Dear Shane, EnergyPlus normally responds favorably to assigning a Sizing:Parameter Sizing Factor greater than 1.0. ASHRAE 90.1 requires a factor of 1.15 for Cooling systems and 1.25 for heating systems. There are many other reasons why you may be experiencing the high number of unmet load hours, but that’s a start! The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Shane Watson When on simulating the idf model on design days, i am getting a large number of timeset point not met hours. What would be the correct way to reduce the setpoint not met hours and upto what limit. Thanks in advance. From: Drury B Crawley <dbcrawley@xxxxxxxxx> It is better to use design conditions from Chapter 14 of 2009 ASHRAE Fundamentals. If there are design data for that location, the .zip file will contain a .ddy file with that design data (design days). Otherwise you will have to create design day objects with the data from ASHRAE. You can read about design days in the ASHRAE document.
On Thu, Feb 10, 2011 at 8:17 AM, Shane Watson <mechenergy@xxxxxxxxx> wrote: Hi everyone, I am simulating a VAV system in an office building, Sizing of the system is done with weather file by using the objectSizing period:Weather file days. Is it a correct way to size the system on the weather file and let the software decide the design condtions. What impact it will have on the HVAC energy consumption. Thanks in advance. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |