[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Controlling zone temperature using a boundary file



Omar,

You can use the Schedule:File object for this. Works like a charm.

Liam O'Brien

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "omarvelling" <laxoayi@...> wrote:
>
> Dear All,
> Is there any way in E+ that allows the user to change the heating/cooling set point of a certain zone at each simulation time-step by using a boundary file?
> The boundary file will contain time and dry bulb temperature to be used as the zone set temperature. If an ideal control is applied to that zone, providing the cooling or heating needed, the set temperature will be the zone temperature. Provided that there is an "unlimited" cooling device, the temperature in the zone will be maintained at the set point temperature.
> 
> Regards,
> Omar Ibraheem
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/