The geometry stays where it is described.
For a high rise buildings so the z-coordinates for the multiplied floor should be an average for all floors being modeled. Unless there are neighboring buildings that are shading yours, the solar affects are not adjusted for height. However, the outdoor air temperatures and wind speeds are adjusted for height and these can be significant for really tall buildings.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay Devanathan
Sent: Wednesday, December 22, 2010 2:53 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Floor Multipliers
Hello,
When a Zone Group-Zone List object is used to implement floor multiplication, does doing this place the floor above the typical multiplied floor at a height it actually is present in the real building or it stays as it is drawn in the model? Would there be significant differences in solar effects if the height is not reflecting the real height of the floor (like for a 30 or 40-story building)?
Thank you.
Regards,
Vinay
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___