[EnergyPlus_Support] Re: Warning Message: air volume flow per cooling capacity out of range
I don't know if you will be able to do that in DB.
Did you see which is the flow/capacity range you have to stay within?
0.00004027 < [m3/s]/W < 0.00006041
Good luck!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "bcmcgr" <bcmcgr@...> wrote:
>
> Thank you both for your prompt help. It is definitely appreciated.
>
> Can either of you explain to me how you "ensure that the maximum supply flow is changed accordingly". I can definitely change the max to design conditions but I'm not sure how to do this in either E+ or DB.
>
> Thanks again.
>
> Brendan
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "James V Dirkes II, PE" <jim@> wrote:
> >
> > Dear Brendan,
> >
> >
> >
> > The airflow / watt warning is a common one for me, also, for manually sized
> > systems.
> >
> >
> >
> > I have not tried it yet, but the E+ Help desk suggested that I put two coils
> > in series to eliminate the warning. This effectively will leave the airflow
> > the same but cuts the coil capacity in half for each coil. it might work!
> >
> >
> >
> > p.s., This fix will probably not significantly affect your results unless
> > you have accurate part load curve information for your coils. If you DO
> > have that information, you may be able to cobble some part load coefficients
> > (different for each coil) that will do the trick.
> >
> >
> >
> > The Building Performance Team
> > James V. Dirkes II, P.E., LEED AP
> > 1631 Acacia Drive NW
> > Grand Rapids, MI 49504
> > 616 450 8653
> >
> >
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of bcmcgr
> > Sent: Wednesday, February 09, 2011 2:15 PM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: [EnergyPlus_Support] Warning Message: air volume flow per cooling
> > capacity out of range
> >
> >
> >
> >
> >
> > "Rated air volume flow rate per watt of rated total cooling capacity is out
> > of range."
> >
> > I'm working on a LEED project using Design Builder and my Proposed model
> > gets the above "Severe Error" when the model is run in E+. I can get around
> > this by having Design Builder "autosize" my HVAC system but then when I
> > check the HVAC system sizing output from E+ my sizes (capacities) are much
> > less than the actual design.
> >
> > It's important to note here that I'm modeling the minimum ventilation
> > (outside air) per ASHRAE 62.1 (ie per person and per area) which is much
> > smaller than the capabilities of the system.
> >
> > Has anyone encountered this in the past? Should I just submit the model as
> > if it's autosized?
> >
> > And, of course, I'm being rushed to submit by Friday. Any help on this is
> > much appreciated.
> >
> > Thanks in advance.
> >
> > Brendan
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/