EnergyPlus can't model holes in surfaces so you should just comment out or remove that one.
At 05:26 AM 2/25/2011, Jaime Zuluaga Machado wrote:
HI!
From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
Thanks, I have solved this with your help.
I guess the problem was that the small one surface was not abble to discribe like Building Surface, so iIhad to make it like a fenestrion surface.
Now i get just one error:
** Severe ** FenestrationSurface:Detailed="VOID SPACE SOUTH" has an opaque surface construction; it should have a window construction.
This space that i want to simulate is a void space, is like a windows but this one is open.
Would you give me some advice to do this.
Thanks
Jaime Zuluaga M
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thu, 24 February, 2011 17:52:10
Subject: Re: [EnergyPlus_Support] Simulation
errors
Now go fix this surface - VOID SPACE SOUTH:
** Warning ** Floor Tilt=90.0, much less than expected tilt of 180,
for Surface=VOID SPACE SOUTH, in Zone=ZONE_2
Then look at the 3rd vertex for the surface WALL EAST:
** Severe ** Suspected non-planar surface:"WALL EAST", Max "out of
line"=1.02916E-002 at Vertex # 3
Then go make your door or window a rectangle:
** Severe ** Suspected 4-sided but non-rectangular Window, Door or
GlassDoor:
** ~~~ ** Surface=WINDOWS SOUTH, Diagonal1=39.187, Diagonal2=39.245
Get it now?
On 2/24/2011 5:48 PM, Jaime Zuluaga Machado wrote:
> ** Warning ** Floor Tilt=90.0, much less than expected tilt of 180,
> for Surface=VOID SPACE SOUTH, in Zone=ZONE_2
--
Richard A. Raustad