hello all.
Lately i've been using IdealLoadsAirSystem template to quickly control a zone temperature. I have a temperature profile i want to keep, and from there i create a heating and cooling schedule with a dT of 0.5 degrees from the temp profile. And its been working well up till today, when i got this unexpected severe error:
** Severe ** InitPurchasedAir: For ZoneHVAC:IdealLoadsAirSystem = ZMZONEHVAC:IDEALLOADSAIRSYSTEM serving Zone ZM
** ~~~ ** ..the supply air temperature for cooling [13.00] is greater than the zone cooling mean air temperature (MAT) setpoint [12.90].
** ~~~ ** ..For operative and comfort thermostat controls, the MAT setpoint is computed.
** ~~~ ** ..This error may indicate that the mean radiant temperature or another comfort factor is too warm.
** ~~~ ** Environment=FLUXO_EXT_BOTTOM, at Simulation time=04/24 03:10 - 03:20
I havent done anything diferently other than using a diferent temperature profile, and i'm not understading where the 13ºC limitation might come from. HVAC related, only have the two schedules for cooling/heating and one IdealLoadsAirSystem for the zone in question. any help in figuring this one out is very welcome, thank you.
Pedro
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___