[EnergyPlus_Support] Packaged VAV Cooling Coil
I'm a real beginner at this, so if you can help, please talk down to me.
I'm modeling an existing building with a 70 ton packaged VAV with reheat. An eQUEST model of the same building used a minimum design flow rate of 0.5 cfm/sf = 8 m^3/sec. I'm told that 1 ton of AC capacity translates to 350--500 cfm of airflow, so I used 425 cfm, which is approximately 14 m^3/sec. I converted 70 tons to approx 246kW, and used a sensible heat ratio of 0.75.
I can see that the minimum volumetric flow rate per watt is too small, but even if I change 8 to 12, I still get exactly the same error with the same (rated) number:
"At low speed rated air volume flow rate per watt of rated total cooling capacity is out of range. Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[3.790E-005], Max Rated Vol Flow Per Watt=[6.041E-005]."
Tweaking both max and min numbers only confuses me. If I change them to 15 and 14, respectively, I get:
"Rated air volume flow rate per watt of rated total cooling capacity is out of range. Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.093E-005], Max Rated Vol Flow Per Watt=[6.041E-005]."
Can someone tell me what's going on here?
Randy
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/