In EnergyPlus, adiabatic surfaces are modeled as having the same temperature on both sides of the surface, but only inside face of the surface exchanges heat with the zone. This means that heat can be stored in the mass of the wall, but only makes it back into the zone if it is conducted through the inside face. Any heat lost through the outside face is ignored by the simulation. Essentially, you can only utilize half of the mass in the wall. FYI � this is also what is done in the case of the ThermalMass objects and is why the documentation suggest that you use twice the surface area when modeling thermal mass. Hope that helps, Neal Kruis From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Thodwris Xaritidis Hi louis, From: Luis Blanes <lmblanes@xxxxxxxxx> Dear __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.