    0, 11.2776, 0,                      !- X,Y,Z  1 {m}

    6.4008, 11.2776, 0,                 !- X,Y,Z  2 {m}

    6.4008, 7.62, 0,                    !- X,Y,Z  3 {m}

    10.668, 7.62, 0,                    !- X,Y,Z  4 {m}

    10.668, -1.8288, 0,                 !- X,Y,Z  5 {m}

    7.0104, -1.8288, 0,                 !- X,Y,Z  6 {m}

    7.0104, 0, 0,                       !- X,Y,Z  7 {m}

    0, 0, 0;                            !- X,Y,Z  8 {m}

 

BuildingSurface:Detailed,

    IntFloor6,               !- Name

    Ceiling,                 !- Surface Type

    RevFinInsUnfinUAFloor,   !- Construction Name

    Living,                  !- Zone Name

    Surface,                 !- Outside Boundary Condition

    Floor6,                  !- Outside Boundary Condition Object

    NoSun,                   !- Sun Exposure

    NoWind,                  !- Wind Exposure

    0,                       !- View Factor to Ground

    8,                       !- Number of Vertices

    6.4008, 11.2776, 5.4864,            !- X,Y,Z  1 {m}

    0, 11.2776, 5.4864,                 !- X,Y,Z  2 {m}

    0, 0, 5.4864,                       !- X,Y,Z  3 {m}

    7.0104, 0, 5.4864,                  !- X,Y,Z  4 {m}

    7.0104, -1.8288, 5.4864,            !- X,Y,Z  5 {m}

    10.668, -1.8288, 5.4864,            !- X,Y,Z  6 {m}

    10.668, 7.62, 5.4864,               !- X,Y,Z  7 {m}

    6.4008, 7.62, 5.4864;               !- X,Y,Z  8 {m}

 

BuildingSurface:Detailed,

    Roof2,                   !- Name

    Roof,                    !- Surface Type

    FinInsExtRoof,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    3.9624, -1.8288, 2.8703016,         !- X,Y,Z  1 {m}

    7.0104, -1.8288, 2.8703016,         !- X,Y,Z  2 {m}

    7.0104, -0.9144, 3.2513016,         !- X,Y,Z  3 {m}

    3.9624, -0.9144, 3.2513016;         !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof3,                   !- Name

    Roof,                    !- Surface Type

   UnfinUninsExtGrgRoof,    !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 3.6576, 2.8703016,          !- X,Y,Z  1 {m}

    6.4008, 6.4008, 2.8703016,          !- X,Y,Z  2 {m}

    3.2004, 6.4008, 4.2038016,          !- X,Y,Z  3 {m}

    3.2004, 3.6576, 4.2038016;          !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof4,                   !- Name

    Roof,                    !- Surface Type

    UnfinUninsExtGrgRoof,    !- Construction Name

    Garage,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    0, 6.4008, 2.8703016,               !- X,Y,Z  1 {m}

    0, 3.6576, 2.8703016,               !- X,Y,Z  2 {m}

    3.2004, 3.6576, 4.2038016,          !- X,Y,Z  3 {m}

    3.2004, 6.4008, 4.2038016;          !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof5,                   !- Name

    Roof,                    !- Surface Type

   UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    6,                       !- Number of Vertices

    0, 0, 0.127101600000001,            !- X,Y,Z  1 {m}

    7.0104, 0, 0.127101600000001,       !- X,Y,Z  2 {m}

    8.8392, 1.8288, 0.8891016,          !- X,Y,Z  3 {m}

    10.668, 0, 0.127101600000001,       !- X,Y,Z  4 {m}

    10.668, 3.81, 1.7145,               !- X,Y,Z  5 {m}

    0, 3.81, 1.7145;                    !- X,Y,Z  6 {m}

 

BuildingSurface:Detailed,

    Roof6,                   !- Name

    Roof,                    !- Surface Type

    UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    7.0104, 0, 0.127101600000001,       !- X,Y,Z  1 {m}

    7.0104, -1.8288, 0.127101600000001, !- X,Y,Z  2 {m}

    8.8392, -1.8288, 0.8891016,         !- X,Y,Z  3 {m}

    8.8392, 1.8288, 0.8891016;          !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof7,                   !- Name

    Roof,                    !- Surface Type

    UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    6,                       !- Number of Vertices

    10.668, 7.62, 0.127101600000001,    !- X,Y,Z  1 {m}

    6.4008, 7.62, 0.127101600000001,    !- X,Y,Z  2 {m}

    3.2004, 4.4196, 1.4606016,          !- X,Y,Z  3 {m}

    0, 7.62, 0.127101600000001,         !- X,Y,Z  4 {m}

    0, 3.81, 1.7145,                    !- X,Y,Z  5 {m}

    10.668, 3.81, 1.7145;               !- X,Y,Z  6 {m}

 

BuildingSurface:Detailed,

    Roof8,                   !- Name

    Roof,                    !- Surface Type

    UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    6.4008, 7.62, 0.127101600000001,    !- X,Y,Z  1 {m}

    6.4008, 11.2776, 0.127101600000001, !- X,Y,Z  2 {m}

    3.2004, 11.2776, 1.4606016,         !- X,Y,Z  3 {m}

    3.2004, 4.4196, 1.4606016;          !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof9,                   !- Name

    Roof,                    !- Surface Type

    UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    8.8392, 1.8288, 0.8891016,          !- X,Y,Z  1 {m}

    8.8392, -1.8288, 0.8891016,         !- X,Y,Z  2 {m}

    10.668, -1.8288, 0.127101600000001, !- X,Y,Z  3 {m}

    10.668, 0, 0.127101600000001;       !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof10,                  !- Name

    Roof,                    !- Surface Type

    UnfinInsExtRoof,         !- Construction Name

    UnfinishedAttic,         !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    3.2004, 4.4196, 1.4606016,          !- X,Y,Z  1 {m}

    3.2004, 11.2776, 1.4606016,         !- X,Y,Z  2 {m}

    0, 11.2776, 0.127101600000001,      !- X,Y,Z  3 {m}

    0, 7.62, 0.127101600000001;         !- X,Y,Z  4 {m}

 

BuildingSurface:Detailed,

    Roof12,                  !- Name

    Roof,                    !- Surface Type

    FinInsExtRoof,           !- Construction Name

    Living,                  !- Zone Name

    Outdoors,                !- Outside Boundary Condition

    ,                        !- Outside Boundary Condition Object

    SunExposed,              !- Sun Exposure

    WindExposed,             !- Wind Exposure

    autocalculate,           !- View Factor to Ground

    4,                       !- Number of Vertices

    7.0104, 0, 2.8703016,               !- X,Y,Z  1 {m}

    3.9624, 0, 2.8703016,               !- X,Y,Z  2 {m}

    3.9624, -0.9144, 3.2513016,         !- X,Y,Z  3 {m}

    7.0104, -0.9144, 3.2513016;         !- X,Y,Z  4 {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: WALL:ADIABATIC ===========

 

Wall:Adiabatic,

    RADuctWall,              !- Name

    AdiabaticConst,          !- Construction Name

    RA Duct Zone,            !- Zone Name

    0,                       !- Azimuth Angle {deg}

    90,                      !- Tilt Angle {deg}

    0,                       !- Starting X Coordinate {m}

    75,                      !- Starting Y Coordinate {m}

    0,                       !- Starting Z Coordinate {m}

    1,                       !- Length {m}

    1;                       !- Height {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: ROOF ===========

 

Roof,

    Horizontal,              !- Name

    AdiabaticConst,          !- Construction Name

    Dummy,                   !- Zone Name

    0,                       !- Azimuth Angle {deg}

    0,                       !- Tilt Angle {deg}

    0,                       !- Starting X Coordinate {m}

    30.48,                   !- Starting Y Coordinate {m}

    0,                       !- Starting Z Coordinate {m}

    0.1,                     !- Length {m}

    0.1;                     !- Width {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED ===========

 

FenestrationSurface:Detailed,

    Wall1-Window1,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall1,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 4.7204376, 0.9604248,            !- X,Y,Z  1 {m}

    0, 3.84048, 0.9604248,              !- X,Y,Z  2 {m}

    0, 3.84048, 2.1336,                 !- X,Y,Z  3 {m}

    0, 4.7204376, 2.1336;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall1-Window2,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall1,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 3.77952, 0.9604248,              !- X,Y,Z  1 {m}

    0, 2.8995624, 0.9604248,            !- X,Y,Z  2 {m}

    0, 2.8995624, 2.1336,               !- X,Y,Z  3 {m}

    0, 3.77952, 2.1336;                 !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall2-Window1,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall2,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0.5477256, 0, 1.1301984,            !- X,Y,Z  1 {m}

    1.3005816, 0, 1.1301984,            !- X,Y,Z  2 {m}

    1.3005816, 0, 2.1336,               !- X,Y,Z  3 {m}

    0.5477256, 0, 2.1336;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall2-Window2,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall2,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    1.3615416, 0, 1.1301984,            !- X,Y,Z  1 {m}

    2.1143976, 0, 1.1301984,            !- X,Y,Z  2 {m}

    2.1143976, 0, 2.1336,               !- X,Y,Z  3 {m}

    1.3615416, 0, 2.1336;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall2-Window3,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall2,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    2.6618184, 0, 1.1301984,            !- X,Y,Z  1 {m}

    3.4146744, 0, 1.1301984,            !- X,Y,Z  2 {m}

    3.4146744, 0, 2.1336,               !- X,Y,Z  3 {m}

    2.6618184, 0, 2.1336;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall4-Door1,             !- Name

    Door,                    !- Surface Type

    Doors,                   !- Construction Name

    Wall4,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    ,                        !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    4.2672, -1.8288, 0,                 !- X,Y,Z  1 {m}

    5.1816, -1.8288, 0,                 !- X,Y,Z  2 {m}

    5.1816, -1.8288, 2.033016,          !- X,Y,Z  3 {m}

    4.2672, -1.8288, 2.033016;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall4-Window1,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall4,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    6.3325248, -1.8288, 0.986028,       !- X,Y,Z  1 {m}

    7.19328, -1.8288, 0.986028,         !- X,Y,Z  2 {m}

    7.19328, -1.8288, 2.1336,           !- X,Y,Z  3 {m}

    6.3325248, -1.8288, 2.1336;         !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall4-Window2,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall4,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    7.25424, -1.8288, 0.986028,         !- X,Y,Z  1 {m}

    8.1149952, -1.8288, 0.986028,       !- X,Y,Z  2 {m}

    8.1149952, -1.8288, 2.1336,         !- X,Y,Z  3 {m}

    7.25424, -1.8288, 2.1336;           !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall4-Window3,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall4,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    8.96112, -1.8288, 0.986028,         !- X,Y,Z  1 {m}

    9.8218752, -1.8288, 0.986028,       !- X,Y,Z  2 {m}

    9.8218752, -1.8288, 2.1336,         !- X,Y,Z  3 {m}

    8.96112, -1.8288, 2.1336;           !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall5-Window1,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall5,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 1.3615416, 1.1289792,       !- X,Y,Z  1 {m}

    10.668, 2.115312, 1.1289792,        !- X,Y,Z  2 {m}

    10.668, 2.115312, 2.1336,           !- X,Y,Z  3 {m}

    10.668, 1.3615416, 2.1336;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall5-Window2,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall5,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 0.5468112, 1.1289792,       !- X,Y,Z  1 {m}

    10.668, 1.3005816, 1.1289792,       !- X,Y,Z  2 {m}

    10.668, 1.3005816, 2.1336,          !- X,Y,Z  3 {m}

    10.668, 0.5468112, 2.1336;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall5-Window3,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall5,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 4.4906184, 1.1289792,       !- X,Y,Z  1 {m}

    10.668, 5.2443888, 1.1289792,       !- X,Y,Z  2 {m}

    10.668, 5.2443888, 2.1336,          !- X,Y,Z  3 {m}

    10.668, 4.4906184, 2.1336;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall7-Window1,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall7,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    9.20496, 7.62, 0.9924288,           !- X,Y,Z  1 {m}

    8.3490816, 7.62, 0.9924288,         !- X,Y,Z  2 {m}

    8.3490816, 7.62, 2.1336,            !- X,Y,Z  3 {m}

    9.20496, 7.62, 2.1336;              !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall7-Window2,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall7,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.1217984, 7.62, 0.9924288,        !- X,Y,Z  1 {m}

    9.26592, 7.62, 0.9924288,           !- X,Y,Z  2 {m}

    9.26592, 7.62, 2.1336,              !- X,Y,Z  3 {m}

    10.1217984, 7.62, 2.1336;           !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall7-Window3,           !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall7,                   !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    7.80288, 7.62, 0.9924288,           !- X,Y,Z  1 {m}

    6.9470016, 7.62, 0.9924288,         !- X,Y,Z  2 {m}

    6.9470016, 7.62, 2.1336,            !- X,Y,Z  3 {m}

    7.80288, 7.62, 2.1336;              !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall10-Door1,            !- Name

    Door,                    !- Surface Type

    GarageDoor,              !- Construction Name

    Wall10,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    ,                        !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    5.7912, 6.4008, 0,                  !- X,Y,Z  1 {m}

    3.5052, 6.4008, 0,                  !- X,Y,Z  2 {m}

    3.5052, 6.4008, 2.1336,             !- X,Y,Z  3 {m}

    5.7912, 6.4008, 2.1336;             !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall10-Door2,            !- Name

    Door,                    !- Surface Type

    GarageDoor,              !- Construction Name

    Wall10,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    ,                        !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    2.8956, 6.4008, 0,                  !- X,Y,Z  1 {m}

    0.6096, 6.4008, 0,                  !- X,Y,Z  2 {m}

    0.6096, 6.4008, 2.1336,             !- X,Y,Z  3 {m}

    2.8956, 6.4008, 2.1336;             !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall13-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall13,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 8.621268, 3.8148768,             !- X,Y,Z  1 {m}

    0, 7.8248256, 3.8148768,            !- X,Y,Z  2 {m}

    0, 7.8248256, 4.8768,               !- X,Y,Z  3 {m}

    0, 8.621268, 4.8768;                !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall13-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall13,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 7.7635608, 3.8148768,            !- X,Y,Z  1 {m}

    0, 6.9671184, 3.8148768,            !- X,Y,Z  2 {m}

    0, 6.9671184, 4.8768,               !- X,Y,Z  3 {m}

    0, 7.7635608, 4.8768;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall13-Window3,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall13,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 4.3104816, 3.8148768,            !- X,Y,Z  1 {m}

    0, 3.5140392, 3.8148768,            !- X,Y,Z  2 {m}

    0, 3.5140392, 4.8768,               !- X,Y,Z  3 {m}

    0, 4.3104816, 4.8768;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall13-Window4,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall13,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    0, 3.4530792, 3.8148768,            !- X,Y,Z  1 {m}

    0, 2.6566368, 3.8148768,            !- X,Y,Z  2 {m}

    0, 2.6566368, 4.8768,               !- X,Y,Z  3 {m}

    0, 3.4530792, 4.8768;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall16-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall16,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    7.9229712, -1.8288, 3.6960048,      !- X,Y,Z  1 {m}

    8.80872, -1.8288, 3.6960048,        !- X,Y,Z  2 {m}

    8.80872, -1.8288, 4.8768,           !- X,Y,Z  3 {m}

    7.9229712, -1.8288, 4.8768;         !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall16-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall16,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    8.86968, -1.8288, 3.6960048,        !- X,Y,Z  1 {m}

    9.7554288, -1.8288, 3.6960048,      !- X,Y,Z  2 {m}

    9.7554288, -1.8288, 4.8768,         !- X,Y,Z  3 {m}

    8.86968, -1.8288, 4.8768;           !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall17-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall17,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 1.3615416, 3.8721792,       !- X,Y,Z  1 {m}

    10.668, 2.115312, 3.8721792,        !- X,Y,Z  2 {m}

    10.668, 2.115312, 4.8768,           !- X,Y,Z  3 {m}

    10.668, 1.3615416, 4.8768;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall17-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall17,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 0.5468112, 3.8721792,       !- X,Y,Z  1 {m}

    10.668, 1.3005816, 3.8721792,       !- X,Y,Z  2 {m}

    10.668, 1.3005816, 4.8768,          !- X,Y,Z  3 {m}

    10.668, 0.5468112, 4.8768;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall17-Window3,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall17,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.668, 4.4906184, 3.8721792,       !- X,Y,Z  1 {m}

    10.668, 5.2443888, 3.8721792,       !- X,Y,Z  2 {m}

    10.668, 5.2443888, 4.8768,          !- X,Y,Z  3 {m}

    10.668, 4.4906184, 4.8768;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall18-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall18,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    9.20496, 7.62, 3.7356288,           !- X,Y,Z  1 {m}

    8.3490816, 7.62, 3.7356288,         !- X,Y,Z  2 {m}

    8.3490816, 7.62, 4.8768,            !- X,Y,Z  3 {m}

    9.20496, 7.62, 4.8768;              !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall18-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall18,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    10.1217984, 7.62, 3.7356288,        !- X,Y,Z  1 {m}

    9.26592, 7.62, 3.7356288,           !- X,Y,Z  2 {m}

    9.26592, 7.62, 4.8768,              !- X,Y,Z  3 {m}

    10.1217984, 7.62, 4.8768;           !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall18-Window3,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall18,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    7.80288, 7.62, 3.7356288,           !- X,Y,Z  1 {m}

    6.9470016, 7.62, 3.7356288,         !- X,Y,Z  2 {m}

    6.9470016, 7.62, 4.8768,            !- X,Y,Z  3 {m}

    7.80288, 7.62, 4.8768;              !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall19-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall19,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    6.4008, 9.0428064, 3.7941504,       !- X,Y,Z  1 {m}

    6.4008, 9.8550984, 3.7941504,       !- X,Y,Z  2 {m}

    6.4008, 9.8550984, 4.8768,          !- X,Y,Z  3 {m}

    6.4008, 9.0428064, 4.8768;          !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall27-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall27,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    1.0503408, 0, 3.6764976,            !- X,Y,Z  1 {m}

    1.95072, 0, 3.6764976,              !- X,Y,Z  2 {m}

    1.95072, 0, 4.8768,                 !- X,Y,Z  3 {m}

    1.0503408, 0, 4.8768;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall27-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall27,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    2.01168, 0, 3.6764976,              !- X,Y,Z  1 {m}

    2.9120592, 0, 3.6764976,            !- X,Y,Z  2 {m}

    2.9120592, 0, 4.8768,               !- X,Y,Z  3 {m}

    2.01168, 0, 4.8768;                 !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall28-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall28,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    4.6661832, 0, 3.8240208,            !- X,Y,Z  1 {m}

    5.45592, 0, 3.8240208,              !- X,Y,Z  2 {m}

    5.45592, 0, 4.8768,                 !- X,Y,Z  3 {m}

    4.6661832, 0, 4.8768;               !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

   Wall28-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall28,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    5.51688, 0, 3.8240208,              !- X,Y,Z  1 {m}

    6.3066168, 0, 3.8240208,            !- X,Y,Z  2 {m}

    6.3066168, 0, 4.8768,               !- X,Y,Z  3 {m}

    5.51688, 0, 4.8768;                 !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall30-Window1,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall30,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    1.2192, 11.2776, 3.8075616,         !- X,Y,Z  1 {m}

    0.4169664, 11.2776, 3.8075616,      !- X,Y,Z  2 {m}

    0.4169664, 11.2776, 4.8768,         !- X,Y,Z  3 {m}

    1.2192, 11.2776, 4.8768;            !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

   Wall30-Window2,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall30,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    2.0823936, 11.2776, 3.8075616,      !- X,Y,Z  1 {m}

    1.28016, 11.2776, 3.8075616,        !- X,Y,Z  2 {m}

    1.28016, 11.2776, 4.8768,           !- X,Y,Z  3 {m}

    2.0823936, 11.2776, 4.8768;         !- X,Y,Z  4 {m}

 

FenestrationSurface:Detailed,

    Wall30-Window3,          !- Name

    Window,                  !- Surface Type

    Windows,                 !- Construction Name

    Wall30,                  !- Building Surface Name

    ,                        !- Outside Boundary Condition Object

    0.5,                     !- View Factor to Ground

    WindowShadingControl,    !- Shading Control Name

    ,                        !- Frame and Divider Name

    1.0,                     !- Multiplier

    4,                       !- Number of Vertices

    5.5827168, 11.2776, 3.8075616,      !- X,Y,Z  1 {m}

    4.7804832, 11.2776, 3.8075616,      !- X,Y,Z  2 {m}

    4.7804832, 11.2776, 4.8768,         !- X,Y,Z  3 {m}

    5.5827168, 11.2776, 4.8768;         !- X,Y,Z  4 {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: WINDOWPROPERTY:SHADINGCONTROL ===========

 

WindowProperty:ShadingControl,

    WindowShadingControl,    !- Name

    InteriorShade,           !- Shading Type

    ,                        !- Construction with Shading Name

    OnIfScheduleAllows,      !- Shading Control Type

    WindowShadingSchedule,   !- Schedule Name

    ,                        !- Setpoint {W/m2, W or deg C}

    Yes,                     !- Shading Control Is Scheduled

    No,                      !- Glare Control Is Active

    CoolingShade,            !- Shading Device Material Name

    ,                        !- Type of Slat Angle Control for Blinds

    ;                        !- Slat Angle Schedule Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: INTERNALMASS ===========

 

InternalMass,

    LivingPartition,         !- Name

    FinUninsFinWall,         !- Construction Name

    Living,                  !- Zone Name

    203.00763527424;         !- Surface Area {m2}

 

InternalMass,

    LivingSpaceFurniture,    !- Name

    LivingFurniture,         !- Construction Name

    Living,                  !- Zone Name

    81.977642496;            !- Surface Area {m2}

 

InternalMass,

    GarageSpaceFurniture,    !- Name

    GarageFurniture,         !- Construction Name

    Garage,                  !- Zone Name

    4.097024064;             !- Surface Area {m2}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SHADING:BUILDING:DETAILED ===========

 

Shading:Building:Detailed,

    Wall21,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -1.3716, -8.9916, 2.7432,           !- X,Y,Z  1 {m}

    -1.3716, -7.1628, 2.7432,           !- X,Y,Z  2 {m}

    -1.3716, -6.2484, 3.2513016,        !- X,Y,Z  3 {m}

    -1.3716, -7.0104, 3.5689032;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Wall32,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -5.334, 2.7432,             !- X,Y,Z  1 {m}

    -5.334, -8.9916, 2.7432,            !- X,Y,Z  2 {m}

    -5.334, -7.0104, 3.5689032,         !- X,Y,Z  3 {m}

    -5.334, -5.334, 2.8703016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Roof1,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -8.6868, 2.8703016,         !- X,Y,Z  1 {m}

    -1.3716, -8.6868, 2.8703016,        !- X,Y,Z  2 {m}

    -1.3716, -7.0104, 3.5689032,        !- X,Y,Z  3 {m}

    -5.334, -7.0104, 3.5689032;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Roof11,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -1.3716, -5.334, 2.8703016,         !- X,Y,Z  1 {m}

    -5.334, -5.334, 2.8703016,          !- X,Y,Z  2 {m}

    -5.334, -7.0104, 3.5689032,         !- X,Y,Z  3 {m}

    -1.3716, -7.0104, 3.5689032;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave1,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -8.9916, 2.7432,            !- X,Y,Z  1 {m}

    -1.3716, -8.9916, 2.7432,           !- X,Y,Z  2 {m}

    -1.3716, -8.6868, 2.8703016,        !- X,Y,Z  3 {m}

    -5.334, -8.6868, 2.8703016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave2,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -1.3716, -7.4676, 2.7432,           !- X,Y,Z  1 {m}

    1.6764, -7.4676, 2.7432,            !- X,Y,Z  2 {m}

    1.6764, -7.1628, 2.8703016,         !- X,Y,Z  3 {m}

    -1.3716, -7.1628, 2.8703016;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave3,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, 5.9436, 2.7432,             !- X,Y,Z  1 {m}

    1.3716, 8.6868, 2.7432,             !- X,Y,Z  2 {m}

    1.0668, 8.6868, 2.8703016,          !- X,Y,Z  3 {m}

    1.0668, 5.9436, 2.8703016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave4,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, 8.6868, 2.7432,            !- X,Y,Z  1 {m}

    -5.6388, 5.9436, 2.7432,            !- X,Y,Z  2 {m}

    -5.334, 5.9436, 2.8703016,          !- X,Y,Z  3 {m}

    -5.334, 8.6868, 2.8703016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave5,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

   -5.334, -5.6388, 5.4864,            !- X,Y,Z  1 {m}

    1.3716, -5.6388, 5.4864,            !- X,Y,Z  2 {m}

    1.6764, -5.334, 5.6135016,          !- X,Y,Z  3 {m}

    -5.334, -5.334, 5.6135016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave6,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, -5.6388, 5.4864,            !- X,Y,Z  1 {m}

    1.3716, -7.1628, 5.4864,            !- X,Y,Z  2 {m}

   1.6764, -7.1628, 5.6135016,         !- X,Y,Z  3 {m}

    1.6764, -5.334, 5.6135016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave7,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    5.334, 2.5908, 5.4864,              !- X,Y,Z  1 {m}

    1.3716, 2.5908, 5.4864,             !- X,Y,Z  2 {m}

    1.0668, 2.286, 5.6135016,           !- X,Y,Z  3 {m}

    5.334, 2.286, 5.6135016;            !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave8,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, 2.5908, 5.4864,             !- X,Y,Z  1 {m}

    1.3716, 5.9436, 5.4864,             !- X,Y,Z  2 {m}

    1.0668, 5.9436, 5.6135016,          !- X,Y,Z  3 {m}

    1.0668, 2.286, 5.6135016;           !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave9,                   !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    5.6388, -7.1628, 5.4864,            !- X,Y,Z  1 {m}

    5.6388, -5.6388, 5.4864,            !- X,Y,Z  2 {m}

    5.334, -5.334, 5.6135016,           !- X,Y,Z  3 {m}

    5.334, -7.1628, 5.6135016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave10,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, 5.9436, 5.4864,            !- X,Y,Z  1 {m}

    -5.6388, 2.5908, 5.4864,            !- X,Y,Z  2 {m}

    -5.334, 2.286, 5.6135016,           !- X,Y,Z  3 {m}

    -5.334, 5.9436, 5.6135016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave11,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -1.0668, -6.2484, 3.2513016,        !- X,Y,Z  1 {m}

    -1.3716, -6.2484, 3.2513016,        !- X,Y,Z  2 {m}

    -1.3716, -7.0104, 3.5689032,        !- X,Y,Z  3 {m}

    -1.0668, -7.0104, 3.5689032;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave12,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

   -1.3716, -8.9916, 2.7432,           !- X,Y,Z  1 {m}

    -1.0668, -8.9916, 2.7432,           !- X,Y,Z  2 {m}

    -1.0668, -7.0104, 3.5689032,        !- X,Y,Z  3 {m}

    -1.3716, -7.0104, 3.5689032;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave13,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, 8.9916, 2.7432,            !- X,Y,Z  1 {m}

    -5.6388, 8.6868, 2.7432,            !- X,Y,Z  2 {m}

   -2.1336, 8.6868, 4.2038016,         !- X,Y,Z  3 {m}

    -2.1336, 8.9916, 4.2038016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave14,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, 8.6868, 2.7432,             !- X,Y,Z  1 {m}

    1.3716, 8.9916, 2.7432,             !- X,Y,Z  2 {m}

    -2.1336, 8.9916, 4.2038016,         !- X,Y,Z  3 {m}

    -2.1336, 8.6868, 4.2038016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave15,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    5.6388, -7.4676, 5.4864,            !- X,Y,Z  1 {m}

    5.6388, -7.1628, 5.4864,            !- X,Y,Z  2 {m}

    3.5052, -7.1628, 6.3755016,         !- X,Y,Z  3 {m}

    3.5052, -7.4676, 6.3755016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave16,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, -7.1628, 5.4864,            !- X,Y,Z  1 {m}

    1.3716, -7.4676, 5.4864,            !- X,Y,Z  2 {m}

    3.5052, -7.4676, 6.3755016,         !- X,Y,Z  3 {m}

    3.5052, -7.1628, 6.3755016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave17,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, 6.2484, 5.4864,            !- X,Y,Z  1 {m}

    -5.6388, 5.9436, 5.4864,            !- X,Y,Z  2 {m}

    -2.1336, 5.9436, 6.9470016,         !- X,Y,Z  3 {m}

    -2.1336, 6.2484, 6.9470016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave18,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    1.3716, 5.9436, 5.4864,             !- X,Y,Z  1 {m}

    1.3716, 6.2484, 5.4864,             !- X,Y,Z  2 {m}

    -2.1336, 6.2484, 6.9470016,         !- X,Y,Z  3 {m}

    -2.1336, 5.9436, 6.9470016;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave19,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    5.6388, 2.5908, 5.4864,             !- X,Y,Z  1 {m}

    5.334, 2.5908, 5.4864,              !- X,Y,Z  2 {m}

    5.334, -1.524, 7.2009,              !- X,Y,Z  3 {m}

    5.6388, -1.524, 7.2009;             !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave20,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    5.334, -5.6388, 5.4864,             !- X,Y,Z  1 {m}

    5.6388, -5.6388, 5.4864,            !- X,Y,Z  2 {m}

    5.6388, -1.524, 7.2009,             !- X,Y,Z  3 {m}

    5.334, -1.524, 7.2009;              !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave21,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, -5.6388, 5.4864,           !- X,Y,Z  1 {m}

    -5.334, -5.6388, 5.4864,            !- X,Y,Z  2 {m}

    -5.334, -1.524, 7.2009,             !- X,Y,Z  3 {m}

    -5.6388, -1.524, 7.2009;            !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave22,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, 2.5908, 5.4864,             !- X,Y,Z  1 {m}

    -5.6388, 2.5908, 5.4864,            !- X,Y,Z  2 {m}

    -5.6388, -1.524, 7.2009,            !- X,Y,Z  3 {m}

    -5.334, -1.524, 7.2009;             !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave23,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -5.0292, 2.7432,            !- X,Y,Z  1 {m}

    -5.6388, -5.0292, 2.7432,           !- X,Y,Z  2 {m}

    -5.6388, -5.334, 2.8703016,         !- X,Y,Z  3 {m}

    -5.334, -5.334, 2.8703016;          !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave24,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.6388, -8.9916, 2.7432,           !- X,Y,Z  1 {m}

    -5.334, -8.9916, 2.7432,            !- X,Y,Z  2 {m}

    -5.334, -7.0104, 3.5689032,         !- X,Y,Z  3 {m}

    -5.6388, -7.0104, 3.5689032;        !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Eave25,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -5.334, 2.8703016,          !- X,Y,Z  1 {m}

    -5.6388, -5.334, 2.8703016,         !- X,Y,Z  2 {m}

    -5.6388, -7.0104, 3.5689032,        !- X,Y,Z  3 {m}

    -5.334, -7.0104, 3.5689032;         !- X,Y,Z  4 {m}

 

Shading:Building:Detailed,

    Shade1,                  !- Name

    ,                        !- Transmittance Schedule Name

    4,                       !- Number of Vertices

    -5.334, -8.6868, 2.7432,            !- X,Y,Z  1 {m}

    -1.3716, -8.6868, 2.7432,           !- X,Y,Z  2 {m}

    -1.3716, -5.334, 2.7432,            !- X,Y,Z  3 {m}

    -5.334, -5.334, 2.7432;             !- X,Y,Z  4 {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SURFACEPROPERTY:CONVECTIONCOEFFICIENTS ===========

 

SurfaceProperty:ConvectionCoefficients,

    RADuctWall,              !- Surface Name

    Inside,                  !- Convection Coefficient 1 Location

    Value,                   !- Convection Coefficient 1 Type

    5.5;                     !- Convection Coefficient 1 {W/m2-K}

 

 

!-   ===========  ALL OBJECTS IN CLASS: PEOPLE ===========

 

People,

    Living People,           !- Name

    Living,                  !- Zone or ZoneList Name

    Occupancy,               !- Number of People Schedule Name

    People,                  !- Number of People Calculation Method

    2.64,                    !- Number of People

    ,                        !- People per Zone Floor Area {person/m2}

    ,                        !- Zone Floor Area per Person {m2/person}

    0.32,                    !- Fraction Radiant

    0.573,                   !- Sensible Heat Fraction

    Occupant Activity,       !- Activity Level Schedule Name

    0,                       !- Carbon Dioxide Generation Rate {m3/s-W}

    Yes,                     !- Enable ASHRAE 55 Comfort Warnings

    ZoneAveraged,            !- Mean Radiant Temperature Calculation Type

    ,                        !- Surface Name/Angle Factor List Name

    Work Eff Sch,            !- Work Efficiency Schedule Name

    Clothing Sch,            !- Clothing Insulation Schedule Name

    Air Velo Sch,            !- Air Velocity Schedule Name

    Fanger,                  !- Thermal Comfort Model 1 Type

    Pierce,                  !- Thermal Comfort Model 2 Type

    KSU;                     !- Thermal Comfort Model 3 Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: LIGHTS ===========

 

Lights,

    Living HW & Plugin Lighting,  !- Name

    Living,                  !- Zone or ZoneList Name

    InteriorLightingProfile, !- Schedule Name

    LightingLevel,           !- Design Level Calculation Method

    484.3095,                !- Lighting Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Return Air Fraction

    0.6,                     !- Fraction Radiant

    0.2,                     !- Fraction Visible

    0;                       !- Fraction Replaceable

 

Lights,

    Garage Lighting,         !- Name

    Garage,                  !- Zone or ZoneList Name

    GarageLightingProfile,   !- Schedule Name

    LightingLevel,           !- Design Level Calculation Method

    11.28251,                !- Lighting Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Return Air Fraction

    0.6,                     !- Fraction Radiant

    0.2,                     !- Fraction Visible

    0;                       !- Fraction Replaceable

 

 

!-   ===========  ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========

 

ElectricEquipment,

    Refrigerator,            !- Name

    Living,                  !- Zone or ZoneList Name

    Refrigerator,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    65.3589041095888,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0,                       !- Fraction Lost

    Appl;                    !- End-Use Subcategory

 

ElectricEquipment,

    CeilingFans,             !- Name

    Living,                  !- Zone or ZoneList Name

    CeilingFansMaster,       !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    74,                      !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0.486,                   !- Fraction Radiant

    0,                       !- Fraction Lost

    Misc;                    !- End-Use Subcategory

 

ElectricEquipment,

    Misc Elec Load,          !- Name

    Living,                  !- Zone or ZoneList Name

    MiscPlugLoad,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    525.768769315068,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0.02,                    !- Fraction Latent

    0.486,                   !- Fraction Radiant

    0.17,                    !- Fraction Lost

    Misc;                    !- End-Use Subcategory

 

ElectricEquipment,

    Cooking Range,           !- Name

    Living,                  !- Zone or ZoneList Name

    CookingRange,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    205.541425061425,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0.3,                     !- Fraction Latent

    0.24,                    !- Fraction Radiant

    0.3,                     !- Fraction Lost

    Appl;                    !- End-Use Subcategory

 

ElectricEquipment,

    Clothes Washer,          !- Name

    Living,                  !- Zone or ZoneList Name

    ClothesWasher,           !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    11.3022119318203,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0.48,                    !- Fraction Radiant

    0.2,                     !- Fraction Lost

    Appl;                    !- End-Use Subcategory

 

ElectricEquipment,

    Clothes Dryer,           !- Name

    Living,                  !- Zone or ZoneList Name

    ClothesDryer,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    273.015494042797,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0.05,                    !- Fraction Latent

    0.09,                    !- Fraction Radiant

    0.8,                     !- Fraction Lost

    Appl;                    !- End-Use Subcategory

 

ElectricEquipment,

    Dishwasher,              !- Name

    Living,                  !- Zone or ZoneList Name

    Dishwasher,              !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    29.2227541703976,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0.15,                    !- Fraction Latent

    0.36,                    !- Fraction Radiant

    0.25,                    !- Fraction Lost

    Appl;                    !- End-Use Subcategory

 

ElectricEquipment,

    House Exhaust Fan Load,  !- Name

    Living,                  !- Zone or ZoneList Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0.5,                     !- Fraction Lost

    VentFans;                !- End-Use Subcategory

 

ElectricEquipment,

    Range Hood Fan Load,     !- Name

    Living,                  !- Zone or ZoneList Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    1,                       !- Fraction Lost

    VentFans;                !- End-Use Subcategory

 

ElectricEquipment,

    Bath Exhaust Fan Load,   !- Name

    Living,                  !- Zone or ZoneList Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    1,                       !- Fraction Lost

    VentFans;                !- End-Use Subcategory

 

 

!-   ===========  ALL OBJECTS IN CLASS: GASEQUIPMENT ===========

 

GasEquipment,

    Misc Gas Load,           !- Name

    Living,                  !- Zone or ZoneList Name

    MiscPlugLoad,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    38.1655462589731,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0.02,                    !- Fraction Latent

    0.486,                   !- Fraction Radiant

    0.17,                    !- Fraction Lost

    0,                       !- Carbon Dioxide Generation Rate {m3/s-W}

    Misc;                    !- End-Use Subcategory

 

GasEquipment,

    Cooking Range,           !- Name

    Living,                  !- Zone or ZoneList Name

    CookingRange,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0.2,                     !- Fraction Latent

    0.18,                    !- Fraction Radiant

    0.5,                     !- Fraction Lost

    0,                       !- Carbon Dioxide Generation Rate {m3/s-W}

    Appl;                    !- End-Use Subcategory

 

GasEquipment,

    Clothes Dryer,           !- Name

    Living,                  !- Zone or ZoneList Name

    ClothesDryer,            !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0.05,                    !- Fraction Latent

    0.06,                    !- Fraction Radiant

    0.85,                    !- Fraction Lost

    0,                       !- Carbon Dioxide Generation Rate {m3/s-W}

    Appl;                    !- End-Use Subcategory

 

 

!-   ===========  ALL OBJECTS IN CLASS: OTHEREQUIPMENT ===========

 

OtherEquipment,

    SinkHeatGain,            !- Name

    Living,                  !- Zone Name

    Sinks,                   !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    21.33587544192,          !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0.312222222222222,       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    ShowerHeatGain,          !- Name

    Living,                  !- Zone Name

    Showers,                 !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    108.76013936424,         !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0.48719723183391,        !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    BathHeatGain,            !- Name

    Living,                  !- Zone Name

    Baths,                   !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    14.3034500542752,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    DHWDistHeatGain,         !- Name

    Living,                  !- Zone Name

    DHWDist,                 !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    97.6505113265132,        !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplySensibleLeakageToLiving,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplyLatentLeakageToLiving,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    1,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplyDuctConductionToLiving,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplyDuctConductionToAHZone,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    ReturnDuctConductionToPlenum,  !- Name

    RA Duct Zone,            !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    ReturnDuctConductionToAHZone,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplySensibleLeakageToAHZone,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    SupplyLatentLeakageToAHZone,  !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    1,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    ReturnSensibleLeakageEquip,  !- Name

    RA Duct Zone,            !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    0,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

OtherEquipment,

    ReturnLatentLeakageEquip,!- Name

    RA Duct Zone,            !- Zone Name

    AlwaysOn,                !- Schedule Name

    EquipmentLevel,          !- Design Level Calculation Method

    0,                       !- Design Level {W}

    ,                        !- Watts per Zone Floor Area {W/m2}

    ,                        !- Watts per Person {W/Person}

    1,                       !- Fraction Latent

    0,                       !- Fraction Radiant

    0;                       !- Fraction Lost

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEINFILTRATION:EFFECTIVELEAKAGEAREA ===========

 

ZoneInfiltration:EffectiveLeakageArea,

    GarageInfiltration,      !- Name

    Garage,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    36.87201,                !- Effective Air Leakage Area {cm2}

    0.0002225123589806,      !- Stack Coefficient

    0.0001863672731397;      !- Wind Coefficient

 

ZoneInfiltration:EffectiveLeakageArea,

    UAtcInfiltration,        !- Name

    UnfinishedAttic,         !- Zone Name

    AlwaysOn,                !- Schedule Name

    556.9355,                !- Effective Air Leakage Area {cm2}

    0.0001191495264175,      !- Stack Coefficient

    0.000136071688527;       !- Wind Coefficient

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEINFILTRATION:FLOWCOEFFICIENT ===========

 

ZoneInfiltration:FlowCoefficient,

    Living Infiltration,     !- Name

    Living,                  !- Zone Name

    AlwaysOn,                !- Schedule Name

    1,                       !- Flow Coefficient

    1,                       !- Stack Coefficient

    1,                       !- Pressure Exponent

    1,                       !- Wind Coefficient

    1;                       !- Shelter Factor

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEVENTILATION:DESIGNFLOWRATE ===========

 

ZoneVentilation:DesignFlowRate,

    Natural Ventilation,     !- Name

    Living,                  !- Zone or ZoneList Name

    NatVentAvailability,     !- Schedule Name

    Flow/Zone,               !- Design Flow Rate Calculation Method

    0.001,                   !- Design Flow Rate {m3/s}

    ,                        !- Flow Rate per Zone Floor Area {m3/s-m2}

    ,                        !- Flow Rate per Person {m3/s-person}

    ,                        !- Air Changes per Hour

   Natural,                 !- Ventilation Type

    0,                       !- Fan Pressure Rise {Pa}

    1,                       !- Fan Total Efficiency

    1,                       !- Constant Term Coefficient

    0,                       !- Temperature Term Coefficient

    0,                       !- Velocity Term Coefficient

    0;                       !- Velocity Squared Term Coefficient

 

 

!-   ===========  ALL OBJECTS IN CLASS: EXTERIOR:LIGHTS ===========

 

Exterior:Lights,

    Exterior Lighting,       !- Name

    ExteriorLightingProfile, !- Schedule Name

    83.38577,                !- Design Level {W}

    ScheduleNameOnly;        !- Control Option

 

 

!-   ===========  ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========

 

Sizing:Parameters,

    1.1,                     !- Heating Sizing Factor

    1.1,                     !- Cooling Sizing Factor

    1;                       !- Timesteps in Averaging Window

 

 

!-   ===========  ALL OBJECTS IN CLASS: SIZING:ZONE ===========

 

Sizing:Zone,

    Living,                  !- Zone Name

    12.7777777777778,        !- Zone Cooling Design Supply Air Temperature {C}

    48.8888888888889,        !- Zone Heating Design Supply Air Temperature {C}

    0.008,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}

    0,                       !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}

    ,                        !- Outdoor Air Method

    ,                        !- Outdoor Air Flow per Person {m3/s}

    ,                        !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}

    ,                        !- Outdoor Air Flow per Zone {m3/s}

    ,                        !- Zone Heating Sizing Factor

    ,                        !- Zone Cooling Sizing Factor

    ,                        !- Cooling Design Air Flow Method

    ,                        !- Cooling Design Air Flow Rate {m3/s}

    ,                        !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}

    ,                        !- Cooling Minimum Air Flow {m3/s}

    ,                        !- Cooling Minimum Air Flow Fraction

    ,                        !- Heating Design Air Flow Method

    ,                        !- Heating Design Air Flow Rate {m3/s}

    ,                        !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}

    ;                        !- Heating Maximum Air Flow {m3/s}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SIZING:SYSTEM ===========

 

Sizing:System,

    Central Air System,      !- AirLoop Name

    Sensible,                !- Type of Load to Size On

    0,                       !- Design Outdoor Air Flow Rate {m3/s}

    0,                       !- Minimum System Air Flow Ratio

    48.8888888888889,        !- Preheat Design Temperature {C}

    0,                       !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}

    12.7777777777778,        !- Precool Design Temperature {C}

    0.008,                   !- Precool Design Humidity Ratio {kg-H2O/kg-Air}

    12.7777777777778,        !- Central Cooling Design Supply Air Temperature {C}

    48.8888888888889,        !- Central Heating Design Supply Air Temperature {C}

    Noncoincident,           !- Sizing Option

    No,                      !- 100% Outdoor Air in Cooling

    No,                      !- 100% Outdoor Air in Heating

    0.008,                   !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}

    0,                       !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}

    DesignDay,               !- Cooling Design Air Flow Method

    0,                       !- Cooling Design Air Flow Rate {m3/s}

    DesignDay,               !- Heating Design Air Flow Method

    0;                       !- Heating Design Air Flow Rate {m3/s}

 

 

!-   ===========  ALL OBJECTS IN CLASS: SIZING:PLANT ===========

 

Sizing:Plant,

    DHW Loop,                !- Plant or Condenser Loop Name

    Heating,                 !- Loop Type

    54.4444444444445,        !- Design Loop Exit Temperature {C}

    5.55555555555556;        !- Loop Design Temperature Difference {deltaC}

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:HUMIDISTAT ===========

 

ZoneControl:Humidistat,

    Living Zone Humidistat,  !- Name

    Living,                  !- Zone Name

    RelativeHumiditySetpoint,!- Humidifying Relative Humidity Setpoint Schedule Name

    RelativeHumiditySetpoint;!- Dehumidifying Relative Humidity Setpoint Schedule Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========

 

ZoneControl:Thermostat,

    Living Zone Thermostat,  !- Name

    Living,                  !- Zone or ZoneList Name

    LivingZoneControl,       !- Control Type Schedule Name

    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type

    Living Zone Temperature SP;  !- Control 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:DUALSETPOINT ===========

 

ThermostatSetpoint:DualSetpoint,

    Living Zone Temperature SP,  !- Name

    HeatingSetPoint,         !- Heating Setpoint Temperature Schedule Name

    CoolingSetPoint;         !- Cooling Setpoint Temperature Schedule Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:DEHUMIDIFIER:DX ===========

 

ZoneHVAC:Dehumidifier:DX,

    Zone DX Dehumidifier,    !- Name

    AlwaysOn,                !- Availability Schedule Name

    DXDehumidifier Inlet Node,  !- Air Inlet Node Name

    DXDehumidifier Outlet Node,  !- Air Outlet Node Name

    52.04941203,             !- Rated Water Removal {L/day}

    1.10,                    !- Rated Energy Factor {L/kWh}

    0.113256,                !- Rated Air Flow Rate {m3/s}

    DXDH-WaterRemove-Cap-fT, !- Water Removal Curve Name

    DXDH-EnergyFactor-fT,    !- Energy Factor Curve Name

    DXDH-PLF-fPLR,           !- Part Load Fraction Correlation Curve Name

    10,                      !- Minimum Dry-Bulb Temperature for Dehumidifier Operation {C}

    40,                      !- Maximum Dry-Bulb Temperature for Dehumidifier Operation {C}

    ;                        !- Off-Cycle Parasitic Electric Load {W}

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:ENERGYRECOVERYVENTILATOR ===========

 

ZoneHVAC:EnergyRecoveryVentilator,

    ERV,                     !- Name

    AlwaysOn,                !- Availability Schedule Name

    ERV Heat Exchanger,      !- Heat Exchanger Name

    0.024567114,             !- Supply Air Flow Rate {m3/s}

    0.024567114,             !- Exhaust Air Flow Rate {m3/s}

    ERV Supply Fan,          !- Supply Air Fan Name

    ERV Exhaust Fan,         !- Exhaust Air Fan Name

    ERV Controller;          !- Controller Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:ENERGYRECOVERYVENTILATOR:CONTROLLER ===========

 

ZoneHVAC:EnergyRecoveryVentilator:Controller,

    ERV Controller,          !- Name

    ,                        !- Temperature High Limit {C}

    ,                        !- Temperature Low Limit {C}

    ,                        !- Enthalpy High Limit {J/kg}

    ,                        !- Dewpoint Temperature Limit {C}

    ,                        !- Electronic Enthalpy Limit Curve Name

    NoExhaustAirTemperatureLimit,  !- Exhaust Air Temperature Limit

    NoExhaustAirEnthalpyLimit,  !- Exhaust Air Enthalpy Limit

    AlwaysOff,               !- Time of Day Economizer Flow Control Schedule Name

    No;                      !- High Humidity Control Flag

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:UNCONTROLLED ===========

 

AirTerminal:SingleDuct:Uncontrolled,

    Living Zone Direct Air,  !- Name

    AlwaysOn,                !- Availability Schedule Name

    Living Supply Node,      !- Zone Supply Air Node Name

    autosize;                !- Maximum Air Flow Rate {m3/s}

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========

 

ZoneHVAC:EquipmentList,

    Living Zone Equipment,   !- Name

    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type

    ERV,                     !- Zone Equipment 1 Name

    1,                       !- Zone Equipment 1 Cooling Sequence

    1,                       !- Zone Equipment 1 Heating or No-Load Sequence

    ZoneHVAC:Dehumidifier:DX,!- Zone Equipment 2 Object Type

    Zone DX Dehumidifier,    !- Zone Equipment 2 Name

    2,                       !- Zone Equipment 2 Cooling Sequence

    2,                       !- Zone Equipment 2 Heating or No-Load Sequence

    AirTerminal:SingleDuct:Uncontrolled,  !- Zone Equipment 3 Object Type

    Living Zone Direct Air,  !- Zone Equipment 3 Name

    3,                       !- Zone Equipment 3 Cooling Sequence

    3;                       !- Zone Equipment 3 Heating or No-Load Sequence

 

 

!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========

 

ZoneHVAC:EquipmentConnections,

    Living,                  !- Zone Name

    Living Zone Equipment,   !- Zone Conditioning Equipment List Name

    Living Supply Nodes,     !- Zone Air Inlet Node or NodeList Name

    Living Exhaust Nodes,    !- Zone Air Exhaust Node or NodeList Name

    Living Zone Air Node,    !- Zone Air Node Name

    Living Return Node;      !- Zone Return Air Node Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: FAN:_ONOFF_ ===========

 

Fan:OnOff,

    ERV Supply Fan,          !- Name

    AlwaysOn,                !- Availability Schedule Name

    0.28314,                 !- Fan Efficiency

    300,                     !- Pressure Rise {Pa}

    0.024567114,             !- Maximum Flow Rate {m3/s}

    1,                       !- Motor Efficiency

    1,                       !- Motor In Airstream Fraction

    ERV Supply Fan Inlet Node,  !- Air Inlet Node Name

    ERV Supply Fan Outlet Node,  !- Air Outlet Node Name

   Fan-EIR-fPLR,            !- Fan Power Ratio Function of Speed Ratio Curve Name

    ,                        !- Fan Efficiency Ratio Function of Speed Ratio Curve Name

    VentFans;                !- End-Use Subcategory

 

Fan:OnOff,

    ERV Exhaust Fan,         !- Name

    AlwaysOn,                !- Availability Schedule Name

    0.28314,                 !- Fan Efficiency

    300,                     !- Pressure Rise {Pa}

    0.024567114,             !- Maximum Flow Rate {m3/s}

    1,                       !- Motor Efficiency

    0,                       !- Motor In Airstream Fraction

    ERV Exhaust Fan Inlet Node,  !- Air Inlet Node Name

    ERV Exhaust Fan Outlet Node,  !- Air Outlet Node Name

    Fan-EIR-fPLR,            !- Fan Power Ratio Function of Speed Ratio Curve Name

    ,                        !- Fan Efficiency Ratio Function of Speed Ratio Curve Name

    VentFans;                !- End-Use Subcategory

 

Fan:OnOff,

    Supply Fan,              !- Name

    AlwaysOff,               !- Availability Schedule Name

    0.38786301369863,        !- Fan Efficiency

    300,                     !- Pressure Rise {Pa}

    autosize,                !- Maximum Flow Rate {m3/s}

    1,                       !- Motor Efficiency

    1,                       !- Motor In Airstream Fraction

    Air Supply Inlet Node,   !- Air Inlet Node Name

    Heating Coil Inlet Node, !- Air Outlet Node Name

    ,                        !- Fan Power Ratio Function of Speed Ratio Curve Name

    ,                        !- Fan Efficiency Ratio Function of Speed Ratio Curve Name

    HVACFan;                 !- End-Use Subcategory

 

 

!-   ===========  ALL OBJECTS IN CLASS: COIL:COOLING:DX:SINGLESPEED ===========

 

Coil:Cooling:DX:SingleSpeed,

    DX Cooling Coil,         !- Name

    CoolingSeasonSchedule,   !- Availability Schedule Name

    autosize,                !- Rated Total Cooling Capacity {W}

    autosize,                !- Rated Sensible Heat Ratio

    3.22279677526955,        !- Rated COP

    autosize,                !- Rated Air Flow Rate {m3/s}

    773.468955287137,        !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)}

    Cooling Coil Inlet Node, !- Air Inlet Node Name

    Air Supply Outlet Node,  !- Air Outlet Node Name

    Cool-Cap-fT,             !- Total Cooling Capacity Function of Temperature Curve Name

    ConstantCubic,           !- Total Cooling Capacity Function of Flow Fraction Curve Name

    Cool-EIR-fT,             !- Energy Input Ratio Function of Temperature Curve Name

    ConstantCubic,           !- Energy Input Ratio Function of Flow Fraction Curve Name

    Cool-PLF-fPLR,           !- Part Load Fraction Correlation Curve Name

    1000,                    !- Nominal Time for Condensate Removal to Begin {s}

    1.5,                     !- Ratio of Initial Moisture Evaporation Rate and Steady State Latent Capacity {dimensionless}

    3,                       !- Maximum Cycling Rate {cycles/hr}

    45,                      !- Latent Capacity Time Constant {s}

    ,                        !- Condenser Air Inlet Node Name

    AirCooled,               !- Condenser Type

    ,                        !- Evaporative Condenser Effectiveness {dimensionless}

    ,                        !- Evaporative Condenser Air Flow Rate {m3/s}

    ,                        !- Evaporative Condenser Pump Rated Power Consumption {W}

    0,                       !- Crankcase Heater Capacity {W}

    12.7777777777778,        !- Maximum Outdoor Dry-Bulb Temperature for Crankcase Heater Operation {C}

    ,                        !- Supply Water Storage Tank Name

    Condensate Tank 1;       !- Condensate Collection Water Storage Tank Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: COIL:HEATING:GAS ===========

 

Coil:Heating:Gas,

    Furnace Heating Coil,    !- Name

    HeatingSeasonSchedule,   !- Availability Schedule Name

    0.930045000000002,       !- Gas Burner Efficiency

    autosize,                !- Nominal Capacity {W}

    Heating Coil Inlet Node, !- Air Inlet Node Name

    Cooling Coil Inlet Node, !- Air Outlet Node Name

    ,                        !- Temperature Setpoint Node Name

    ,                        !- Parasitic Electric Load {W}

    Furnace-PLF-fPLR;        !- Part Load Fraction Correlation Curve Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: HEATEXCHANGER:AIRTOAIR:SENSIBLEANDLATENT ===========

 

HeatExchanger:AirToAir:SensibleAndLatent,

    ERV Heat Exchanger,      !- Name

    AlwaysOn,                !- Availability Schedule Name

    0.024567114,             !- Nominal Supply Air Flow Rate {m3/s}

    0.72,                    !- Sensible Effectiveness at 100% Heating Air Flow {dimensionless}

    0.72,                    !- Latent Effectiveness at 100% Heating Air Flow {dimensionless}

    0.72,                    !- Sensible Effectiveness at 75% Heating Air Flow {dimensionless}

    0.72,                    !- Latent Effectiveness at 75% Heating Air Flow {dimensionless}

    0.72,                    !- Sensible Effectiveness at 100% Cooling Air Flow {dimensionless}

    0.72,                    !- Latent Effectiveness at 100% Cooling Air Flow {dimensionless}

    0.72,                    !- Sensible Effectiveness at 75% Cooling Air Flow {dimensionless}

    0.72,                    !- Latent Effectiveness at 75% Cooling Air Flow {dimensionless}

    ERV Outside Air Inlet Node,  !- Supply Air Inlet Node Name

    ERV Supply Fan Inlet Node,  !- Supply Air Outlet Node Name

    Living Exhaust Node,     !- Exhaust Air Inlet Node Name

    ERV Exhaust Fan Inlet Node,  !- Exhaust Air Outlet Node Name

    ,                        !- Nominal Electric Power {W}

    ,                        !- Supply Air Outlet Temperature Control

    ,                        !- Heat Exchanger Type

    ;                        !- Frost Control Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:UNITARYHEATCOOL ===========

 

AirLoopHVAC:UnitaryHeatCool,

    Forced Air System,       !- Name

    AlwaysOn,                !- Availability Schedule Name

    Air Supply Inlet Node,   !- Unitary System Air Inlet Node Name

    Air Supply Outlet Node,  !- Unitary System Air Outlet Node Name

    SupplyFanOperation,      !- Supply Air Fan Operating Mode Schedule Name

    48.8888888888889,        !- Maximum Supply Air Temperature {C}

    autosize,                !- Supply Air Flow Rate During Cooling Operation {m3/s}

    autosize,                !- Supply Air Flow Rate During Heating Operation {m3/s}

    0,                       !- Supply Air Flow Rate When No Cooling or Heating is Needed {m3/s}

    Living,                  !- Controlling Zone or Thermostat Location

    Fan:OnOff,               !- Supply Fan Object Type

    Supply Fan,              !- Supply Fan Name

    BlowThrough,             !- Fan Placement

    Coil:Heating:Gas,        !- Heating Coil Object Type

    Furnace Heating Coil,    !- Heating Coil Name

    Coil:Cooling:DX:SingleSpeed,  !- Cooling Coil Object Type

    DX Cooling Coil,         !- Cooling Coil Name

    None;                    !- Dehumidification Control Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC ===========

 

AirLoopHVAC,

    Central Air System,      !- Name

    ,                        !- Controller List Name

    ,                        !- Availability Manager List Name

    autosize,                !- Design Supply Air Flow Rate {m3/s}

    Air Supply Branches,     !- Branch List Name

    ,                        !- Connector List Name

    Air Supply Inlet Node,   !- Supply Side Inlet Node Name

    Air Demand Outlet Node,  !- Demand Side Outlet Node Name

    Air Demand Inlet Node,   !- Demand Side Inlet Node Names

    Air Supply Outlet Node;  !- Supply Side Outlet Node Names

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:ZONESPLITTER ===========

 

AirLoopHVAC:ZoneSplitter,

    Zone Splitter,           !- Name

    Air Demand Inlet Node,   !- Inlet Node Name

    Living Supply Node;      !- Outlet 1 Node Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:SUPPLYPATH ===========

 

AirLoopHVAC:SupplyPath,

    Supply Air Path,         !- Name

    Air Demand Inlet Node,   !- Supply Air Path Inlet Node Name

    AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type

    Zone Splitter;           !- Component 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:RETURNPLENUM ===========

 

AirLoopHVAC:ReturnPlenum,

    Return Plenum,           !- Name

    RA Duct Zone,            !- Zone Name

    RA Plenum Air Node,      !- Zone Node Name

    Air Demand Outlet Node,  !- Outlet Node Name

    Living Return Node;      !- Inlet 1 Node Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:RETURNPATH ===========

 

AirLoopHVAC:ReturnPath,

    Return Air Path,         !- Name

    Air Demand Outlet Node,  !- Return Air Path Outlet Node Name

    AirLoopHVAC:ReturnPlenum,!- Component 1 Object Type

    Return Plenum;           !- Component 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========

 

Branch,

    Supply Air Branch,       !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    AirLoopHVAC:UnitaryHeatCool,  !- Component 1 Object Type

    Forced Air System,       !- Component 1 Name

    Air Supply Inlet Node,   !- Component 1 Inlet Node Name

    Air Supply Outlet Node,  !- Component 1 Outlet Node Name

    Active;                  !- Component 1 Branch Control Type

 

Branch,

    Mains Inlet Branch,      !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    Pump:VariableSpeed,      !- Component 1 Object Type

    Mains Pressure,          !- Component 1 Name

    Mains Inlet Node,        !- Component 1 Inlet Node Name

    Mains Pressure Outlet Node,  !- Component 1 Outlet Node Name

    Active;                  !- Component 1 Branch Control Type

 

Branch,

    Water Heater Branch,     !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    WaterHeater:Mixed,       !- Component 1 Object Type

    Water Heater,            !- Component 1 Name

    Water Heater Use Inlet Node,  !- Component 1 Inlet Node Name

    Water Heater Use Outlet Node,  !- Component 1 Outlet Node Name

    Passive;                 !- Component 1 Branch Control Type

 

Branch,

    DHW Supply Outlet Branch,!- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    Pipe:Adiabatic,          !- Component 1 Object Type

    DHW Supply Outlet Pipe,  !- Component 1 Name

    DHW Supply Outlet Pipe Inlet Node,  !- Component 1 Inlet Node Name

    DHW Supply Outlet Node,  !- Component 1 Outlet Node Name

    Passive;                 !- Component 1 Branch Control Type

 

Branch,

    DHW Demand Inlet Branch, !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    Pipe:Adiabatic,          !- Component 1 Object Type

    DHW Demand Inlet Pipe,   !- Component 1 Name

    DHW Demand Inlet Node,   !- Component 1 Inlet Node Name

    DHW Demand Inlet Pipe Outlet Node,  !- Component 1 Outlet Node Name

    Passive;                 !- Component 1 Branch Control Type

 

Branch,

    Water Demand Branch,     !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    WaterUse:Connections,    !- Component 1 Object Type

    Domestic Hot Water,      !- Component 1 Name

    Water Demand Inlet Node, !- Component 1 Inlet Node Name

    Water Demand Outlet Node,!- Component 1 Outlet Node Name

    Active;                  !- Component 1 Branch Control Type

 

Branch,

    Mains Makeup Branch,     !- Name

    autosize,                !- Maximum Flow Rate {m3/s}

    ,                        !- Pressure Drop Curve Name

    Pipe:Adiabatic,          !- Component 1 Object Type

    Mains Makeup Pipe,       !- Component 1 Name

    Mains Makeup Pipe Inlet Node,  !- Component 1 Inlet Node Name

    Mains Makeup Node,       !- Component 1 Outlet Node Name

    Passive;                 !- Component 1 Branch Control Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: BRANCHLIST ===========

 

BranchList,

    Air Supply Branches,     !- Name

    Supply Air Branch;       !- Branch 1 Name

 

BranchList,

    DHW Supply Branches,     !- Name

    Mains Inlet Branch,      !- Branch 1 Name

    Water Heater Branch,     !- Branch 2 Name

    DHW Supply Outlet Branch;!- Branch 3 Name

 

BranchList,

    DHW Demand Branches,     !- Name

    DHW Demand Inlet Branch, !- Branch 1 Name

    Water Demand Branch,     !- Branch 2 Name

    Mains Makeup Branch;     !- Branch 3 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========

 

Connector:Splitter,

    DHW Supply Splitter,     !- Name

    Mains Inlet Branch,      !- Inlet Branch Name

    Water Heater Branch;     !- Outlet Branch 1 Name

 

Connector:Splitter,

    DHW Demand Splitter,     !- Name

    DHW Demand Inlet Branch, !- Inlet Branch Name

    Water Demand Branch;     !- Outlet Branch 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========

 

Connector:Mixer,

    DHW Supply Mixer,        !- Name

    DHW Supply Outlet Branch,!- Outlet Branch Name

    Water Heater Branch;     !- Inlet Branch 1 Name

 

Connector:Mixer,

    DHW Demand Mixer,        !- Name

    Mains Makeup Branch,     !- Outlet Branch Name

    Water Demand Branch;     !- Inlet Branch 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: CONNECTORLIST ===========

 

ConnectorList,

    DHW Supply Connectors,   !- Name

    Connector:Splitter,      !- Connector 1 Object Type

    DHW Supply Splitter,     !- Connector 1 Name

    Connector:Mixer,         !- Connector 2 Object Type

    DHW Supply Mixer;        !- Connector 2 Name

 

ConnectorList,

    DHW Demand Connectors,   !- Name

    Connector:Splitter,      !- Connector 1 Object Type

    DHW Demand Splitter,     !- Connector 1 Name

    Connector:Mixer,         !- Connector 2 Object Type

    DHW Demand Mixer;        !- Connector 2 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: NODELIST ===========

 

NodeList,

    Living Supply Nodes,     !- Name

    Living Supply Node,      !- Node 1 Name

    DXDehumidifier Outlet Node,  !- Node 2 Name

    ERV Supply Fan Outlet Node;  !- Node 3 Name

 

NodeList,

    Living Exhaust Nodes,    !- Name

    DXDehumidifier Inlet Node,  !- Node 1 Name

    ERV Exhaust Fan Inlet Node,  !- Node 2 Name

    Living Exhaust Node;     !- Node 3 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========

 

OutdoorAir:Node,

    ERV Outside Air Inlet Node,  !- Name

    2.7432;                  !- Height Above Ground {m}

 

 

!-   ===========  ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========

 

Pipe:Adiabatic,

    DHW Supply Outlet Pipe,  !- Name

    DHW Supply Outlet Pipe Inlet Node,  !- Inlet Node Name

    DHW Supply Outlet Node;  !- Outlet Node Name

 

Pipe:Adiabatic,

    DHW Demand Inlet Pipe,   !- Name

    DHW Demand Inlet Node,   !- Inlet Node Name

    DHW Demand Inlet Pipe Outlet Node;  !- Outlet Node Name

 

Pipe:Adiabatic,

    Mains Makeup Pipe,       !- Name

    Mains Makeup Pipe Inlet Node,  !- Inlet Node Name

    Mains Makeup Node;       !- Outlet Node Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========

 

Pump:VariableSpeed,

    Mains Pressure,          !- Name

    Mains Inlet Node,        !- Inlet Node Name

    Mains Pressure Outlet Node,  !- Outlet Node Name

    0.01,                    !- Rated Flow Rate {m3/s}

    1,                       !- Rated Pump Head {Pa}

    0,                       !- Rated Power Consumption {W}

    1,                       !- Motor Efficiency

    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream

    0,                       !- Coefficient 1 of the Part Load Performance Curve

    1,                       !- Coefficient 2 of the Part Load Performance Curve

    0,                       !- Coefficient 3 of the Part Load Performance Curve

    0,                       !- Coefficient 4 of the Part Load Performance Curve

    0,                       !- Minimum Flow Rate {m3/s}

    Intermittent;            !- Pump Control Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: WATERHEATER:MIXED ===========

 

WaterHeater:Mixed,

    Water Heater,            !- Name

    0.1514,                  !- Tank Volume {m3}

    WaterHeaterSP1Schedule,  !- Setpoint Temperature Schedule Name

    2,                       !- Deadband Temperature Difference {deltaC}

    99,                      !- Maximum Temperature Limit {C}

    Modulate,                !- Heater Control Type

    10015.227,               !- Heater Maximum Capacity {W}

    0,                       !- Heater Minimum Capacity {W}

    0,                       !- Heater Ignition Minimum Flow Rate {m3/s}

    0,                       !- Heater Ignition Delay {s}

    NaturalGas,              !- Heater Fuel Type

    0.8,                     !- Heater Thermal Efficiency

    ,                        !- Part Load Factor Curve Name

    ,                        !- Off Cycle Parasitic Fuel Consumption Rate {W}

    ,                        !- Off Cycle Parasitic Fuel Type

    ,                        !- Off Cycle Parasitic Heat Fraction to Tank

    ,                        !- On Cycle Parasitic Fuel Consumption Rate {W}

    ,                        !- On Cycle Parasitic Fuel Type

    ,                        !- On Cycle Parasitic Heat Fraction to Tank

    Zone,                    !- Ambient Temperature Indicator

    ,                        !- Ambient Temperature Schedule Name

    Garage,                  !- Ambient Temperature Zone Name

    ,                        !- Ambient Temperature Outdoor Air Node Name

    2.80603828610423,        !- Off Cycle Loss Coefficient to Ambient Temperature {W/K}

    1,                       !- Off Cycle Loss Fraction to Zone

    2.80603828610423,        !- On Cycle Loss Coefficient to Ambient Temperature {W/K}

    1,                       !- On Cycle Loss Fraction to Zone

    ,                        !- Peak Use Flow Rate {m3/s}

    ,                        !- Use Flow Rate Fraction Schedule Name

    ,                        !- Cold Water Supply Temperature Schedule Name

    Water Heater Use Inlet Node,  !- Use Side Inlet Node Name

    Water Heater Use Outlet Node,  !- Use Side Outlet Node Name

    1.0,                     !- Use Side Effectiveness

    ,                        !- Source Side Inlet Node Name

    ,                        !- Source Side Outlet Node Name

    1,                       !- Source Side Effectiveness

    autosize,                !- Use Side Design Flow Rate {m3/s}

    ,                        !- Source Side Design Flow Rate {m3/s}

    1.5;                     !- Indirect Water Heating Recovery Time {hr}

 

 

!-   ===========  ALL OBJECTS IN CLASS: PLANTLOOP ===========

 

PlantLoop,

    DHW Loop,                !- Name

    Water,                   !- Fluid Type

    DHW Loop Operation,      !- Plant Equipment Operation Scheme Name

    DHW Supply Outlet Node,  !- Loop Temperature Setpoint Node Name

    100,                     !- Maximum Loop Temperature {C}

    0,                       !- Minimum Loop Temperature {C}

    0.01,                    !- Maximum Loop Flow Rate {m3/s}

    0,                       !- Minimum Loop Flow Rate {m3/s}

    autocalculate,           !- Plant Loop Volume {m3}

    Mains Inlet Node,        !- Plant Side Inlet Node Name

    DHW Supply Outlet Node,  !- Plant Side Outlet Node Name

    DHW Supply Branches,     !- Plant Side Branch List Name

    DHW Supply Connectors,   !- Plant Side Connector List Name

    DHW Demand Inlet Node,   !- Demand Side Inlet Node Name

    Mains Makeup Node,       !- Demand Side Outlet Node Name

    DHW Demand Branches,     !- Demand Side Branch List Name

    DHW Demand Connectors,   !- Demand Side Connector List Name

    Optimal;                 !- Load Distribution Scheme

 

 

!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========

 

PlantEquipmentList,

    DHW Plant Equipment,     !- Name

    WaterHeater:Mixed,       !- Equipment 1 Object Type

    Water Heater;            !- Equipment 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:HEATINGLOAD ===========

 

PlantEquipmentOperation:HeatingLoad,

    DHW Control Scheme,      !- Name

    0.0,                     !- Load Range 1 Lower Limit {W}

    1000000000000000,        !- Load Range 1 Upper Limit {W}

    DHW Plant Equipment;     !- Range 1 Equipment List Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES ===========

 

PlantEquipmentOperationSchemes,

    DHW Loop Operation,      !- Name

    PlantEquipmentOperation:HeatingLoad,  !- Control Scheme 1 Object Type

    DHW Control Scheme,      !- Control Scheme 1 Name

    AlwaysOn;                !- Control Scheme 1 Schedule Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:SENSOR ===========

 

EnergyManagementSystem:Sensor,

    Sensor_HeatingSeasonSchedule,  !- Name

    HeatingSeasonSchedule,   !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Sensor_CoolingSeasonSchedule,  !- Name

    CoolingSeasonSchedule,   !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    SensibleLoadPredicted,   !- Name

    Living,                  !- Output:Variable or Output:Meter Index Key Name

    Zone/Sys Sensible Load Predicted;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    CeilingFansSetup_sch,    !- Name

    CeilingFansSetup,        !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Tout,                    !- Name

    Living,                  !- Output:Variable or Output:Meter Index Key Name

    Zone Outdoor Dry Bulb;   !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Hout,                    !- Name

    ,                        !- Output:Variable or Output:Meter Index Key Name

    Outdoor Enthalpy;        !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Pbar,                    !- Name

    ,                        !- Output:Variable or Output:Meter Index Key Name

    Outdoor Barometric Pressure;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Tin,                     !- Name

    Living,                  !- Output:Variable or Output:Meter Index Key Name

    Zone Mean Air Temperature;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Win,                     !- Name

    Living,                  !- Output:Variable or Output:Meter Index Key Name

    Zone Mean Air Humidity Ratio;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Wout,                    !- Name

    ,                        !- Output:Variable or Output:Meter Index Key Name

    Outdoor Humidity Ratio;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Vwind,                   !- Name

    ,                        !- Output:Variable or Output:Meter Index Key Name

    Wind Speed;              !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    WH_sch,                  !- Name

    AlwaysOn,                !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Range_sch,               !- Name

    RangeHood,               !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Bath_sch,                !- Name

    BathExhaust,             !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Clothes_dryer_sch,       !- Name

    ClothesDryerExhaust,     !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    NVAvail,                 !- Name

    NatVentAvailability,     !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    NVSP,                    !- Name

    NatVentTemp,             !- Output:Variable or Output:Meter Index Key Name

    Schedule Value;          !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Q_heat,                  !- Name

    Furnace Heating Coil,    !- Output:Variable or Output:Meter Index Key Name

    Heating Coil Gas Consumption;  !- Output:Variable or Output:Meter Name

 

EnergyManagementSystem:Sensor,

    Q_WH,                    !- Name

    Water Heater,            !- Output:Variable or Output:Meter Index Key Name

    Water Heater Gas Consumption;  !- Output:Variable or Output:Meter Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:ACTUATOR ===========

 

EnergyManagementSystem:Actuator,

    SupplyFanAvailabilityOverride,  !- Name

    SupplyFanAvailability,   !- Actuated Component Unique Name

    Schedule:Constant,       !- Actuated Component Type

    Schedule Value;          !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    CeilingFanScheduleOverride,  !- Name

    CeilingFansMaster,       !- Actuated Component Unique Name

    Schedule:Constant,       !- Actuated Component Type

    Schedule Value;          !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    WholeHouseFanPowerOverride,  !- Name

    House Exhaust Fan Load,  !- Actuated Component Unique Name

    ElectricEquipment,       !- Actuated Component Type

    Electric Power Level;    !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    RangeHoodFanPowerOverride,  !- Name

    Range Hood Fan Load,     !- Actuated Component Unique Name

    ElectricEquipment,       !- Actuated Component Type

    Electric Power Level;    !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    BathExhaustFanPowerOverride,  !- Name

    Bath Exhaust Fan Load,   !- Actuated Component Unique Name

    ElectricEquipment,       !- Actuated Component Type

    Electric Power Level;    !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    NatVentFlow,             !- Name

    Natural Ventilation,     !- Actuated Component Unique Name

    Zone Ventilation,        !- Actuated Component Type

    Air Exchange Flow Rate;  !- Actuated Component Control Type

 

EnergyManagementSystem:Actuator,

    InfilFlow,               !- Name

    Living Infiltration,     !- Actuated Component Unique Name

    Zone Infiltration,       !- Actuated Component Type

   Air Exchange Flow Rate;  !- Actuated Component Control Type

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAMCALLINGMANAGER ===========

 

EnergyManagementSystem:ProgramCallingManager,

    FanAvailabilityProgramManager,  !- Name

    AfterPredictorBeforeHVACManagers,  !- EnergyPlus Model Calling Point

    SupplyFanScheduleProgram;!- Program Name 1

 

EnergyManagementSystem:ProgramCallingManager,

    CeilingFanProgramManager,!- Name

    BeginTimestepBeforePredictor,  !- EnergyPlus Model Calling Point

    CeilingFanScheduleProgram;  !- Program Name 1

 

EnergyManagementSystem:ProgramCallingManager,

    AirflowCalculator,       !- Name

    BeginTimestepBeforePredictor,  !- EnergyPlus Model Calling Point

    InfiltrationProgram,     !- Program Name 1

    NaturalVentilationProgram,  !- Program Name 2

    LocalWindSpeedProgram;   !- Program Name 3

 

EnergyManagementSystem:ProgramCallingManager,

    HVACOutputReporting,     !- Name

    EndOfSystemTimestepBeforeHVACReporting,  !- EnergyPlus Model Calling Point

    HeatingFuelConversionProgram,  !- Program Name 1

    WaterHeatingFuelConversionProgram,  !- Program Name 2

    ZeroMeterProgram;        !- Program Name 3

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:PROGRAM ===========

 

EnergyManagementSystem:Program,

    SupplyFanScheduleProgram,!- Name

    Set SupplyFanAvailabilityOverride = 1,  !- Program Line 1

    If Sensor_HeatingSeasonSchedule == 0 && SensibleLoadPredicted > 0,  !- Program Line 2

    Set SupplyFanAvailabilityOverride = 0,  !- A4

    EndIf,                   !- A5

    If Sensor_CoolingSeasonSchedule == 0 && SensibleLoadPredicted < 0,  !- A6

    Set SupplyFanAvailabilityOverride = 0,  !- A7

    EndIf;                   !- A8

 

EnergyManagementSystem:Program,

    CeilingFanScheduleProgram,  !- Name

    If CeilingFansSetup_sch == 0,  !- Program Line 1

    Set CeilingFanScheduleOverride = 0,  !- Program Line 2

    ElseIf Tin <24.3888888888889,  !- A4

    Set CeilingFanScheduleOverride = 0,  !- A5

    Else,                    !- A6

    Set CeilingFanScheduleOverride = 1,  !- A7

    EndIf;                   !- A8

 

EnergyManagementSystem:Program,

    InfiltrationProgram,     !- Name

    Set Tdiff = Tin - Tout,  !- Program Line 1

    Set DeltaT = @Abs Tdiff, !- Program Line 2

    Set c =0.0186678539272857,  !- A4

    Set Cs =0.0914908105247515,  !- A5

    Set Cw =0.158717056678613,  !- A6

    Set n =0.67,             !- A7

    Set sft =0.518999545453675,  !- A8

    Set Qn = (((c*Cs*(DeltaT^n))^2)+(((c*Cw)*((sft*Vwind)^(2*n)))^2))^0.5,  !- A9

    Set Tdiff = Tin - Tout,  !- A10

    Set DeltaT = @Abs Tdiff, !- A11

    Set QWH = WH_sch*0.024567114,  !- A12

    Set Qrange = Range_sch*0.04719,  !- A13

    Set Qdryer = Clothes_dryer_sch*0.04719,  !- A14

    Set Qbath = Bath_sch*0.04719,  !- A15

    Set Qu = Qrange+Qbath+Qdryer+DuctLeakOAMakeupFlowRate,  !- A16

    Set Qb = QWH,            !- A17

    Set WholeHouseFanPowerOverride = 0,  !- A18

    Set faneff_sp =0.4719,   !- A19

    Set RangeHoodFanPowerOverride = (Qrange*300)/faneff_sp,  !- A20

    Set BathExhaustFanPowerOverride = (Qbath*300)/faneff_sp,  !- A21

    Set Infilflow = ((Qu^2) + (Qn^2))^0.5,  !- A22

    Set InfMechVent = Qb + Infilflow;  !- A23

 

EnergyManagementSystem:Program,

    LocalWindSpeedProgram,   !- Name

    Set VwindL = Vwind*0.576666161615194;  !- Program Line 1

 

EnergyManagementSystem:Program,

    NaturalVentilationProgram,  !- Name

    Set Tdiff = Tin - Tout,  !- Program Line 1

    Set DeltaT = @Abs Tdiff, !- Program Line 2

    Set Phiin = @RhFnTdbWPb Tin Win Pbar,  !- A4

    Set Hin = @HFnTdbRhPb Tin Phiin Pbar,  !- A5

    Set NVArea =12057.7631145048,  !- A6

    Set Cs =0.0002016679587629,  !- A7

    Set Cw =0.0002992894757568,  !- A8

    Set MaxNV =3.2079762,    !- A9

    Set SGNV = (NVAvail*NVArea)*((((Cs*DeltaT)+(Cw*(Vwind^2)))^0.5)/1000),  !- A10

    If Wout < 0.0155 && Phiin < 0.70 && Tin > NVSP,  !- A11

    Set NVadj1 = (Tin - NVSP)/(Tin - Tout),  !- A12

    Set NVadj2 = @Min NVadj1 1,  !- A13

    Set NVadj3 = @Max NVadj2 0,  !- A14

    Set NVadj = SGNV*NVadj3, !- A15

    Set NatVentFlow = @Min NVadj MaxNV,  !- A16

    Else,                    !- A17

    Set NatVentFlow = 0,     !- A18

    EndIf;                   !- A19

 

EnergyManagementSystem:Program,

    ZeroMeterProgram,        !- Name

    Set ZeroMeter = 0;       !- Program Line 1

 

EnergyManagementSystem:Program,

    HeatingFuelConversionProgram,  !- Name

    Set Q_FuelOil = 0,       !- Program Line 1

    Set Q_Propane = 0,       !- Program Line 2

    Set Q_Gas = Q_heat;      !- A4

 

EnergyManagementSystem:Program,

    WaterHeatingFuelConversionProgram,  !- Name

    Set Q_WH_FuelOil = 0,    !- Program Line 1

    Set Q_WH_Propane = 0,    !- Program Line 2

    Set Q_WH_Gas = Q_WH;     !- A4

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:GLOBALVARIABLE ===========

 

EnergyManagementSystem:GlobalVariable,

    DuctLeakOAMakeupFlowRate;!- Erl Variable 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: ENERGYMANAGEMENTSYSTEM:OUTPUTVARIABLE ===========

 

EnergyManagementSystem:OutputVariable,

    Zone Infil/MechVent Flow Rate [m3/s],  !- Name

    InfMechVent,             !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    InfiltrationProgram;     !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Whole House Fan Vent Flow Rate [m3/s],  !- Name

    QWH,                     !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    InfiltrationProgram;     !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Range Hood Fan Vent Flow Rate [m3/s],  !- Name

    Qrange,                  !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    InfiltrationProgram;     !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Bath Exhaust Fan Vent Flow Rate [m3/s],  !- Name

    Qbath,                   !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    InfiltrationProgram;     !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Clothes Dryer Exhaust Fan Vent Flow Rate [m3/s],  !- Name

    Qdryer,                  !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    InfiltrationProgram;     !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Local Wind Speed [m/s],  !- Name

    VwindL,                  !- EMS Variable Name

   Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    LocalWindSpeedProgram;   !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Zone Natural Ventilation Flow Rate [m3/s],  !- Name

    NatVentFlow,             !- EMS Variable Name

    Averaged,                !- Type of Data in Variable

    ZoneTimestep,            !- Update Frequency

    NaturalVentilationProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    ZeroMeter [J],           !- Name

    ZeroMeter,               !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    ZeroMeterProgram;        !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Heating FuelOil [m3],    !- Name

    Q_FuelOil,               !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    HeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Heating Propane [m3],    !- Name

    Q_Propane,               !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    HeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Heating Gas [J],         !- Name

    Q_Gas,                   !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    HeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Water Heating FuelOil [m3],  !- Name

    Q_WH_FuelOil,            !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    WaterHeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Water Heating Propane [m3],  !- Name

    Q_WH_Propane,            !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    WaterHeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

EnergyManagementSystem:OutputVariable,

    Water Heating Gas [J],   !- Name

    Q_WH_Gas,                !- EMS Variable Name

    Summed,                  !- Type of Data in Variable

    SystemTimestep,          !- Update Frequency

    WaterHeatingFuelConversionProgram;  !- EMS Program or Subroutine Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========

 

SetpointManager:Scheduled,

    DHW Loop Setpoint Manager,  !- Name

    Temperature,             !- Control Variable

    DHWSupplySetpoint,       !- Schedule Name

    DHW Supply Outlet Node;  !- Setpoint Node or NodeList Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: WATERUSE:EQUIPMENT ===========

 

WaterUse:Equipment,

    Clothes Washer,          !- Name

    Domestic Hot Water,      !- End-Use Subcategory

    0.0000010913964336,      !- Peak Flow Rate {m3/s}

    ClothesWasher,           !- Flow Rate Fraction Schedule Name

    CWWaterTempSchedule;     !- Target Temperature Schedule Name

 

WaterUse:Equipment,

    Dishwasher,              !- Name

    Domestic Hot Water,      !- End-Use Subcategory

    0.0000004110326749,      !- Peak Flow Rate {m3/s}

    Dishwasher,              !- Flow Rate Fraction Schedule Name

    DWWaterTempSchedule;     !- Target Temperature Schedule Name

 

WaterUse:Equipment,

    Sinks,                   !- Name

    Domestic Hot Water,      !- End-Use Subcategory

    0.0000021244857201,      !- Peak Flow Rate {m3/s}

    Sinks,                   !- Flow Rate Fraction Schedule Name

    SSBWaterTempSchedule;    !- Target Temperature Schedule Name

 

WaterUse:Equipment,

    Showers,                 !- Name

    Domestic Hot Water,      !- End-Use Subcategory

    0.0000037816253253,      !- Peak Flow Rate {m3/s}

    Showers,                 !- Flow Rate Fraction Schedule Name

    SSBWaterTempSchedule;    !- Target Temperature Schedule Name

 

WaterUse:Equipment,

    Baths,                   !- Name

    Domestic Hot Water,      !- End-Use Subcategory

    0.0000009695683818,      !- Peak Flow Rate {m3/s}

    Baths,                   !- Flow Rate Fraction Schedule Name

    SSBWaterTempSchedule;    !- Target Temperature Schedule Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: WATERUSE:CONNECTIONS ===========

 

WaterUse:Connections,

    Domestic Hot Water,      !- Name

    Water Demand Inlet Node, !- Inlet Node Name

    Water Demand Outlet Node,!- Outlet Node Name

    ,                        !- Supply Water Storage Tank Name

    ,                        !- Reclamation Water Storage Tank Name

    ,                        !- Hot Water Supply Temperature Schedule Name

    ,                        !- Cold Water Supply Temperature Schedule Name

    None,                    !- Drain Water Heat Exchanger Type

    ,                        !- Drain Water Heat Exchanger Destination

    ,                        !- Drain Water Heat Exchanger U-Factor Times Area {W/K}

    Sinks,                   !- Water Use Equipment 1 Name

    Showers,                 !- Water Use Equipment 2 Name

    Clothes Washer,          !- Water Use Equipment 3 Name

    Dishwasher,              !- Water Use Equipment 4 Name

    Baths;                   !- Water Use Equipment 5 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: WATERUSE:STORAGE ===========

 

WaterUse:Storage,

    Condensate Tank 1,       !- Name

    CC2 Condensate Drain Tank,  !- Water Quality Subcategory

    2,                       !- Maximum Capacity {m3}

    0,                       !- Initial Volume {m3}

    ,                        !- Design In Flow Rate {m3/s}

    ,                        !- Design Out Flow Rate {m3/s}

    ,                        !- Overflow Destination

    None,                    !- Type of Supply Controlled by Float Valve

    ,                        !- Float Valve On Capacity {m3}

    ,                        !- Float Valve Off Capacity {m3}

    ,                        !- Backup Mains Capacity {m3}

    ,                        !- Other Tank Name

    ScheduledTemperature,    !- Water Thermal Mode

    DWWaterTempSchedule,     !- Water Temperature Schedule Name

    Zone,                    !- Ambient Temperature Indicator

    ,                        !- Ambient Temperature Schedule Name

    dummy;                   !- Zone Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: CURVE:QUADRATIC ===========

 

Curve:Quadratic,

    DXDH-PLF-fPLR,           !- Name

    0.87000000,              !- Coefficient1 Constant

    0.13000000,              !- Coefficient2 x

    0.00000000,              !- Coefficient3 x**2

    0,                       !- Minimum Value of x

    1,                       !- Maximum Value of x

    0.7,                     !- Minimum Curve Output

    1;                       !- Maximum Curve Output

 

Curve:Quadratic,

    Furnace-PLF-fPLR,        !- Name

    0.8,                     !- Coefficient1 Constant

    0.2,                     !- Coefficient2 x

    0,                       !- Coefficient3 x**2

    0,                       !- Minimum Value of x

    1,                       !- Maximum Value of x

    0.7,                     !- Minimum Curve Output

    1;                       !- Maximum Curve Output

 

Curve:Quadratic,

    Cool-PLF-fPLR,           !- Name

    0.80141423,              !- Coefficient1 Constant

    0.23744685,              !- Coefficient2 x

    -0.0393773,              !- Coefficient3 x**2

    0,                       !- Minimum Value of x

    1,                       !- Maximum Value of x

    0.7,                     !- Minimum Curve Output

    1;                       !- Maximum Curve Output

 

 

!-   ===========  ALL OBJECTS IN CLASS: CURVE:CUBIC ===========

 

Curve:Cubic,

    FanEffCurve,             !- Name

    0,                       !- Coefficient1 Constant

    1,                       !- Coefficient2 x

    0,                       !- Coefficient3 x**2

    0,                       !- Coefficient4 x**3

    0,                       !- Minimum Value of x

    1,                       !- Maximum Value of x

    0,                       !- Minimum Curve Output

    1;                       !- Maximum Curve Output

 

Curve:Cubic,

    ConstantCubic,           !- Name

    1,                       !- Coefficient1 Constant

    0,                       !- Coefficient2 x

    0,                       !- Coefficient3 x**2

    0,                       !- Coefficient4 x**3

    -100,                    !- Minimum Value of x

    100;                     !- Maximum Value of x

 

 

!-   ===========  ALL OBJECTS IN CLASS: CURVE:EXPONENT ===========

 

Curve:Exponent,

    FanPowerCurve,           !- Name

    0,                       !- Coefficient1 Constant

    1,                       !- Coefficient2 Constant

    3,                       !- Coefficient3 Constant

    -100,                    !- Minimum Value of x

    100;                     !- Maximum Value of x

 

 

!-   ===========  ALL OBJECTS IN CLASS: CURVE:BIQUADRATIC ===========

 

Curve:Biquadratic,

    DXDH-WaterRemove-Cap-fT, !- Name

    -1.28176163,             !- Coefficient1 Constant

    0.02479092,              !- Coefficient2 x

    -0.00026154,             !- Coefficient3 x**2

    0.02119506,              !- Coefficient4 y

    -0.00008918,             !- Coefficient5 y**2

    0.00053490,              !- Coefficient6 x*y

    -100,                    !- Minimum Value of x

    100,                     !- Maximum Value of x

    -100,                    !- Minimum Value of y

    100;                     !- Maximum Value of y

 

Curve:Biquadratic,

    DXDH-EnergyFactor-fT,    !- Name

    -2.42694382,             !- Coefficient1 Constant

    0.08753404,              !- Coefficient2 x

    -0.00106911,             !- Coefficient3 x**2

    0.04393239,              !- Coefficient4 y

    -0.00015526,             !- Coefficient5 y**2

    -0.00013789,             !- Coefficient6 x*y

    -100,                    !- Minimum Value of x

    100,                     !- Maximum Value of x

    -100,                    !- Minimum Value of y

    100;                     !- Maximum Value of y

 

Curve:Biquadratic,

    Cool-Cap-fT,             !- Name

    1.26489391,              !- Coefficient1 Constant

    -0.035054982,            !- Coefficient2 x

    0.00211086,              !- Coefficient3 x**2

    -0.001526886,            !- Coefficient4 y

    -0.0000070308,           !- Coefficient5 y**2

    -0.0004691844,           !- Coefficient6 x*y

    -100,                    !- Minimum Value of x

    100,                     !- Maximum Value of x

    -100,                    !- Minimum Value of y

    100;                     !- Maximum Value of y

 

Curve:Biquadratic,

    Cool-EIR-fT,             !- Name

    0.38402403,              !- Coefficient1 Constant

   0.029696724,             !- Coefficient2 x

    -0.0011329308,           !- Coefficient3 x**2

    0.006490674,             !- Coefficient4 y

    0.0002626992,            !- Coefficient5 y**2

    -0.0001207224,           !- Coefficient6 x*y

    -100,                    !- Minimum Value of x

    100,                     !- Maximum Value of x

    -100,                    !- Minimum Value of y

    100;                     !- Maximum Value of y

 

Curve:Biquadratic,

    ConstantBiquadratic,     !- Name

    1,                       !- Coefficient1 Constant

    0,                       !- Coefficient2 x

    0,                       !- Coefficient3 x**2

    0,                       !- Coefficient4 y

    0,                       !- Coefficient5 y**2

    0,                       !- Coefficient6 x*y

    -100,                    !- Minimum Value of x

    100,                     !- Maximum Value of x

    -100,                    !- Minimum Value of y

    100;                     !- Maximum Value of y

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========

 

Output:VariableDictionary,IDF;

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:CONSTRUCTIONS ===========

 

Output:Constructions,Construction;

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:ENERGYMANAGEMENTSYSTEM ===========

 

 

Output:EnergyManagementSystem,

    NotByUniqueKeyNames,     !- Actuator Availability Dictionary Reporting

    NotByUniqueKeyNames,     !- Internal Variable Availability Dictionary Reporting

    ErrorsOnly;              !- EMS Runtime Language Debug Output Level

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========

 

Output:Table:SummaryReports,

    AllSummaryAndMonthly;    !- Report 1 Name

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:TABLE:MONTHLY ===========

 

Output:Table:Monthly,

    Cooling Energy,          !- Name

    3,                       !- Digits After Decimal

    Cooling:Electricity,     !- Variable or Meter 1 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 1

 

Output:Table:Monthly,

    Heating Energy,          !- Name

    3,                       !- Digits After Decimal

    Heating:Gas_,            !- Variable or Meter 1 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 1

    Heating:FuelOil,         !- Variable or Meter 2 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 2

    Heating:Propane,         !- Variable or Meter 3 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 3

    Heating:Electricity,     !- Variable or Meter 4 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 4

 

Output:Table:Monthly,

    Cool Fan/Pump Energy,    !- Name

    3,                       !- Digits After Decimal

    CoolingCoils:EnergyTransfer,  !- Variable or Meter 1 Name

    HoursNonZero,            !- Aggregation Type for Variable or Meter 1

    HVACFan:Fans:Electricity,!- Variable or Meter 2 Name

    SumOrAverageDuringHoursShown,  !- Aggregation Type for Variable or Meter 2

    GSHPPump:Electricity,    !- Variable or Meter 3 Name

    SumOrAverageDuringHoursShown;  !- Aggregation Type for Variable or Meter 3

 

Output:Table:Monthly,

    Heating Fan/Pump Energy, !- Name

    3,                       !- Digits After Decimal

    HeatingCoils:EnergyTransfer,  !- Variable or Meter 1 Name

    HoursNonZero,            !- Aggregation Type for Variable or Meter 1

    HVACFan:Fans:Electricity,!- Variable or Meter 2 Name

    SumOrAverageDuringHoursShown,  !- Aggregation Type for Variable or Meter 2

    GSHPPump:Electricity,    !- Variable or Meter 3 Name

    SumOrAverageDuringHoursShown,  !- Aggregation Type for Variable or Meter 3

    HydronicPump:Electricity,!- Variable or Meter 4 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 4

 

Output:Table:Monthly,

    Hot Water Energy,        !- Name

    3,                       !- Digits After Decimal

    WaterHeating:Gas_,       !- Variable or Meter 1 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 1

    WaterHeating:FuelOil,    !- Variable or Meter 2 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 2

    WaterHeating:Propane,    !- Variable or Meter 3 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 3

    WaterSystems:Electricity,!- Variable or Meter 4 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 4

    SDHWPump:Electricity,    !- Variable or Meter 5 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 5

 

Output:Table:Monthly,

    Lighting Energy,         !- Name

    3,                       !- Digits After Decimal

    GeneralLights:Electricity,  !- Variable or Meter 1 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 1

 

Output:Table:Monthly,

    Large Appliance Energy,  !- Name

    3,                       !- Digits After Decimal

    Appl:InteriorEquipment:Gas,  !- Variable or Meter 1 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 1

    Appl:InteriorEquipment:Electricity,  !- Variable or Meter 2 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 2

 

Output:Table:Monthly,

    Vent Fan Energy,         !- Name

    3,                       !- Digits After Decimal

    VentFans:Electricity,    !- Variable or Meter 1 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 1

 

Output:Table:Monthly,

    Misc Energy,             !- Name

    3,                       !- Digits After Decimal

    Misc:InteriorEquipment:Gas,  !- Variable or Meter 1 Name

    SumOrAverage,            !- Aggregation Type for Variable or Meter 1

    Misc:InteriorEquipment:Electricity,  !- Variable or Meter 2 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 2

 

Output:Table:Monthly,

    PV Energy,               !- Name

    3,                       !- Digits After Decimal

    PV:Electricity,          !- Variable or Meter 1 Name

    SumOrAverage;            !- Aggregation Type for Variable or Meter 1

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========

 

OutputControl:Table:Style,

    CommaAndHTML,            !- Column Separator

    InchPound;               !- Unit Conversion

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========

 

Output:Variable,*,Zone/Sys Sensible Cooling Energy,Hourly;

Output:Variable,*,Outdoor Dry Bulb,Hourly;

Output:Variable,*,Zone/Sys Sensible Heating Rate,Hourly;

Output:Variable,*,Zone/Sys Sensible Cooling Rate,Hourly;

Output:Variable,*,Zone Air Relative Humidity,Hourly;

Output:Variable,*,AirflowNetwork Duct Leak Sensible Gain Rate,Hourly;

Output:Variable,*,AirflowNetwork Duct Leak Sensible Loss Rate,Hourly;

Output:Variable,*,Zone Ventilation Fan Electric Consumption,Hourly;

Output:Variable,*,Total HVAC Electric Demand,Hourly;

Output:Variable,*,Time Not Comfortable Summer Clothes,Hourly;

Output:Variable,*,Time Not Comfortable Winter Clothes,Hourly;

Output:Variable,*,Time Not Comfortable Summer Clothes,Hourly;

Output:Variable,*,Time Cooling Setpoint Not Met While Occupied,Hourly;

Output:Variable,*,Time Not Comfortable Summer Or Winter Clothes,Hourly;

Output:Variable,*,Zone/Sys Air Temperature,Hourly;

Output:Variable,*,FangerPMV,Hourly;

Output:Variable,*,FangerPPD,Hourly;

Output:Variable,*,PiercePMVET,Hourly;

Output:Variable,*,PiercePMVSET,Hourly;

Output:Variable,*,PierceDISC,Hourly;

Output:Variable,*,PierceTSENS,Hourly;

Output:Variable,*,KsuTSV,Hourly;

Output:Variable,*,ThermalComfortMRT,Hourly;

Output:Variable,*,ThermalComfort Operative Temperature,Hourly;

Output:Variable,*,Time Cooling Setpoint Not Met While Occupied,Hourly;

Output:Variable,*,Time Cooling Setpoint Not Met,Hourly;

Output:Variable,*,DX Cooling Coil Electric Consumption,Hourly;

Output:Variable,*,DX Coil Total Cooling Energy,Hourly;

Output:Variable,*,DX Cooling Coil Electric Power,Hourly;

Output:Variable,*,DX Cooling Coil Runtime Fraction,Hourly;

Output:Variable,*,On/Off Fan Runtime Fraction,Hourly;

Output:Variable,*,Air Loop System Cycle On/Off Status,Hourly;

Output:Variable,*,Plant Loop System Cycle On/Off Status,Hourly;

Output:Variable,*,Plant Loop Cooling Demand,Hourly;

Output:Variable,*,Plant Loop Heating Demand,Hourly;

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:METER ===========

 

Output:Meter,Cooling:Electricity,Hourly;

Output:Meter,Cooling:Electricity,Hourly;

Output:Meter,HVACFan:Fans:Electricity,Hourly;

Output:Meter,HVACFan:Fans:Electricity,Hourly;

Output:Meter,Electricity:HVAC,Hourly;

Output:Meter,Electricity:HVAC,Hourly;

Output:Meter,EnergyTransfer:HVAC,Hourly;

Output:Meter,EnergyTransfer:HVAC,Hourly;

Output:Meter,Electricity:HVAC,Monthly;

Output:Meter,Electricity:HVAC,Annual;

 

!-   ===========  ALL OBJECTS IN CLASS: METER:CUSTOM ===========

 

 

Meter:Custom,

    Heating:Gas_,            !- Name

    NaturalGas,              !- Fuel Type

    ,                        !- Key Name 1

    Heating Gas;             !- Report Variable or Meter Name 1

 

Meter:Custom,

    Heating:FuelOil,         !- Name

    FuelOil#1,               !- Fuel Type

    ,                        !- Key Name 1

    Heating FuelOil;         !- Report Variable or Meter Name 1

 

Meter:Custom,

    Heating:Propane,         !- Name

    PropaneGas,              !- Fuel Type

    ,                        !- Key Name 1

    Heating Propane;         !- Report Variable or Meter Name 1

 

Meter:Custom,

    GSHPPump:Electricity,    !- Name

    Electricity,             !- Fuel Type

    ZeroMeter;               !- Key Name 1

 

Meter:Custom,

    HydronicPump:Electricity,!- Name

    Electricity,             !- Fuel Type

    ZeroMeter;               !- Key Name 1

 

Meter:Custom,

    WaterHeating:Gas_,       !- Name

    NaturalGas,              !- Fuel Type

    ,                        !- Key Name 1

    Water Heating Gas;       !- Report Variable or Meter Name 1

 

Meter:Custom,

    WaterHeating:FuelOil,    !- Name

    FuelOil#1,               !- Fuel Type

    ,                        !- Key Name 1

    Water Heating FuelOil;   !- Report Variable or Meter Name 1

 

Meter:Custom,

    WaterHeating:Propane,    !- Name

    PropaneGas,              !- Fuel Type

    ,                        !- Key Name 1

    Water Heating Propane;   !- Report Variable or Meter Name 1

 

Meter:Custom,

    SDHWPump:Electricity,    !- Name

    Electricity,             !- Fuel Type

    ,                        !- Key Name 1

    ZeroMeter;               !- Report Variable or Meter Name 1

 

Meter:Custom,

    GeneralLights:Electricity,  !- Name

    Electricity,             !- Fuel Type

    ,                        !- Key Name 1

    InteriorLights:Electricity,  !- Report Variable or Meter Name 1

    ,                        !- Key Name 2

    ExteriorLights:Electricity;  !- Report Variable or Meter Name 2

 

Meter:Custom,

    VentFans:Electricity,    !- Name

    Electricity,             !- Fuel Type

    ,                        !- Key Name 1

    VentFans:Fans:Electricity,  !- Report Variable or Meter Name 1

    ,                        !- Key Name 2

    VentFans:InteriorEquipment:Electricity;  !- Report Variable or Meter Name 2

 

Meter:Custom,

    PV:Electricity,          !- Name

    Electricity,             !- Fuel Type

    ,                        !- Key Name 1

    ZeroMeter;               !- Report Variable or Meter Name 1

 

 

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:DIAGNOSTICS ===========

 

Output:Diagnostics,

    DisplayAdvancedReportVariables;  !- Key 1

 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___